Question: For above ground pools you have to hit 4 posts for the bonding. Is there anything in the code that says the joint plate where the walls of the pool are bolted together have to be bonded?The pool is filled, and my only fear is if I take this support post off to expose the plate with all the bolts I won’t be able to get it back into place because of the pressure of the water. Was going to call the inspector, but I figured I’d ask you guys first.
You're right to be cautious about removing a support post on a filled above-ground pool. That could definitely lead to problems.Here's a breakdown of the bonding requirements and what's generally understood about bonding the wall joints, along with considerations for your situation
NEC Requirements for Above-Ground Pool Bonding (General)
NEC 680.26 is the primary section dealing with pool bonding. It aims to equalize the electrical potential in and around the pool, minimizing the risk of electric shock. Perimeter Equipotential Bonding
This is a crucial element. A solid copper conductor (typically #8 AWG) must be run around the perimeter of the pool. This conductor is connected to:
The pool's metal structure
This includes the pool walls, supporting metal components, and any conductive non-electrical parts that are within reach of a person in the water.
Metal fittings
Any metal fittings like ladders, handrails, etc.
Metal parts of electrical equipment
Pump motors, heaters, lights, etc.
A reinforcing steel grid (if present) or a copper grid. Four Points
The perimeter bonding grid is generally required to be connected to the pool's metal structure at least four points, distributed around the perimeter. This ensures good electrical continuity.
Bonding of Pool Wall Joint Plates
Code Ambiguity
The NEC doesn't explicitly state that every single joint plate needs to be individually bonded. However, it's implied that the entire metal structure of the pool needs to be part of the bonded system.
Interpretation and Common Practice
Most inspectors interpret the code to mean that the entire conductive pool wall structure must be part of the bonded grid. The joint plates, being a key part of that conductive wall, are therefore usually considered to need bonding. The reasoning is that if a fault occurs, any part of the pool wall could become energized, and you want to ensure that any voltage differences are minimized.
Continuity is Key
The underlying goal is to have good electrical continuity throughout the pool wall. If the joint plates are making good, reliable electrical contact with the wall panels, some inspectors might accept that as sufficient (though this is less common). However, rust, corrosion, paint, or other non-conductive coatings between the plates and the wall panels can break that continuity.
Your Specific Situation and Concerns
Water Pressure
You are 100% right to be concerned about removing a support post with the pool filled. The pressure of the water could cause the walls to buckle or even collapse.
Do not remove the support post until you've consulted with a pool professional or the inspector and determined a safe way to proceed. Accessibility
Even if you could safely remove the post, working on a filled pool is a hassle. It's hard to reach things, and you risk getting the bonding wire wet (which isn't ideal).
The Potential Solution (If Bonding is Required)
"Saddle" Clamp with Jumper Wire
Instead of disconnecting the wall, you might be able to use a "saddle" clamp. This is a U-shaped clamp that fits over the edge of the joint plate. You can attach a bonding wire to the saddle clamp, creating a secure connection. Then, run a jumper wire from that saddle clamp to the nearest point on your perimeter bonding grid (one of the posts you've already bonded). This can often be done without fully disassembling anything.
Recommendations
Contact Your Inspector
Call your electrical inspector. Explain your situation exactly as you've described it here. Ask them specifically about the requirement for bonding the joint plates in your area and if they would accept the saddle clamp solution. Their interpretation is what matters.2.
Consider a Pool Professional
If the inspector says the joint plates must* be bonded but isn't sure about the saddle clamp, or if you're uncomfortable doing the work yourself, consult a licensed pool installer. They'll have experience with this and can advise on the safest and most code-compliant way to proceed.3.
Don't Guess
Don't take shortcuts or try to guess what the inspector will accept. Bonding is a safety issue, and it's critical to do it right.4.
Document Everything: Take pictures of your bonding setup before and after any work is done. Keep records of your conversations with the inspector and any pool professionals you consult. This will be helpful during the inspection.In summary, bonding the joint plates is a common requirement, but the specific methods and the inspector's interpretation can vary. Always prioritize safety and compliance with local codes. And definitely don't remove that support post without expert advice! Flag for review