Topic: 230.67 Surge Protection.

User: Madera Wil, Location: 200 West Forth St Madera CA 93637

Asked on: Monday, July 29, 2024 at 2:38 pm EDT
Answered on: Thursday, March 6, 2025 at 12:26 am EST

Question: NEC/CEC 230.67 (B) states, The SPD shall be an integral part of the service equipment or shall be located immediately adjacent thereto.Exception: The SPD shall not be required to be located in the service equipment as required in (B) if located at each level distribution equipment downstream.I want to make sure I'm understanding the exception correctly. I interpret it as saying that the SPD can be installed in a sub panel downstream. What say you?

You are correct in your interpretation. Let's break it down: 230.67(B) - Main Requirement

The SPD (Surge Protective Device)
must be either: Integrated into the main service equipment (the main panel). Located immediately adjacent to the main service equipment.

Exception

The SPD doesn't have to be at the main service entrance if... ...SPDs are installed at each downstream distribution panel (subpanel).

Therefore, your understanding is correct: The exception allows you to install SPDs in subpanels instead of at the main service entrance,
but only if you install an SPD at every distribution panel "downstream" from the main service entrance.
In simpler terms



If you want to protect the whole system and NOT put the SPD at the main panel, you have to put one in every subpanel.
Key Considerations



"Each Level"

This is important. If you have multiple levels of distribution (e.g., Main Panel -> Subpanel 1 -> Subpanel 2), you need SPDs at Subpanel 1
and Subpanel 2 to meet the exception. You can't just skip a level.

Cost

It's crucial to consider the cost of installing SPDs at every subpanel versus the cost of installing a single, potentially more robust, SPD at the main service entrance.

Coordination

SPDs must be properly coordinated to work effectively together. A qualified electrician or engineer should be consulted to ensure that the SPDs are compatible and provide adequate protection throughout the electrical system.


Specific SPD Ratings

Choosing the appropriate SPD voltage rating and surge current capacity (e.g., kA) is essential. The rating depends on the specific location in the system and the expected surge activity.

AHJ (Authority Having Jurisdiction)

Always check with your local electrical inspector or AHJ to ensure compliance with local codes and requirements. They may have specific interpretations or additional rules regarding SPD installations.

Example

Let's say you have a house with:
A main service panel (where the utility meter connects) A subpanel in the garage A subpanel in a workshopTo use the exception, you would need to install an SPD in BOTH the garage subpanel and the workshop subpanel. You would not need to install an SPD at the main service panel in this scenario.

In summary, the exception in 230.67(B) allows you to use a distributed SPD approach, placing SPDs in subpanels, but it requires a complete approach, protecting every level of distribution.