Question: Does NEC allow surface mounting the main disconnect on outside of mobile home?I have a 200A main disconnect that feeds 4/0 -4 wire to the main panel in a mobile home. The panel is pole mounted, feed over head and conduited to the mobile and of course it's right where I want to put a garage/carport. The mobile is on a permanent block foundation but I don't think it's registered with the state (no 433A/B with CA) so it's still considered a mobile home by the state. Exterior walls are 1/4" concrete board siding (not sheet metal).Does code allow for the panel to be moved on to the mobile home and surface mounted, feed under ground from the utility and then move existing mobile home feed to come from new location? And is it under 550.xx?If it's against code, how close to the mobile home can I put a "Free Standing" panel mount per code?P.S. How do you post/load photos, tried but it wouldn't take a flicker link.
Let's break down the situation and address your questions.
NEC and Mobile Home Disconnects NEC 550.32(A) Location Generally, the NEC requires the main disconnect for a mobile home to be located either inside the mobile home or adjacent to it. Adjacent Definition
"Adjacent" isn't strictly defined in the NEC, but the general interpretation is within sight and readily accessible. Typically, this means within 30 feet and on the same premises.
Exterior Mounting
Mounting the disconnect directly on the exterior of the mobile home is generally permissible under the NEC,
as long as it meets all other applicable requirements.Specific Considerations for Your Situation1. Is the Mobile Home Legally a "Mobile Home"? This is crucial. Even with a block foundation, if it's legally still classified as a mobile home by your state (and you say it is), NEC Article 550 applies. The lack of a 433A/B in CA reinforces this.2. Your Proposed Solution
Moving the Disconnect to the Mobile Home
This is potentially acceptable if you meet the NEC requirements for mounting and wiring. You need to ensure the disconnect is rated for outdoor use, properly grounded, and the wiring is protected. It also need to meet the working space requirements of 110.26.
Underground Feed
An underground feed from the utility to the disconnect on the mobile home is fine, provided it meets NEC Article 300 requirements for underground installations (burial depth, conduit type, etc.).
Moving the Existing Feed
Moving the feed that currently goes from the pole to the mobile home to now come from the new disconnect location on the mobile home is electrically sound, as long as you use appropriate wiring methods and ampacity.3.
Important Considerations for Surface Mounting on the Mobile Home
Structural Integrity
Ensure the exterior wall of the mobile home can structurally support the weight of the disconnect enclosure. The concrete board might be sufficient, but you need to evaluate it. You might need to add internal reinforcement to the wall.
Wiring Methods
Ensure the wiring methods used for both the incoming utility feed and the outgoing feed to the mobile home's internal panel are appropriate for the environment (outdoor, potentially wet) and comply with the NEC. Use the appropriate conduit, fittings, and weatherproof boxes as needed.
Working Space
NEC 110.26 requires adequate working space around electrical equipment. Make sure there is enough clearance in front of the disconnect for safe operation and maintenance.
Height
Check local codes or the utility for any requirements on the mounting height of the disconnect.
Grounding
Proper grounding is absolutely critical. The disconnect must be effectively grounded, and the mobile home's grounding system must be properly bonded to the disconnect. Refer to NEC Article 250.
If Moving to the Mobile Home is Against Code (Less Likely but Possible)
If, for some reason, local inspectors interpret the NEC in a way that prohibits mounting on the mobile home (perhaps due to perceived structural concerns or other local rules), the alternative is a
free-standing disconnect. Distance
The NEC doesn't specify a minimum distance from the mobile home for a free-standing disconnect. The key is that it be "adjacent" and "readily accessible." Reasonable interpretations usually keep it within 30 feet.
Mounting
It would need to be mounted on a suitable pole, post, or pedestal that is properly anchored in the ground.
Wiring
You'd still need to run the service entrance conductors from the utility to the free-standing disconnect and then to the mobile home's internal panel, using approved wiring methods.
Key Steps to Take
Consult with Your Local Electrical Inspector
This is the most important step. They have the final say on code interpretation and local amendments. Show them your plan and get their feedback before you start any work. Their interpretation prevails.2.
Check with the Utility Company
They may have specific requirements for the service entrance location and metering.3.
Licensed Electrical Contractor
Seriously consider hiring a licensed electrical contractor to perform the work. They are familiar with the NEC and local codes and can ensure the installation is safe and compliant. They will also be able to pull the necessary permits.
Photo Uploading
Unfortunately, direct photo uploading to this forum is not supported. You would need to use a third-party image hosting service (like Imgur, or similar) and then link to the image in your post using markdown:
In Summary