Question: Does the NEC define this difference? Is 'ampacity' after derating factors? 'Allowable ampacities' are noted on the tables in Article 310... so that's before derating factors. I came across a thread where this was mentioned. Does the term 'ampacity' take derating factors into account, if derating is applicable?

You've hit on a subtle but important distinction in the NEC, and your understanding is mostly correct. Here's a breakdown of the terms and how they relate to derating: Ampacity (as defined in Article 100)

"The current, in amperes, that a conductor can carry continuously under the conditions of use without exceeding its temperature rating."

This is the BASE ampacity before any derating or correction factors are applied.
It's the
potential current-carrying capability based on the conductor's material, size, and insulation, assuming certain ideal conditions. Think of it as the conductor's "raw potential." Allowable Ampacities (as used in NEC Tables like 310.15(B)(16))

This refers to the ampacities listed in the tables in Article 310, specifically Tables 310.15(B)(16), 310.15(B)(17), etc. These tables give ampacities under specific, standardized conditions (e.g., not more than three current-carrying conductors in a raceway, ambient temperature of 30°C, etc.).

These table values are the starting point for your calculations, and you must adjust them if your actual installation conditions differ from the table assumptions.
Therefore, allowable ampacities are before any derating factors are applied. Ampacity (after derating)

This is the
actual current-carrying capacity of the conductor in your specific installation, after applying all applicable derating and correction factors. This is the usable ampacity you must compare against the load. This value must be used to ensure that the conductor is adequately sized for the applied load.

In summary


Look up the
allowable ampacity from the appropriate NEC table (e.g., Table 310.15(B)(16)) based on the conductor type and size.
2. Identify all applicable derating and correction factors. These can include: Ambient temperature correction

(e.g., Table 310.15(B)(16) notes below the table)

Number of current-carrying conductors in a raceway

(Table 310.15(C)(1))


Conduit fill

While not a derating factor in the same way as the above, it's related. Too much fill prevents proper heat dissipation, which can indirectly affect ampacity.

Other special conditions

(e.g., derating for specific types of equipment or environments)3.

Multiply the table value (allowable ampacity) by all applicable derating factors.
This gives you the ampacity after derating or, more accurately, the adjusted ampacity.4. Ensure the adjusted ampacity is greater than or equal to the calculated load current (with any applicable overcurrent protection sizing).Example

Let's say you have a 12 AWG THHN copper conductor and need to determine its ampacity in the following situation:
Ambient temperature: 40°C Number of current-carrying conductors in the same raceway: 61. From Table 310.15(B)(16), the allowable ampacity of 12 AWG THHN copper is 30 amps (for a 30°C ambient temperature).
2. Identify Derating Factors:


Temperature Correction

Table 310.15(B)(16) notes require a correction factor for ambient temperatures other than 30°C. For THHN copper at 40°C, the correction factor is 0.
87.


Number of Conductors

Table 310.15(C)(1) specifies derating factors based on the number of current-carrying conductors. For 6 conductors, the derating factor is 0.
80.3. Calculate Adjusted Ampacity:
Adjusted Ampacity = Allowable Ampacity Temperature Correction Number of Conductors Derating Adjusted Ampacity = 30 amps 0.87 0.80 = 20.88 amps4. Therefore, in this scenario, the 12 AWG THHN conductor, after applying the necessary derating factors, can only safely carry 20.88 amps. You would need to make sure your load does not exceed this, or increase conductor size, or reduce the number of conductors, etc.

Key Takeaway:
The term "ampacity" on its own generally refers to the inherent current-carrying capacity of a conductor before derating. The "allowable ampacities" in the tables are also before derating. It's crucial to understand that the usable ampacity is the ampacity after* applying all relevant derating and correction factors. Flag for review