Question: I am receiving conflicting opinions regarding if additional protection is needed on the motor below. These have EGCs that run with the circuit conductors from the MCCs. A QAQC is saying that NEC requirements are not met and that the motor frames are likely isolated from that steel plate due to the paint. One engineer is saying that the EGC is the only requirement, and that the motors are bonded through the bolts. Another engineer agrees with the QA saying that specific grounding bolts would need to be used.These motors are on modules which have a bus bars that ties into the plant's ground system.I am trying to understand this issue better. Is the frame of a motor protected via the EGC?
Let's break down the grounding requirements for motors, the different opinions you're receiving, and what the NEC generally requires in this situation
Understanding the Core Principles:
Purpose of Grounding
The primary goal of grounding (more accurately, "equipment grounding") is to provide a low-impedance path back to the source of power. This path allows a fault current (e.g., a short circuit from a live conductor to the motor frame) to quickly trip a circuit breaker or blow a fuse, minimizing the risk of electric shock and fire.
Equipment Grounding Conductor (EGC)
The EGC is the dedicated conductor (wire or metallic raceway) run with the circuit conductors and connected to all non-current-carrying metal parts of the electrical system. It's intended to carry fault current back to the source.
Bonding
Bonding connects non-current-carrying metal parts together to create a continuous, low-impedance path. This ensures that if a fault occurs, all connected metal parts are at approximately the same potential, reducing touch voltage and shock hazards.
Addressing the Conflicting Opinions
Engineer #1 (EGC is enough, motors bonded through bolts)
This is a common, and sometimes acceptable, assumption, BUT it's highly dependent on the specific installation and the integrity of the bolted connections. The NEC generally doesn't explicitly prohibit relying on bolted connections if they meet specific criteria (see below), but good engineering practice often calls for more positive grounding.
QA/QC (NEC not met, frames likely isolated, grounding bolts needed)
This viewpoint is more conservative and aligns with best practices for ensuring reliable grounding. The QA/QC concern about paint isolating the motor frame is valid. Paint and corrosion can significantly increase the impedance of bolted connections, making them unreliable for carrying fault current.
Engineer #2 (Agrees with QA, specific grounding bolts needed)
This is a safer approach. "Grounding bolts" often refer to bolts designed to penetrate paint and corrosion and provide a good electrical connection. They often have star washers or serrated surfaces to bite into the metal.
NEC Considerations
NEC 250.4(A)(3)
"Electrical equipment that is required to be grounded shall be connected to the grounding electrode system in a manner that creates a low-impedance ground-fault current path." This is the fundamental principle.
NEC 250.8 (Connection of Grounding and Bonding Equipment)
This section outlines the acceptable methods for connecting grounding and bonding conductors. It includes things like listed pressure connectors, terminal bars, exothermic welding, etc. It DOES NOT explicitly forbid relying on bolted connections under all circumstances, but the quality of the connection is key.
NEC 430.141 (Grounding Motor Frames)
This section specifically addresses grounding of motor frames. It doesn't mandate how to ground the frame, but it clearly requires it to be grounded.
Important Considerations
Vibration
Motors vibrate. Bolted connections can loosen over time, increasing impedance.
Corrosion
Corrosion can form between bolted surfaces, further degrading the connection.
Paint
Paint is an insulator. A thin layer of paint can significantly impede the flow of current.
Listing/Labeling
Motors are generally not listed and labeled to have the metal mounting feet be the only means for grounding.
Your Situation (Motors on Modules with Bus Bars)
The fact that the modules have bus bars tied into the plant's ground system is a positive factor. However, it doesn't automatically solve the problem of grounding each individual motor frame. You need to ensure that the path from the motor frame to that ground bus bar is low impedance and reliable.
Recommended Actions
Evaluate Bolted Connections
Inspect
Are the bolts clean, tight, and corrosion-free? Are they specifically designed for grounding (grounding bolts with star washers or serrated surfaces)?
Test (If Possible)
Use a low-resistance ohmmeter (micro-ohmmeter) to measure the resistance between the motor frame and a known good ground point (like the module's ground bus bar). The resistance should be very low (fractions of an ohm). High resistance indicates a poor connection.2.
Consider Supplemental Grounding
Dedicated Grounding Conductor
The best solution is often to install a dedicated grounding conductor (e.g., a green insulated wire) from a grounding lug on the motor frame to the module's ground bus bar. This provides a positive, low-impedance path, regardless of the integrity of the bolted connections. Use a listed grounding lug suitable for the wire size and application.
Grounding Bolts with Star Washers
If you must rely on bolted connections, use grounding bolts with star washers or serrated surfaces. Clean the mating surfaces of paint and corrosion before installation. Coat with an anti-oxidation compound to prevent corrosion.3.
Document the Grounding System
Maintain detailed documentation of the grounding system, including: Grounding methods used for each motor. Inspection and testing procedures.* Resistance measurements (if performed).4.
Consult with a Qualified Electrical Engineer
Given the conflicting opinions and the potential safety implications, it's wise to consult with a qualified electrical engineer who can review the specific installation and make recommendations based on a thorough assessment.5.
Prioritize Safety
Err on the side of caution. A robust and redundant grounding system is always preferable.
In Summary:
While the EGC is a necessary component of the grounding system, it may not be sufficient on its own to ensure reliable grounding of the motor frame, especially if relying on bolted connections that might be compromised by paint, corrosion, or vibration. Implementing supplemental grounding measures, such as dedicated grounding conductors, is a best practice that enhances safety and reliability. Consult with a qualified engineer to determine the best approach for your specific installation. Flag for review