User: Squiggy969, Location: PA
Asked on: Tuesday, July 30, 2024 at 10:15 am EDT
Answered on: Thursday, March 6, 2025 at 12:27 am EST
Question: Is it legal to feed a 150 amp panel with a 200 amp service rated ATS. Contractor is using 4/0 SER so the wire is protected correctly but assuming the panel is reated for 150 amps is it legal? And if so could you do the same for a 100 amp panel.
Yes, it is generally legal to feed a 150 amp panel with a 200 amp service-rated ATS, and similarly, a 100 amp panel with a 200 amp service-rated ATS, provided all other code requirements are met. Here's a breakdown of why, and the key considerations
Why It's Generally Legal (but with caveats):
ATS as a Switching Device, Not Overcurrent Protection
The ATS is primarily a
switching device, not an overcurrent protection device. Its purpose is to transfer the load between the utility and generator sources. It doesn't inherently dictate the ampacity of the downstream panel. Panel Rating
The panel rating is the maximum amount of current that panel is designed to handle safely. As long as the overcurrent protection feeding the panel (in this case the generator breaker that is feeding the ATS) is sized appropriately, you can feed that panel with a panel or ATS that is rated for more.
Overcurrent Protection is Key
The critical factor is the
overcurrent protection (circuit breaker or fuses) on the generator powering the ATS. This must be sized correctly to protect the 4/0 SER Cable AND to not exceed the panel's rating. Conductor Ampacity
The 4/0 SER is sized correctly to handle the rated amps of the ATS.
How to Ensure Legality and Safety
Overcurrent Protection
The crucial point. The overcurrent protection device protecting the 4/0 SER cable feeding the panel from the generator must be 150 Amps or less for the 150 amp panel and 100 amps or less for the 100 amp panel. This is essential to protect the panel from being overloaded and possibly starting a fire.2.
Load Calculation
Verify that the calculated load on the panel does not exceed 80% of the panel's rating. This is a common practice to avoid nuisance tripping and ensure sufficient capacity for future expansion.3.
Proper Installation
All components (ATS, conductors, panel, grounding) must be installed according to the National Electrical Code (NEC) and any local codes.4.
Wire Size
Ensure that the conductors from the ATS to the panel are appropriately sized for the load and the overcurrent protection. 4/0 SER is appropriate for 150A, 125A or 100A but the lower the breaker that protects it, the better.5.
Grounding
Proper grounding is critical for safety. The system must be properly grounded according to NEC Article 250.
Example: 150 Amp Panel with 200 Amp ATS Use 4/0 SER copper cable (rated for 150 amps depending on temperature rating). Install a 150 amp circuit breaker on the generator feeding the ATS. This breaker is the overcurrent protection for the 4/0 SER feeding the 150 amp panel.
Example: 100 Amp Panel with 200 Amp ATS Use appropriately sized conductors (e.g., #3 copper THHN, or larger depending on the installation method). Determine correct conductor size based on ampacity tables in the NEC. Install a 100 amp circuit breaker on the generator feeding the ATS. This breaker is the overcurrent protection for the SER cable feeding the 100 amp panel.
Important Considerations
Local Codes and AHJ (Authority Having Jurisdiction)
Always consult with your local electrical inspector and AHJ. They have the final say on what is permitted in your area. Local codes may have more restrictive requirements.
ATS Manufacturer's Instructions
Follow the manufacturer's instructions for the ATS installation.
Future Expansion
While it's generally permissible, consider if future expansion of the load on the panel is likely. If so, a larger panel (e.g., a 200 amp panel) might be a better long-term solution (but still requires proper overcurrent protection).
In Summary:
You can legally use a 200 amp service-rated ATS to feed a 150 amp or 100 amp panel, but only if* the overcurrent protection (breaker) on the generator feeding the ATS is sized appropriately to protect the panel and conductors. Proper installation, grounding, and adherence to all NEC and local codes are mandatory. Always consult with a qualified electrician and the local AHJ to ensure compliance. Flag for review