Topic: corner grounded delta troubleshooting

User: chaoakax, Location: Los Angeles

Asked on: Tuesday, July 30, 2024 at 2:17 am EDT
Answered on: Thursday, March 6, 2025 at 12:26 am EST

Question: Hi everyone, I've been doing 99% residential electrical work, and recently decided to take upon a commercial job, which seemed like should have been easy enough but here comes:So its an old office building that has 200A 1ph, 120/240v main for the offices, and a separate 100A 3ph 3 wire 240V meter with a square D 3 phase disconnect right below it. Before using it, i measure the voltage and get:A to ground 240vB to ground 240VC to ground 0A to B 240VA to C 240vB to C 240vnever before having heard about corner grounded delta systems, i automatically assumed the C phase is dead from utility and called for them to check on it and proceeded to installing a 3PH sub panel with breaker main to feed single phase AC units. Clients wanted all mini splits and they are all single phase 30A units. So to picture the overall system, it is a Meter, with the 3ph disconnect at the bottom, feeding a 3ph 100 subpanel with a straight shot of 30ft of EMT conduit. Then from subpanel we fed the AC units with 30A breakers. Edison rep calls tells me that its a normal system and that is how it is supposed to be and it works fine. AC guy turns on 2 of the units and tries firing them up. Nothing happens. Checks at the subpanel on the 100A main breaker at the sub, says gets absolutely no voltages there, and cant get to the Square D 3ph disconnect to check on the fuses because they are locked. So i have to go there to check on it but i am out of ideas what could have gone wrong. On a side note, when i first opened the old 3 ph disconnect, i noticed that only A and B phases had fuses installed and C had nothing. Now, what could have gone wrong? Could it be that the C phase was tapped as neutral at the utility transformer? How should i proceed when troubleshooting this?I appreciate all the help i can get

Okay, this is a situation that definitely calls for a methodical approach. You've encountered a corner-grounded delta system, which can be confusing if you haven't worked with one before. Let's break down the situation and figure out how to proceed.

Understanding Corner-Grounded Delta How it works

In a corner-grounded delta system, one of the phase conductors (in your case, phase C) is intentionally connected to ground at the transformer. This phase becomes your "grounded conductor," effectively taking the place of a neutral in a more common system.


Voltage Readings

Your voltage readings are perfectly normal for this type of system: A to Ground: 240V B to Ground: 240V C to Ground: 0V (because C is ground) A to B: 240V A to C: 240V B to C: 240V

Why use it?
Corner-grounded delta systems are sometimes used in industrial settings. One reason is that they can offer some advantages in terms of fault tolerance and reduced harmonic distortion under certain conditions. They are less common than other systems.

Troubleshooting Steps

Given the information, here’s a plan of attack:1. The Locked Disconnect is Key

You
must get access to the Square D 3-phase disconnect immediately below the meter. This is your first point of failure. Request the client to open it up.

Safety First

Before opening any disconnect, ensure the power is off upstream (if possible) and use proper PPE (insulated gloves, eye protection). Test, test, test.2.

Inspect the Fuses in the Disconnect

This is critical.

Presence

You mentioned finding only A and B phases fused previously. Verify if this is still the case. A corner-grounded delta
can operate with only two fuses (as the grounded phase doesn't require overcurrent protection in many jurisdictions), but it's bad practice and potentially unsafe.

Fuse Rating

Check the fuse amperage rating. Are they appropriate for the 100A service?

Fuse Condition

Are any of the fuses blown? Use a multimeter in continuity mode to test each fuse individually
after removing them from the disconnect.

Replace if Needed

Replace any blown fuses with the correct amperage and voltage rating.

Even if fuses are good, replace them.
Sometimes fuses can look good but have an internal crack that will affect its operation.3. Voltage at the Disconnect (with power on)

If the fuses are intact (or after replacing any blown ones), re-energize the disconnect (carefully!) and measure the voltage at the load side of the disconnect, right where your conductors connect to go to the subpanel. You should get the same readings as you got at the meter (240V A-G, B-G, 0V C-G, 240V A-B, A-C, B-C).4.

