User: JD_2207, Location: Massachest
Asked on: Tuesday, July 30, 2024 at 9:17 am EDT
Answered on: Thursday, March 6, 2025 at 12:27 am EST
Question: According toNec 210.18Can I run an SER cable 4/0From basementFrom an 100amp breaker[Meter socket breaker]To 3rd floorLand on an panelboard150amp /main lug
Let's break down NEC 210.18 and the implications for your proposed SER cable run.
NEC 210.18 is about Branch-Circuit Overcurrent Protection
This section primarily concerns the rating of overcurrent devices (breakers or fuses) protecting individual branch circuits feeding loads. It's not directly related to feeder sizing or the general rules for running SER cable.
The real issue is Feeder Sizing and Overcurrent Protection based on the load.
Here's a breakdown of the factors you need to consider:1. Ampacity of 4/0 SER
The ampacity of 4/0 SER cable depends on the conductor material (Copper or Aluminum) and the temperature rating. Assuming it's rated for 75 degrees (most common and typical limit) and for copper wire, it is typically rated for 180 amps.2.
100 Amp Breaker
You are running a 100 amp breaker in your meter socket. The cable ampacity must be equal or greater.3.
Panelboard Rating
The 150 amp rating of the panelboard on the 3rd floor is the maximum current it can safely handle. It doesn't dictate the required ampacity of the feeder cable. This is a main lug panel which means it requires an overcurrent protection device.4.
Load Calculation - MOST IMPORTANT
You must perform a load calculation (NEC Article 220) to determine the actual load the 3rd floor panel will serve. This includes lighting, receptacles, appliances, and any other equipment that will be connected. This will give you the minimum ampacity required for the feeder.5.
Feeder Overcurrent Protection (Crucial)
The overcurrent protection device (your breaker in the meter socket) must protect the feeder cable. It cannot be larger than the ampacity of the cable, unless certain exceptions apply (e.g., the next higher standard breaker size may be allowed in some cases if the calculated load doesn't perfectly match a standard breaker size, but this is rare for a whole panel feeder and needs careful calculation and justification per NEC).- If your load calculation is 100 amps or less, the 100 amp breaker in the meter socket is suitable.- If your load calculation is significantly higher (e.g., close to 180 amps) a larger feeder cable would be needed to be properly protected.6.
Voltage Drop
Long cable runs can experience voltage drop, which affects the performance of equipment and can be a code violation (NEC 210.19(A)(1) FPN No. 4 and 215.2(A)(1) FPN No. 2). Voltage drop should be considered, especially on longer runs, and can necessitate using a larger conductor size than strictly required by the load calculation.
In Summary and Recommendations1. Load Calculation is Mandatory
Perform a thorough load calculation per NEC Article 220 before doing anything else.2.
Cable Ampacity vs. Breaker Size
The 4/0 SER cable might be acceptable if your calculated load is less than 100 amps and the breaker is sized appropriately. However, the breaker size should never exceed the cable ampacity.3.
Voltage Drop Check
Check for voltage drop, especially with a run to the 3rd floor. It might push you to a larger conductor size.4.
Consider Future Loads
Think about potential future loads (e.g., adding an air conditioner, electric car charger, etc.). It's often wise to upsize the feeder to accommodate future needs.5.
Consult a Qualified Electrician
This is critical. Electrical work can be dangerous and must comply with local codes and the NEC. A qualified electrician can perform the load calculation, assess the existing conditions, and ensure the installation is safe and code-compliant.
Example
Let us say after completing your load calculation for the 3rd floor the load is 80 amps. In this case, the 4/0 SER cable would be acceptable and protected by a 100 amp breaker.
Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. This information is for general guidance only. Always consult with a licensed and qualified electrician for any electrical work. Failure to do so could result in fire, electric shock, or code violations. Flag for review