Topic: Flexible Cable CID2 Location

User: JovialBulge, Location: New England

Asked on: Monday, July 29, 2024 at 9:58 am EDT
Answered on: Thursday, March 6, 2025 at 12:25 am EST

Question: Device is UL listed as explosion proof for CID2 and requires 24VDC @ 250mA to operate. I assume I can install this device within a CID2 location based on this information and referencing this section of the code.500.7(A) Explosionproof equipment500.7(F) Nonincendive circuitI must use flexible wiring to this device based on its location within the overall machine so I assume that has to be done in accordance with the hazardous location. Which brings me here in the code.501.10(A)(1)501.10(B)(2)(1)-(7)Specifically 501.10(B)(6)Flexible cord listed for extra-hard usage and terminated with listed fittings. A conductor for use as an equipment grounding conductor shall be included in the flexible cord.501.140(A)(2)I then meander to Article 400 and more specifically Table 400.4 to determine which cables are considered to be "extra-hard" usage.So long as the cord is correct for the location based on the referenced table above (400.4) and it’s terminated at both ends correctly; one side will be into the device itself which has a female NPT port and then into UL listed type 4 or 4X enclosure. Is there anything else that I need to consider with this installation?

Your thought process and code references are generally correct, but let's break it down with more detail and potential pitfalls to consider

What you've got right:
CID2 Applicability

The device being UL listed as explosion-proof for Class I, Division 2 is the foundation. If the documentation clearly states that listing, you can generally install it in a CID2 location.


Flexible Wiring Necessity

Recognizing the need for flexible wiring due to the machine's construction is important.

NEC 501.10(B)(6)

This is the correct section for Class I, Division 2 with flexible cord.


Extra-Hard Usage and Table 400.4

Identifying the right cable type is crucial.

Grounding Conductor

Essential for safety.


Termination with Listed Fittings

Absolutely critical.

UL Listed Enclosure

Correct for housing the connection outside the explosion-proof device.

Things you NEED to double-check and potential issues


Device Listing Details



The devil is in the details of the UL Listing.
Carefully read the documentation provided with the device. Does the listing explicitly state that it's suitable for use with flexible cord, or does it assume rigid conduit? Some explosion-proof devices are certified assuming direct connection to a rigid conduit system. Using flexible cord might invalidate the listing. Temperature Rating

Verify the ambient temperature of the installation location. The temperature rating of the device and the flexible cord must be suitable for the highest expected ambient temperature plus any temperature rise from the device itself.2.

Flexible Cord Selection (Beyond Table 400.4)



Oil Resistance

Consider the environment. Is there a risk of exposure to oils, chemicals, or solvents? If so, choose a cord specifically listed as oil-resistant (e.g., SOOW, SJOOW, or similar).

Minimum Size

The conductors in the flexible cord must be sized to carry the required 250mA (plus a reasonable safety margin) without exceeding their ampacity rating.


Conductor Material

Copper conductors are almost always required.3.

Fittings and Terminations



Specific Fittings for Hazardous Locations

Don't just use any fitting that fits the NPT port and cord diameter. The fittings
must be specifically listed and marked for use with the chosen flexible cord and for Class I, Division 2 locations. Look for markings like "Ex d IIB T4 Gb" or similar depending on the gas group and temperature class.

Proper Installation

Torque values and sealing requirements for hazardous location fittings are critical. Follow the manufacturer's instructions precisely.

Strain Relief

Ensure adequate strain relief is provided at both the device and the enclosure. The flexible cord and its termination must not be subjected to tension or twisting.


Sealing Fittings

This is highly dependent on the specific environment. You may need to install a sealing fitting within 18" of the enclosure to prevent the passage of gases or vapors.4.

Enclosure Considerations



NEMA Type 4/4X

While NEMA 4 or 4X provides protection against water ingress and corrosion, it does

not
make the enclosure explosion-proof. The enclosure itself does not need to be explosion-proof, however, it may be required if the source of the hazard is within the enclosure. The enclosure needs to be appropriate for the environment and the connection method. Space for Wiring

Ensure the enclosure is large enough to accommodate the cord, the fittings, and the internal wiring with adequate bending radius.5.

Grounding (Earthing)



Dedicated Grounding Conductor

As you mentioned, the flexible cord
must contain a dedicated equipment grounding conductor (EGC).

Proper Termination

The EGC must be properly terminated at both ends (device and enclosure) using listed grounding connectors.

Grounding Path Integrity

Ensure the grounding path from the device to the main electrical panel is continuous and of low impedance.6.

Area Classification Verification



Accurate Classification

Double-check that the area classification (Class I, Division 2) is accurate and based on a qualified hazard assessment. You don't want to underspecify the equipment if a different classification applies.7.

Documentation



Record Keeping

Maintain complete documentation of the installation, including:
Device UL Listing and installation instructions. Flexible cord specifications (manufacturer, part number, ratings). Fitting specifications (manufacturer, part number, hazardous location markings). Enclosure specifications. Inspection records.8.

501.140(A)(2)

This section refers to the "Raceway or Cable Seal." This section states that seals are required for conduits, cable, and raceways that enter enclosures. The enclosure that the device is being wired to falls into this requirement.9.

Local Codes and Regulations



AHJ (Authority Having Jurisdiction)

Always consult with your local electrical inspector or AHJ. They may have additional requirements or interpretations of the NEC.

In summary:
You're on the right track, but the key is to pay meticulous attention to the details of the UL listings, the specifications of the flexible cord and fittings, and the proper installation techniques for hazardous locations. Don't take shortcuts, and always double-check your work. Hazardous location installations demand precision. Consult with a qualified electrical engineer or technician experienced in hazardous location installations if you have any doubts. Flag for review