Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Generator

User: mannyb, Location: Florida

Asked on: Monday, July 29, 2024 at 8:47 pm EDT
Answered on: Thursday, March 6, 2025 at 12:26 am EST

Question: Sizing a generator for Municipal Water Treatment plant. Anything I should take into consideration? Will using the load analysis be enough or should we consider any stop start of motors. Most of the site is motors.

You're right to be thinking beyond a simple load analysis for sizing a generator for a municipal water treatment plant. Here's a breakdown of key considerations beyond a basic load calculation, focusing on the motor-heavy nature of the site

1. Load Analysis: The Foundation, But Not the Whole Picture
Create a Detailed Load Profile



List Every Load

Don't just group similar items. List each pump, motor, control panel, lighting circuit, HVAC unit, and any other electrical device.

Power Consumption

Record the rated power (kW or kVA) for each load. For motors, record both the nameplate kVA and the locked rotor kVA (LRKVA).


Operating Mode

Note whether each load is:

Continuous

Operates constantly (e.g., some lights, SCADA systems).


Intermittent

Operates with regular on/off cycles (e.g., pumps filling a tank). Estimate the duty cycle (percentage of time "on").

Standby

Operates only in emergencies (e.g., backup aerators).


Voltage and Phase

Note the voltage (e.g., 480V, 208V, 120V) and phase (single-phase or three-phase) requirements of each load.

Power Factor

Crucial for accurately calculating kVA from kW. Motor power factors are usually around 0.8 - 0.
9. If you don't have specific values, assume a conservative (lower) power factor.


Diversity Factors



Understand Diversity

Diversity is the probability that not all loads will operate at their full rated capacity simultaneously. This is a critical factor to avoid oversizing.


Apply Diversity Wisely

Be realistic and conservative. Over estimating diversity will cause your system to not work properly. The best diversity factor for a municipality is always 1.

Motor-Specific Diversity

Consider the likelihood of multiple large motors starting simultaneously. This is often lower than the diversity of smaller loads.


Calculate Peak Demand

This is the highest total power demand you expect the generator to supply at any given time. Consider different operational scenarios (e.g., normal operation, high-demand periods, equipment maintenance outages).

2. Motor Starting Considerations (VERY IMPORTANT)


This is where load analysis alone falls short. Motor starting creates a huge inrush of current, several times the motor's running current (locked rotor current, LRC). This can cause: Voltage Dip

Significant voltage drops can cause other equipment to malfunction, damage sensitive electronics, and trip breakers.


Generator Overload

The generator might not be able to supply the inrush current, leading to stalling or shutdown.

Reduced Motor Life

Repeated starts with high inrush current can stress motor windings.

Mitigation Strategies and Sizing for Motor Starting



Calculate Locked Rotor kVA (LRKVA)

As mentioned, this is crucial. You'll find LRKVA or a locked rotor code letter on the motor nameplate. Use this information to determine the inrush current. LRKVA is typically 6 to 10 times the running kVA.

Determine the Largest Motor(s)

Identify the single largest motor or the group of motors most likely to start simultaneously. This will drive the generator sizing.


Motor Starting Methods

The choice of motor starting method significantly impacts the inrush current.

Across-the-Line (Direct-on-Line)

The simplest but produces the highest inrush (typically 6-8 times the full load current). Generally NOT recommended for larger motors.


Reduced Voltage Starting

These methods reduce the voltage applied to the motor during starting, lowering the inrush current. Common methods include:

Autotransformer

Provides the best starting torque with reduced current.


Part Winding

Splits the motor windings.

Reactor or Resistor Starting

Uses external impedance.


Wye-Delta

Starts the motor in a wye configuration and switches to delta after starting.

Solid-State Starters (Soft Starters)

Use silicon-controlled rectifiers (SCRs) to gradually increase the voltage applied to the motor, providing smooth starting and adjustable inrush current. This is often the preferred method for many applications.


Variable Frequency Drives (VFDs)

VFDs provide the "softest" start, controlling both voltage and frequency. They eliminate inrush current altogether. However, VFDs are more expensive and complex than other starting methods.

Generator Sizing for Motor Starting

Here's the general approach:1.

Transient Voltage Dip

Specify the maximum allowable voltage dip during motor starting (e.g., 15-20%). The generator manufacturer will provide performance curves (or use software) showing the voltage dip for different load steps.2.

Subtransient Reactance (Xd")

This parameter of the generator is critical. Lower Xd" means the generator can handle higher inrush currents with less voltage dip. Look for a generator with a low Xd". Synchronous generators usually have better motor starting capability.3.

Generator kVA Rating

The generator kVA rating must be large enough to:
Supply the continuous base load (calculated in your load analysis). Handle the inrush current of the largest motor(s) without excessive voltage dip.4.

Motor Starting Calculations

The generator manufacturer or a qualified electrical engineer should perform detailed calculations to determine the appropriate generator size based on the motor starting method, motor LRKVA, generator Xd", and allowable voltage dip. They will use software and/or formulas to predict the voltage dip and recovery time.

3. Other Important Considerations
Harmonic Distortion

VFDs and other non-linear loads can generate harmonics, which can negatively impact generator performance and damage equipment. Consider:

Harmonic Filters

May be required to reduce harmonic distortion.


Generator Oversizing

Oversizing the generator can help it tolerate harmonics.

THD (Total Harmonic Distortion) Rating

Specify the maximum allowable THD.


Step Load Capability

How quickly can the generator pick up load? This is important if loads are switched on and off rapidly.

Transient Response

How quickly does the generator recover from a load change or voltage dip?


Altitude and Temperature

Derate the generator's capacity for high altitudes and high ambient temperatures.

Fuel Type and Availability

Consider the cost, availability, and storage requirements of different fuel types (diesel, natural gas, propane). Diesel is most common for standby generators.


Emissions Regulations

Ensure the generator meets all applicable emissions regulations.

Sound Levels

Consider noise restrictions in the area.


Redundancy

Depending on the criticality of the water treatment plant, consider using redundant generators for backup.

Automatic Transfer Switch (ATS)

The ATS automatically switches the load between the utility power and the generator during a power outage. Make sure the ATS is properly sized and tested.


Generator Control System

A sophisticated control system can monitor generator performance, manage load shedding, and provide remote monitoring and control.

Regular Maintenance

Schedule regular maintenance for the generator to ensure its reliability.

Who Should Do This?
Qualified Electrical Engineer

Crucially, you need a qualified electrical engineer experienced in generator sizing and motor starting to perform the calculations, select the appropriate equipment, and ensure the system is properly designed.

In summary, a simple load analysis is a starting point, but it's not sufficient for sizing a generator for a motor-heavy water treatment plant. You must carefully consider motor starting characteristics, voltage dip, harmonic distortion, and other factors to ensure a reliable and properly sized generator system. Engage a qualified electrical engineer to perform the necessary calculations and design the system.
Flag for review

Previous Question Next Question