Check Your Wiring and Connections



Conduit Run

You said a straight 30ft EMT run. Are there any signs of damage or pinching to the conduit? Could the conductors have been damaged during the pull? Extremely unlikely since you said voltage readings at the meter were good, but verify anyway.

Continuity Testing

With the power OFF at the Square D disconnect, use a multimeter in continuity mode to check the continuity of each conductor (A, B, and C) from the load side of the Square D disconnect all the way to the lugs in your 100A subpanel. You should have near-zero resistance on each conductor. Also check that all phases are not shorted to ground.


Proper Termination

At both the Square D disconnect and the 100A subpanel, carefully inspect that each conductor is properly terminated and tightened in its lug. Loose connections are a common cause of voltage drop and equipment failure. Make sure there is no corrosion on the wires and that the wires are properly seated in the lugs.

Grounding

Verify that your grounding conductor (equipment grounding conductor, EGC) is properly connected from the subpanel to the Square D disconnect enclosure and back to the grounding electrode system. This is essential for safety.5.

Voltage at the Subpanel (with Disconnect ON)

Once you've verified the wiring and connections, turn on the Square D disconnect. Now, measure the voltage
at the lugs of the 100A main breaker in your subpanel. You should get the same readings: A to Ground: 240V B to Ground: 240V C to Ground: 0V A to B: 240V A to C: 240V B to C: 240VIf you don't get these readings at the subpanel lugs, then you have a problem with the wiring between the Square D disconnect and the subpanel. Go back to step 4 and meticulously re-check everything.6.

Main Breaker in Subpanel



Is it ON?
Double-check that the 100A main breaker in your subpanel is actually switched ON. It sounds obvious, but it's easily overlooked. Voltage on Load Side

With the 100A breaker ON, measure the voltage on the load side of the breaker (the terminals that feed the individual 30A breakers). You should have the same voltage readings as the line side. If you have voltage on the line side but
not the load side of the breaker, the breaker is faulty and needs to be replaced.7.

Mini-Split Wiring and Configuration



Voltage at Mini-Splits

Now that you've verified power is getting to the subpanel and through the breakers, go to each mini-split location and measure the voltage at the mini-split's connection point. You should have 240V between A and B.

Correct Wiring

Make absolutely sure that each mini-split unit is wired correctly for 240V. The wiring diagrams are usually on the unit itself or in the installation manual. Typically, this involves connecting two hots (A and B in your case) and a ground. DO NOT CONNECT TO THE GROUNDED PHASE (C).

Important Considerations
Code Compliance

Corner-grounded delta systems have specific requirements in the National Electrical Code (NEC). Ensure that your installation is compliant, especially regarding grounding, overcurrent protection, and conductor identification. Consult with a qualified electrical inspector.

Neutral

Remember,
you do not have a neutral in the conventional sense. The grounded phase (C) is not a neutral and should not be used as such. It’s a ground. If any equipment requires a neutral (120V), you cannot supply it from this 240V corner-grounded delta system without using a step-down transformer. Your mini-splits should not require a neutral if they are 240V units.

3-Phase Loads

Verify the mini-splits do not require a 3-phase power source. If so, they cannot be connected to the system.

Addressing Your Specific Questions
"Could it be that the C phase was tapped as neutral at the utility transformer?" Yes, that is exactly what is happening in a corner-grounded delta system. The C phase is the grounded conductor, essentially taking the place of a neutral. But, as noted above, you can't just treat it as a neutral. "How should I proceed when troubleshooting this?" Follow the steps outlined above. Start with the disconnect, verify voltage and wiring at each point in the system, and ensure that all equipment is wired correctly.

Summary

The most likely causes are:1. Blown Fuse(s) in the Square D Disconnect

This is the first place to check.2.

Loose Connection

Could be at the Square D disconnect, the subpanel, or even at the mini-split units.3.

Faulty Main Breaker in Subpanel

Possible, but less likely.

A Word of Caution:


Working with electrical systems can be dangerous. If you're not comfortable performing these troubleshooting steps or if you encounter any conditions you don't understand, stop and consult with a qualified and licensed electrician who is familiar with corner-grounded delta systems. It's always better to be safe than sorry. Flag for review