Topic: Refrigerator

User: timmermeier, Location: alton il

Asked on: Monday, July 29, 2024 at 9:07 pm EDT
Answered on: Thursday, March 6, 2025 at 12:26 am EST

Question: Is their any code articles that say a refrigerator on a dedicated circuit ? ( any code article ) ???????????????????????????????????????????????????????

Yes, the National Electrical Code (NEC) addresses refrigerators and dedicated circuits. Here's a breakdown: NEC 210.52(B)(1) Dwelling Unit Receptacle Outlets. (1) Kitchen. In dwelling units, a receptacle outlet shall be installed at each countertop space that is 300 mm (12 in.) or wider. Exception No. 1: A receptacle outlet shall not be required on a wall directly behind a range, counter-mounted cooking unit, or sink. Exception No. 2: Receptacles shall not be required to be installed in islands and peninsulas. (2) Small Appliances. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop receptacle outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment. NEC 210.11(C)(1) Dwelling Unit Branch Circuit Requirements; Kitchen and Other Areas. (1) Small-Appliance Branch Circuits. In addition to the number of branch circuits required by other parts of this section, two or more 20-ampere small-appliance branch circuits shall be provided for all receptacle outlets specified by 210.52(B), except as modified in 210.52(B)(1).

Summary
The refrigerator can be on one of the two 20-amp small appliance circuits required for the kitchen, pantry, breakfast room, dining room, or similar area. This is permitted by NEC 210.52(B)(1).

In summary: While not strictly required to be on a dedicated circuit, refrigerators are intended to be on one of the two or more small appliance circuits, which effectively functions as a dedicated circuit because those circuits only serve the outlets specified in 210.52(B), which includes countertop outlets and refrigeration equipment outlets. Flag for review

Previous Question Next Question