User: Mike Harkey, Location: Little Rock, AR
Asked on: Monday, July 29, 2024 at 10:30 am EDT
Answered on: Thursday, March 6, 2025 at 12:25 am EST
Question: In a 1200A 3P 120/208V switchboard, with (8) 100A 3P breakers feeding (8) different buildings, with the (8) 1/0 panel feeders underground in galvanized rigid steel conduit. Is there a code requirement, or good practice requirement, for a maximum leakage current in these panel feeder conductors, or a minimum impedance when measured with a 'megger'?
You're asking about insulation resistance testing (meggering) and leakage current limits for feeder conductors. Here's a breakdown of what the NEC and good practices say
NEC (National Electrical Code) Considerations:
No Explicit Leakage Current Limit for Existing Installations
The NEC doesn't provide a hard-and-fast leakage current limit for existing installations like yours. It focuses on preventing hazards and ensuring safe operation. There isn't a section that says "you must replace conductors if leakage current exceeds X amps."
Installation Requirements
NEC 110.7 Deteriorating Agents
While not a specific leakage current requirement, this section addresses the overall integrity of wiring. It requires that wiring and equipment be installed in a way that avoids deterioration caused by things like moisture, chemicals, and physical damage. Excessive leakage current could be a symptom of deterioration.
NEC 110.12 Neat and Workmanlike Manner
Poor workmanship during installation (damaged insulation during pulling, improper terminations) can lead to premature insulation breakdown and increased leakage.
NEC 250 Bonding and Grounding
Proper bonding and grounding are critical to safety. If the grounding system isn't effective, leakage currents can create dangerous touch potentials.
Testing After Faults or Damage (Implied Requirement)
The NEC implicitly requires testing after a fault or suspected damage. For example, if a fault occurs that trips a breaker, good practice dictates investigating the cause, inspecting the conductors, and testing their insulation resistance before re-energizing the circuit.
NEC 590 Temporary Installations
These installations may have more stringent requirements.
New Installations
The NEC does indirectly influence insulation resistance levels during installation. Conductors must meet UL standards, which include insulation resistance tests.
Good Practices and Recommended Insulation Resistance Values (Meggering)
Why Meggering? Meggering applies a DC voltage to the conductor and measures the current that flows through the insulation. A higher resistance means better insulation. A low resistance indicates that current is leaking through the insulation, possibly due to moisture, contamination, physical damage, or age. Recommended Minimum Insulation Resistance
General Rule
A common rule of thumb is 1 Megohm per 1000 volts of operating voltage (line-to-line) for a minimum value. For your 208V system, that would be 0.208 Megohms (208,000 ohms). However, this is a very simplified guideline.
More Detailed Recommendations
0.2 to 2 Megohms (Low)
Investigate further. This could indicate insulation degradation. Look for signs of moisture, contamination, physical damage, or overheating. Consider cleaning and re-testing. A trend of decreasing resistance over time is a major concern.
2 to 10 Megohms (Marginal)
Monitor closely. Consider more frequent testing and inspections.
10+ Megohms (Good)
Generally acceptable for most applications.
Factors Affecting Insulation Resistance
Temperature
Insulation resistance decreases as temperature increases. Correct your readings for temperature.
Humidity
High humidity can significantly reduce insulation resistance.
Conductor Length
Longer conductors will have lower insulation resistance readings (more surface area for leakage).
Conductor Age
Insulation degrades over time.
Contamination
Dirt, oil, and other contaminants can reduce insulation resistance.
Megger Test Procedure
De-energize and Isolate
Absolutely crucial! Disconnect the conductors from both the switchboard and the panel. Lockout/Tagout procedures must be followed.2.
Clean
Clean the terminations and exposed insulation.3.
Connect the Megger
Connect one lead to the conductor and the other lead to ground (the conduit is usually a good ground reference, but verify it's properly grounded).4.
Apply Test Voltage
Use a megger with a suitable test voltage (typically 500V DC or 1000V DC for 208V systems). Do not use excessive voltage as it can damage insulation.5.
Record Readings
Note the resistance reading after a specific period (e.g., 1 minute).6.
Discharge
Very important! After the test, discharge the conductor before touching it. High DC voltages can build up.
Leakage Current Measurements
Clamp-On Leakage Current Meter
A specialized clamp-on meter can measure leakage current without disconnecting the conductors. These meters are designed to detect very small currents (mA or even µA).
Acceptable Leakage Current
General Guideline
As a VERY general guideline, leakage current should be less than 5mA per circuit. This is a very loose guideline, and lower is always better.
Context Matters
The acceptable level depends on the application and the sensitivity of downstream equipment. Some electronic equipment is very sensitive to even small leakage currents.
Multiple Circuits
The cumulative leakage current from multiple circuits can be significant, even if each individual circuit is within acceptable limits.
Specific Considerations for Your Situation
Underground Conduit
Underground conduit is a harsh environment. Moisture is a common problem, which can significantly reduce insulation resistance and increase leakage current. Galvanized rigid steel conduit (GRC) is good, but not perfect, protection against moisture.
Multiple Buildings
Feeding multiple buildings increases the risk of ground faults and leakage currents.
1/0 Conductors
1/0 conductors are a reasonable size for 100A circuits, but it's critical that the terminations are properly made and that the conductors aren't damaged during pulling.
Existing Installation
Since it is an existing installation, there will be signs of expected wear and tear. The conductors will not be new, and this is the most important aspect.
Recommendations
Routine Testing
Implement a routine insulation resistance testing program (meggering) for your feeder circuits. The frequency should be based on the age of the installation, the environmental conditions, and the criticality of the loads. Annual testing is a good starting point.2.
Baseline Readings
Establish baseline readings for each circuit when the conductors are known to be in good condition. This will allow you to track changes over time.3.
Investigate Low Readings
If you get low insulation resistance readings or high leakage current readings, investigate the cause. Check for:
Moisture
Evidence of water in the conduit or junction boxes.
Contamination
Dirt, oil, or other contaminants.
Physical Damage
Nicks, cuts, or abrasions on the insulation.
Loose Connections
Improperly tightened terminations.
Overheating
Signs of heat damage on the insulation.4.
Correct Problems
Repair or replace conductors with damaged insulation. Ensure that all connections are clean and tight. Address any moisture problems.5.
Ground Fault Protection
Ensure that your ground fault protection system is functioning properly. This is essential for safety.6.
Documentation
Keep detailed records of all test results and any corrective actions taken.7.
Consult an Expert
If you're unsure about how to perform insulation resistance testing or how to interpret the results, consult a qualified electrician or electrical testing company.
In Summary:
While the NEC doesn't specify a mandatory leakage current limit for existing installations, good electrical safety practices dictate regular insulation resistance testing (meggering) to identify potential problems. A trend of decreasing insulation resistance or increasing leakage current should be investigated and addressed promptly to prevent electrical hazards and ensure the reliability of your system. Use the recommendations outlined above for good minimum megger readings, and what to do if those readings are not met. Flag for review