Topic: NEC 220.82 and 220.84

User: abmorse1, Location: Tulsa, OK

Asked on: Tuesday, July 30, 2024 at 1:58 pm EDT
Answered on: Thursday, March 6, 2025 at 12:28 am EST

Question: Hi all - PE here, but I mostly do commercial work. In the rare occasion I've done residential, I've been using a spreadsheet that works through 220.82 and 220.84 load calculations that was developed by the Sr. Engineer I worked under when I started. He's since retired, but he's an incredibly smart guy with a wealth of experience. I'm not sure if I've found an error in his formulae or if I'm not reading code properly and thought I'd ask here.The way I'm reading the multifamily dwelling calculations, and yes they have fixed electric cooking and HVACTo simplify, I'm ignoring a few items just for this post:*heat pumps, but the way I'm reading it, I'm not sure how to deal with them in 220.84 either*house panel loadsPer 220.82 - to size individual unit panels and feeders:3W/sq ft2 Appliance circuits (1500VA each)1 Laundry circuit (1500VA)Dryer (actual load)other fixed appliances (dishwasher, disposal, etc)Subtotal is 100% of the first 10K VA and 40% of the rest.Added on is largest of:100% of HVAC Cooling65% of HVAC Heating (unless more than 4 heating units)Per 220.84 to size the service to the meter banks:3W/sq ft2 Appliance circuits (1500VA each)1 Laundry circuit (1500VA)Dryer (actual load)other fixed appliances (dishwasher, disposal, etc)Subtotal is 100% of the above.Added on is largest of:100% of HVAC Cooling100% of HVAC Heating (unless more than 4 heating units)That total is multiplied by unit quantity and the factor in table 220.84The spreadsheet I got from the retired Sr. Engineer simply takes the total from 220.82 and multiplies it by the factor in table 220.84 to size the service. Am I reading the code wrong, or has there been an error in the spreadsheet all this time?

You've highlighted a crucial difference between individual dwelling unit load calculations and service load calculations for multifamily dwellings, and your analysis is correct: the spreadsheet appears to be in error.Here's a breakdown to confirm your understanding

Individual Dwelling Unit (220.82)
You're correct in your method for calculating the load of each individual unit. The key takeaway is that you apply the 100%/40% demand factor to the general loads before considering heating and cooling loads. This reduces the load used to calculate the panel size of each unit. The "largest of" heating or cooling is applied after the general lighting and appliance load is calculated, but still helps reduce the overall load on each panel.

Multifamily Service (220.84)
The crucial difference, as you've identified, is that 220.84 requires you to calculate the total load of all the units first using the 100% demand factor for the base load (lighting, small appliance, laundry, dryers, fixed appliances), then the largest of heating or cooling for each unit, before applying the diversity factor from Table 220.84. You are correct in that you are adding 100% of the larger of heat or AC, and then multiplying by the factor.

Why the Difference Matters

The NEC intentionally distinguishes between individual unit load calculations and the service load calculation because it recognizes that not all units will simultaneously draw their maximum possible load. Table 220.84 accounts for this diversity.

Therefore, the spreadsheet is indeed wrong. It's applying the diversity factor to a value that
already has demand factors applied to it at the unit level (the 100%/40% for the base load). This results in an undersized service.

How to Correct the Spreadsheet1. Separate the calculations

Clearly separate the individual unit load calculation (220.82) from the service load calculation (220.84).
2.


Service Load Calculation (220.84)

For the service load calculation, create a new section in your spreadsheet:
Calculate the base load (3 VA/sq ft, appliance circuits, laundry circuits, dryer, etc.) for a

single
dwelling unit without applying the 100%/40% demand factor. Keep it at 100% of the calculated load. Add the larger of the cooling or heating load (also at 100% for the largest). Multiply this single-unit total by the number of units in the building. Now, apply the demand factor from Table 220.84 to this total.

Heat Pumps and 220.84

You're right to question how to handle heat pumps in 220.84. The code language is a little ambiguous. The most common and conservative interpretation is:
For each unit, determine the larger of the heating or cooling load of the heat pump. Use that value at 100% in the service calculation. If the cooling load is higher, use that. If the heating load is higher, use that. You would not* add both the heating and cooling loads together. It's an "either/or" situation.

In Summary

Your understanding of 220.82 and 220.84 is correct. The spreadsheet needs to be modified to correctly calculate the service load per 220.
84. Good catch! It's a testament to your critical thinking as an engineer. You might also consider updating your spreadsheet to reflect changes in newer versions of the NEC, if applicable to your jurisdiction. Flag for review