Topic: Siemens LI and LSI trip units swap.

User: 82angelfan, Location: Hesperia, Ca

Asked on: Tuesday, July 30, 2024 at 8:53 am EDT
Answered on: Thursday, March 6, 2025 at 12:27 am EST

Question: Can I swap trip units?Looking for some information. I have installed Siemens FG250A frames in hospital ER existing main distribution boards. Breakers were provided by owner. The trip units in the breakers are LSI model 555. The one-line and the coordinated study show LI model 555 trip units. One is 100amps the other is 150amps. The issue at hand is that the dial settings do not match the coordinated study and sense this is an OSHPD job we cannot get the TIO signed off.Is it possible to change the trip units without removing the breaker from the gear. I'm trying to avoid multiple shut downs.

Let's break down your situation and address the feasibility of swapping trip units in your Siemens FG250A breakers.

Understanding the Issue



Mismatch

You have LSI trip units installed, but the design calls for LI trip units. This is a critical difference, especially regarding coordination studies and OSHPD approval.


LSI vs. LI



LI

Long Time and Instantaneous protection only.


LSI

Long Time, Short Time, and Instantaneous protection. The Short Time feature adds complexity and another layer of coordination that needs to be accounted for.

OSHPOD Significance

OSHPD (California's Office of Statewide Health Planning and Development) has strict requirements for healthcare facility electrical systems, including coordination studies, to ensure reliability and safety. Discrepancies can definitely hold up sign-off.


Shutdown Aversion

Minimizing shutdowns in a hospital ER environment is paramount.

Can You Swap Trip Units In-Place?
General Feasibility



It
may be possible to change the trip units in-place, but this is highly dependent on the specific Siemens breaker model, trip unit design, and clearance within the switchboard. Many Siemens breakers have modular trip units designed for replacement. However, you MUST verify this. Crucial Considerations and Caveats


Siemens Documentation is King



Before anything, consult the Siemens breaker's instruction manual and any available documentation for the specific FG250A frame and 555 trip unit family.
This documentation will explicitly state if in-place trip unit replacement is an approved procedure and provide detailed instructions. Look for sections on "Maintenance," "Upgrading," or "Trip Unit Replacement."2. Safety First (De-energization)

Even if the documentation suggests in-place replacement,

best practice and probably OSHPD requirements demand de-energizing the breaker before working on it.
Working on a live medium-voltage breaker is incredibly dangerous and likely violates safety regulations. While you're trying to avoid a full shutdown, a controlled, planned shutdown is still necessary.3. Clearance and Accessibility

Assess whether you have sufficient physical clearance within the switchboard to access the trip unit, remove it, and install the new one without obstruction.4.

Trip Unit Compatibility

Ensure the replacement LI trip units (100A and 150A) are the

exact
replacements specified for the FG250A frame. Part numbers must match! Just because it's "LI Model 555" doesn't guarantee direct compatibility.5. Qualified Personnel

This work

must
be performed by qualified and experienced electrical personnel familiar with Siemens breakers and safety procedures.6. Torque Specifications

Pay very close attention to any torque specifications for the trip unit mounting screws/hardware.7.

Testing After Replacement

After replacing the trip units, thorough testing is mandatory. This includes:

Visual Inspection

Double-check all connections and mounting.


Functional Testing

Verify that the Long Time and Instantaneous trip functions operate correctly. Ideally, use a primary injection test set to simulate fault conditions.

Record Keeping

Document the trip unit replacement (serial numbers of old and new units) and the testing results.

Recommended Course of Action


Contact Siemens Directly

This is your BEST first step. Contact Siemens Technical Support with the breaker model number, trip unit information, and your situation. They can provide definitive guidance on in-place replacement feasibility, compatible trip unit part numbers, and any specific instructions or warnings.2.

Review the One-Line and Coordination Study

Before making any changes, double-check the original one-line diagram and coordination study. Confirm that LI trip units are indeed the correct specification. There is the slightest chance that the breakers were ordered incorrectly, or the one-line is wrong.3.

Develop a Detailed Shutdown Plan

Assume a shutdown will be required. Create a detailed plan that minimizes the impact on the ER. Consider:


Timing

Schedule the work during off-peak hours, if possible.

Backup Power

Ensure backup power systems are fully operational and tested.


Communication

Communicate the planned shutdown clearly to hospital staff.4.

Acquire Correct Trip Units

Order the correct Siemens LI trip units (100A and 150A) with the correct part numbers based on Siemens' guidance.5.

Perform the Trip Unit Replacement (with Shutdown)

Follow Siemens' instructions meticulously.6.

Thorough Testing and Documentation

As outlined above.7.

Update Coordination Study (if necessary)

If the trip unit changes affect the coordination curves significantly, you might need to update the coordination study.8.

Resubmit for OSHPD Approval

Provide all documentation, including the updated coordination study (if needed), to OSHPD for review and approval.

Why the LSI Units Might Have Been Used (Speculation)



Availability

The LSI units may have been more readily available at the time of installation.


Cost

LSI units might have been slightly cheaper, but this is unlikely given the overall project cost.

Misunderstanding

Someone may have incorrectly assumed that LSI units were a suitable substitute for LI units.

In summary, while in-place trip unit replacement
might* be possible, it is not guaranteed and depends heavily on the specific Siemens equipment and safety considerations. Contacting Siemens, thorough planning, and a controlled shutdown are crucial to ensuring a safe and compliant solution for your OSHPD project.