User: Moistness, Location: PA
Asked on: Tuesday, July 30, 2024 at 10:24 am EDT
Answered on: Thursday, March 6, 2025 at 12:28 am EST
Question: I have a question that every time I think I know the answer, I read or watch a video that makes me doubt myself.On a service, residential or industrial, the conductors that pass through the meter now need to enter a "disconnect" outside of the home or building.My question is, the bounding jumper that bounds the neutral to ground, does this happen in the disconnect outside of the home and thus the neutral and ground will need to be separated from that point on or do you also tie the neutral and ground together say in a lighting panel that this disconnect is feeding, that before this new code came down, was your service disconnect and where the bonding jumper bonded the neutral to ground?Another question, does this "disconnect" need to have over current protection, or can it just be non-fused?If true, do you even bond the neutral in the disconnect or do you keep them separate until you land on the first over current protected device?If you can point me to the NEC for the answer it would be much appreciated.Thank you.
Okay, this is a common area of confusion, and you're right to be careful. Here's the breakdown based on the NEC, aiming to clarify the bonding and grounding requirements when you have an outdoor service disconnect
Key Concepts and NEC References:
Service Disconnect
The main switch or breaker that disconnects the entire building from the utility power.
Service Entrance Conductors
The conductors from the utility's point of connection to the service disconnect.
Grounding Electrode Conductor (GEC)
The conductor that connects the service equipment (usually the neutral bus) to the grounding electrode system (ground rods, water pipe, etc.).
Main Bonding Jumper (MBJ)
The connection between the grounded (neutral) conductor and the equipment grounding conductor (ground bus) at the service equipment.
Separately Derived System
A power source (like a generator or transformer) that is electrically isolated from the utility supply and requires its own bonding and grounding.
Your Specific Questions Addressed
Bonding Jumper Location (Neutral to Ground)
The main bonding jumper MUST be located at the service disconnect. With an outside disconnect, this means the bonding jumper is located in the outside disconnect enclosure. This is absolutely critical. See NEC 250.24(C) and 250.
28. Therefore, the neutral and ground conductors MUST be separated after the outdoor disconnect. This means that in your example, you would not bond the neutral and ground together again in the lighting panel fed from the outside disconnect. Why is this important? Bonding the neutral and ground at multiple points creates parallel paths for neutral current. This can lead to circulating currents on the grounding system, causing nuisance tripping, voltage drops, and potentially dangerous conditions.2. Overcurrent Protection in the Outdoor Disconnect
The NEC requires overcurrent protection at the service disconnect. NEC 230.91 states "Service overcurrent devices shall be an integral part of the service disconnecting means or shall be located immediately adjacent thereto." This means a fused disconnect or a circuit breaker. A non-fused disconnect is not sufficient for a service disconnect.3. Bonding in the Disconnect (Revisited)
Yes, you
MUST bond the neutral and ground in the disconnect enclosure via the main bonding jumper. This is where the neutral conductor is connected to the equipment grounding bus, which is connected to the enclosure and the grounding electrode conductor (GEC). From the disconnect onwards, the neutral (grounded conductor) and equipment grounding conductors are kept separate. The neutral goes to the neutral bus in the downstream panel, and the equipment grounding conductors are connected to the ground bus.
Summarized Steps
Outdoor Disconnect
Install an overcurrent-protected disconnect (fused disconnect or circuit breaker). Bring the service entrance conductors (hot, neutral) from the meter to the disconnect. Bring the grounding electrode conductor (GEC) to the disconnect.
Install the main bonding jumper (MBJ) inside the disconnect enclosure, bonding the neutral to the ground. Connect the GEC to the ground bus in the disconnect.2. From the Disconnect to the Downstream Panel (e.g., Lighting Panel)
Run a feeder (hot conductors, neutral, and equipment grounding conductor) from the disconnect to the downstream panel.
Keep the neutral and ground conductors separate from this point on. In the downstream panel: Connect the hot conductors to the breakers. Connect the neutral to the neutral bus. Connect the equipment grounding conductor to the ground bus.
Important Considerations
Local Amendments
Always check with your local authority having jurisdiction (AHJ) for any local amendments or interpretations of the NEC.
Proper Sizing
Ensure all conductors (service entrance, feeders, GEC, etc.) are properly sized according to the NEC. (See Article 310).
Grounding Electrode System
Make sure your grounding electrode system is adequate. (See Article 250, Part III).
UL Listing
Use UL-listed equipment for your service disconnect and panels.
Example
Imagine the service conductors come into a 200A fused disconnect mounted outside your house.1. Inside the disconnect: The neutral from the meter lands on a neutral bus. The equipment grounding conductors are connected to a grounding bus.
A thick copper strap (the main bonding jumper) connects the neutral bus to the grounding bus inside the disconnect. The grounding electrode conductor (from your ground rods) is connected to the grounding bus. 200A fuses protect the hot legs.2. From the disconnect to the main panel inside the house: A 200A-rated feeder (two hots, a neutral, and a separate ground wire) runs to the panel. Inside the main panel: The hots connect to the main breaker. The neutral connects to the neutral bus (which is isolated from the enclosure). The ground wire connects to the ground bus (which is bonded to the enclosure).
In Summary:
The key to getting this right is to understand that the bonding of the neutral and ground happens only once* at the service disconnect (in your case, the outdoor disconnect). From there, you treat the downstream panel as a subpanel, keeping the neutral and ground separate.Always consult the current edition of the NEC and local codes, and when in doubt, consult with a qualified electrician. This information is for educational purposes and should not be considered a substitute for professional advice. Good luck! Flag for review