Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Commercial 600 amp service

User: TYINMW, Location: TEXAS

Asked on: Monday, July 29, 2024 at 12:11 pm EDT
Answered on: Thursday, March 6, 2025 at 12:25 am EST

Question: On a 600 amp 208 volt 3 phase underground service, is there a maximum distance allowed between secondary side of transsocket and exterior service disconnect?TIA

You're asking about insulation resistance testing (meggering) and leakage current limits for feeder conductors. Here's a breakdown of what the NEC and good practices say

NEC (National Electrical Code) Considerations:
No Explicit Leakage Current Limit for Existing Installations

The NEC doesn't provide a hard-and-fast leakage current limit for
existing installations like yours. It focuses on preventing hazards and ensuring safe operation. There isn't a section that says "you must replace conductors if leakage current exceeds X amps."

Installation Requirements



NEC 110.7 Deteriorating Agents

While not a specific leakage current requirement, this section addresses the overall integrity of wiring. It requires that wiring and equipment be installed in a way that avoids deterioration caused by things like moisture, chemicals, and physical damage. Excessive leakage current could be a
symptom of deterioration.

NEC 110.12 Neat and Workmanlike Manner

Poor workmanship during installation (damaged insulation during pulling, improper terminations) can lead to premature insulation breakdown and increased leakage.

NEC 250 Bonding and Grounding

Proper bonding and grounding are
critical to safety. If the grounding system isn't effective, leakage currents can create dangerous touch potentials.

Testing After Faults or Damage (Implied Requirement)

The NEC implicitly requires testing after a fault or suspected damage. For example, if a fault occurs that trips a breaker, good practice dictates investigating the cause, inspecting the conductors, and testing their insulation resistance before re-energizing the circuit.

NEC 590 Temporary Installations

These installations may have more stringent requirements.


New Installations

The NEC does indirectly influence insulation resistance levels during installation. Conductors must meet UL standards, which include insulation resistance tests.

Good Practices and Recommended Insulation Resistance Values (Meggering)



Why Meggering?
Meggering applies a DC voltage to the conductor and measures the current that flows through the insulation. A higher resistance means better insulation. A low resistance indicates that current is leaking through the insulation, possibly due to moisture, contamination, physical damage, or age. Recommended Minimum Insulation Resistance



General Rule

A common rule of thumb is 1 Megohm per 1000 volts of operating voltage (line-to-line) for a
minimum value. For your 208V system, that would be 0.208 Megohms (208,000 ohms). However, this is a very simplified guideline.

More Detailed Recommendations



0.2 to 2 Megohms (Low)

Investigate further. This could indicate insulation degradation. Look for signs of moisture, contamination, physical damage, or overheating. Consider cleaning and re-testing. A trend of decreasing resistance over time is a major concern.


2 to 10 Megohms (Marginal)

Monitor closely. Consider more frequent testing and inspections.

10+ Megohms (Good)

Generally acceptable for most applications.


Factors Affecting Insulation Resistance



Temperature

Insulation resistance
decreases as temperature increases. Correct your readings for temperature.

Humidity

High humidity can significantly reduce insulation resistance.

Conductor Length

Longer conductors will have lower insulation resistance readings (more surface area for leakage).


Conductor Age

Insulation degrades over time.

Contamination

Dirt, oil, and other contaminants can reduce insulation resistance.


Megger Test Procedure


De-energize and Isolate

Absolutely crucial! Disconnect the conductors from both the switchboard and the panel. Lockout/Tagout procedures must be followed.2.

Clean

Clean the terminations and exposed insulation.3.

Connect the Megger

Connect one lead to the conductor and the other lead to ground (the conduit is usually a good ground reference, but verify it's properly grounded).4.

Apply Test Voltage

Use a megger with a suitable test voltage (typically 500V DC or 1000V DC for 208V systems). Do not use excessive voltage as it can damage insulation.5.

Record Readings

Note the resistance reading after a specific period (e.g., 1 minute).6.

Discharge

Very important! After the test, discharge the conductor before touching it. High DC voltages can build up.

Leakage Current Measurements



Clamp-On Leakage Current Meter

A specialized clamp-on meter can measure leakage current without disconnecting the conductors. These meters are designed to detect very small currents (mA or even µA).


Acceptable Leakage Current



General Guideline

As a VERY general guideline, leakage current should be
less than 5mA per circuit. This is a very loose guideline, and lower is always better.

Context Matters

The acceptable level depends on the application and the sensitivity of downstream equipment. Some electronic equipment is very sensitive to even small leakage currents.

Multiple Circuits

The
cumulative leakage current from multiple circuits can be significant, even if each individual circuit is within acceptable limits.

Specific Considerations for Your Situation



Underground Conduit

Underground conduit is a harsh environment. Moisture is a common problem, which can significantly reduce insulation resistance and increase leakage current. Galvanized rigid steel conduit (GRC) is good, but not perfect, protection against moisture.

Multiple Buildings

Feeding multiple buildings increases the risk of ground faults and leakage currents.


1/0 Conductors

1/0 conductors are a reasonable size for 100A circuits, but it's critical that the terminations are properly made and that the conductors aren't damaged during pulling.

Existing Installation

Since it is an existing installation, there will be signs of expected wear and tear. The conductors will not be new, and this is the most important aspect.

Recommendations


Routine Testing

Implement a routine insulation resistance testing program (meggering) for your feeder circuits. The frequency should be based on the age of the installation, the environmental conditions, and the criticality of the loads. Annual testing is a good starting point.2.

Baseline Readings

Establish baseline readings for each circuit when the conductors are known to be in good condition. This will allow you to track changes over time.3.

Investigate Low Readings

If you get low insulation resistance readings or high leakage current readings, investigate the cause. Check for:


Moisture

Evidence of water in the conduit or junction boxes.

Contamination

Dirt, oil, or other contaminants.


Physical Damage

Nicks, cuts, or abrasions on the insulation.

Loose Connections

Improperly tightened terminations.


Overheating

Signs of heat damage on the insulation.4.

Correct Problems

Repair or replace conductors with damaged insulation. Ensure that all connections are clean and tight. Address any moisture problems.5.

Ground Fault Protection

Ensure that your ground fault protection system is functioning properly. This is essential for safety.6.

Documentation

Keep detailed records of all test results and any corrective actions taken.7.

Consult an Expert

If you're unsure about how to perform insulation resistance testing or how to interpret the results, consult a qualified electrician or electrical testing company.

In Summary:


While the NEC doesn't specify a mandatory leakage current limit for existing installations, good electrical safety practices dictate regular insulation resistance testing (meggering) to identify potential problems. A trend of decreasing insulation resistance or increasing leakage current should be investigated and addressed promptly to prevent electrical hazards and ensure the reliability of your system. Use the recommendations outlined above for good minimum megger readings, and what to do if those readings are not met. Flag for review

Previous Question Next Question