Topic: How is the meter itself grounded for ring type meter sockets

User: electro486, Location: USA

Asked on: Tuesday, July 30, 2024 at 1:27 pm EDT
Answered on: Thursday, March 6, 2025 at 12:28 am EST

Question: Hello quick practical question for you all that have experience installing meters,For a plug-in type ANSI C12 Form 2S Class 200 meter (typical 200A meter for Form 2S meter sockets in North America) how does the meter itself get grounded? For most meters, I see a horizontal busbar/grounding terminal on the back of the meter at the midline. For ringless meter sockets, I typically see rings (see picture) or terminals around the left and right sides such that the meter's grounding terminal would contact this when inserted. However, for a ring type meter sockets (see example) they don't have these internal grounding rings and the meter's grounding terminal (aka surge relief gap?) looks like it makes contact with the ringed panel (which is painted) rather than any grounding terminal inside the meter socket. ANSI C12.7 does specify that "in sockets of all types, means shall be provided for grounding the surge relief gaps of the watthour meter" so they must have a grounding means, but not sure if that would just be a grounding screw or if the intention is one takes off paint at the appropriate location on the ringed cover or something.Can anyone shed light on how a Form 2S meter is intended to be grounded when installed in a ring type meter socket?Thanks for the help!

You've hit on a very common point of confusion and a detail often overlooked. You're right to question how effective that grounding contact is through paint. Here's the breakdown of how Form 2S meters are grounded in ring-type sockets, and the best practices

The Intended Method (and its Shortcomings):
Contact with the Ringed Cover

As you've correctly observed, the intended grounding method
is for the meter's grounding terminal (the horizontal bar/gap on the back) to make contact with the ringed cover of the meter socket. This is how the surge relief gap is meant to be grounded.

Relying on the Ring's Grounding

The effectiveness of this method heavily relies on the ring itself being reliably bonded to the meter enclosure, which should be grounded to the electrical service's grounding electrode system.

The Problem: Paint & Corrosion



Paint as an Insulator

The biggest problem, as you identified, is that paint is an insulator. Contact through painted surfaces provides very little ground-fault path. Even a thin layer of paint significantly increases resistance.


Corrosion Over Time

Over time, corrosion can further degrade the electrical contact between the meter's grounding bar and the ringed cover. This increases resistance and reduces the effectiveness of the ground path.

Best Practices for Reliable Grounding

Here's how to ensure proper grounding, overcoming the limitations of the standard installation:1.

Scrape Paint (Essential)

Before installing the meter,

always scrape away paint from the area on the ringed cover where the meter's grounding bar will make contact.
Use a wire brush, knife, or sandpaper to expose bare metal. Make sure the area is at least as large as the meter's grounding bar.2. Anti-Oxidant Compound

Apply an anti-oxidant compound (like No-Ox-Id or Penetrox) to the exposed metal on the ringed cover before installing the meter. This will help prevent corrosion and maintain a good electrical connection.3.

Verify Enclosure Grounding

Critically, verify that the meter socket enclosure is properly bonded to the service's grounding electrode system. Check the grounding conductor connection inside the meter socket enclosure. This connection is what actually provides the low-impedance path back to the source, completing the ground fault circuit.4.

Optional: Add a Grounding Jumper (Best Practice)

For the most reliable grounding, consider adding a short grounding jumper wire between the meter's grounding terminal (the horizontal bar) and a dedicated grounding point inside the meter socket enclosure (i.e. the equipment grounding conductor termination point). This bypasses the reliance on the ringed cover altogether.

Caution

This might not be allowed by the utility in some areas, so check with your local utility before adding the jumper. If allowed, use appropriate sized stranded copper grounding conductor with a lug for the meter and appropriate lug for the grounding termination point.

Important Considerations



Local Codes and Utility Requirements

Always follow local electrical codes and the requirements of your local utility company. They may have specific rules or preferred methods for grounding meters.

Safety First

De-energize the circuit before working on the meter socket. Work should only be performed by qualified electricians.


Inspection

During routine maintenance, inspect the grounding connection to ensure it is still clean and tight. Reapply anti-oxidant compound as needed.

Ringless vs. Ring-Type

The ringless style with the grounding rings is definitely a more robust and reliable grounding method than the reliance on ringed covers.

In summary, while the
intended grounding method for Form 2S meters in ring-type sockets is contact with the ringed cover, the practical* and safe approach is to scrape paint, use anti-oxidant compound, verify enclosure grounding, and ideally, add a grounding jumper if allowed.
Proper grounding is critical for safety and protecting equipment from voltage surges. Flag for review