Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Load Shedding

User: ksheldon, Location: Houston

Asked on: Tuesday, July 30, 2024 at 2:34 pm EDT
Answered on: Thursday, March 6, 2025 at 12:29 am EST

Question: I plan to use an inverter-generator to provide backup power to a residence. I am looking for a system to shed loads when the total demand exceeds the maximum continuous output of the inverter generator. I have seen systems that trip when the frequency of the supply drops below a threshold. That works when the generator starts to slow under heavy load. In the case of an inverter, I think the frequency would remain constant, though the voltage would drop when the load exceeds the capacity of the generator. I am looking for a load management solution that triggers when the total system current exceeds a threshold, or when the voltage drops below a threshold. Any suggestions?

You're right, frequency-based load shedding is less reliable with inverter-generators. They are designed to maintain a stable frequency as long as the voltage regulator can keep up. Your focus on voltage droop and current overload is the right approach. Here's a breakdown of solutions, from simple to more complex

1. Simple Current Monitoring with Overcurrent Relays/Sensors:
Concept

Monitor the total current drawn from the generator. When it exceeds a pre-set threshold, selectively disconnect non-essential loads.


Components



Current Transformer (CT) or Hall-Effect Current Sensor

A CT clamps around the main feed wire from the generator. It produces a low-voltage AC current proportional to the main current. Hall-effect sensors are an alternative that can measure DC and AC.


Overcurrent Relay/Controller

This device takes the current signal from the CT or Hall-Effect sensor. You set a threshold current. When that threshold is exceeded, the relay trips, activating a contact.

Contactors/Relays

These are electrically operated switches. The output of the overcurrent relay controls these. Each contactor controls a specific load you want to shed.


Wiring

1. Generator output -> Main Breaker Panel.
2. CT (or Hall-Effect sensor) on the main feed wire between the generator and the main breaker panel.3. CT secondary -> Overcurrent relay/controller.
4. Overcurrent relay output -> Contactors controlling non-essential loads. For example: Contactor 1: Controls electric water heater. Contactor 2: Controls electric dryer. Contactor 3: Controls non-essential lighting.5. Each contactor is wired to interrupt power to its respective load.


Advantages

Relatively simple to implement. Directly targets the overload condition (current). Fast response.

Disadvantages

Requires wiring changes in your electrical panel. Requires understanding of electrical wiring and safety. Threshold setting needs careful calibration based on the generator's continuous current rating.

Example Products



Overcurrent Relays

Eaton Cutler-Hammer C440, ABB REF615, Siemens 7SJ80. (These are usually more industrial-focused but offer precise control)


Hall-Effect Current Sensors with Relays

Many options available from Allegro MicroSystems, LEM, and others. Search for "Hall effect current sensor relay module."

Contactors

Eaton, Schneider Electric, Siemens. Choose the appropriate amperage rating for the load you are controlling.

2. Voltage Monitoring with Under-Voltage Relays



Concept

Continuously monitor the generator's output voltage. If it drops below a pre-set threshold, shed loads.

Components



Voltage Transformer (Potential Transformer - PT)

Steps down the generator's voltage to a safe level for the relay. This is often not necessary for 120V systems; the relay can directly measure the voltage.



Under-Voltage Relay

Monitors the voltage and trips when it falls below the set point.


Contactors/Relays

As described above, to control the loads.

Wiring

1. Generator output -> Main Breaker Panel.
2. PT primary -> Generator output.
Skip this if you're directly connecting to a 120V system.3. PT secondary -> Under-Voltage Relay (or direct connection to the relay).
4. Under-Voltage Relay output -> Contactors controlling non-essential loads.


Advantages

Relatively simple to implement. Reacts to voltage sag, which is a symptom of overload.

Disadvantages

Voltage droop can also be caused by other factors besides overload (e.g., long wire runs). So, it might trigger unnecessarily. Voltage droop might not be a direct indicator of overload on a modern inverter-generator that aggressively tries to maintain voltage. Requires wiring changes.

Example Products



Under-Voltage Relays

Eaton Cutler-Hammer C440, ABB REF615, Siemens 7SJ80. (Again, industrial-focused but offer precise control)

Simple Voltage Monitor Relays

Search on Amazon or eBay for "AC voltage monitor relay."


Contactors

Eaton, Schneider Electric, Siemens.

3. Combined Current and Voltage Monitoring



Concept

Use
both current and voltage monitoring. This provides a more robust solution, reducing false positives. Shed loads only if both the current exceeds its threshold and the voltage drops below its threshold.

Components

All components from options 1 and 2.

Logic Gate (e.g., AND gate)

The outputs of the overcurrent relay and the under-voltage relay are connected to an AND gate. The contactors are activated only if both relays are tripped.

Wiring

1. As per Options 1 and 2.
2. Overcurrent relay output -> AND gate input 1.3. Under-Voltage relay output -> AND gate input 2.
4. AND gate output -> Contactors controlling non-essential loads.


Advantages

More reliable and less prone to false positives than either method alone. Reacts to both overload and voltage sag, giving a better picture of the generator's health.

Disadvantages

More complex wiring. Higher cost.

4. More Sophisticated Load Management Systems (Programmable Logic Controllers - PLCs)



Concept

Use a PLC to monitor voltage, current, and potentially other parameters (e.g., generator temperature, fuel level). Program the PLC to implement complex load shedding algorithms.

Components



Current Transformers (CTs) or Hall-Effect Sensors

As described above.

Voltage Transducers

Convert voltage levels to signals that the PLC can read.


PLC

The brains of the system.

Input/Output (I/O) Modules

Allow the PLC to read the sensor signals and control the contactors.


Contactors/Relays

As described above.

Wiring

1. Generator output -> Main Breaker Panel.
2. CTs/Hall-Effect Sensors and Voltage Transducers are connected to the generator output.3. Sensor outputs -> PLC I/O modules.
4. PLC I/O modules -> Contactors controlling non-essential loads.


Advantages

Extremely flexible and customizable. Can implement complex load shedding strategies (e.g., shedding loads in stages, prioritizing certain loads). Can log data and provide alerts.

Disadvantages

Significant programming and technical expertise required. Highest cost. Overkill for many residential applications.

Example Products



PLCs

Allen-Bradley Micro800 series, Siemens LOGO!, Omron CP1E.


I/O Modules

From the same PLC manufacturer.

Software

Usually comes with the PLC and requires a license.

5. "Smart" Energy Management Systems (EMS)



Concept

Integrated systems that monitor energy usage in real-time and automatically manage loads. Some are specifically designed for backup power situations.

Components



Whole-house energy monitor

Measures current, voltage, and power consumption at the main panel.

Smart breakers or controllable outlets

To switch loads on/off remotely.


Central controller/hub

Manages the system and communicates with the energy monitor and smart breakers.

Mobile app/web interface

For monitoring and control.


Wiring

Whole-house energy monitor is installed in the main panel. Smart breakers replace standard breakers for loads you want to control. Smart outlets replace standard outlets. Controller connects to your home network (Wi-Fi or Ethernet).

Advantages

Easy to install (relative to a PLC-based system). User-friendly interface. Often includes features like energy monitoring, reporting, and remote control. Can integrate with other smart home devices.

Disadvantages

Can be expensive. May require a subscription fee for some features. Relies on cloud connectivity for some functionality. Consider this if your power outages also disrupt internet service.

Example Products



Span Smart Panel

A complete smart electrical panel replacement with built-in load management.


Lutron Caseta Smart Switches and Dimmers

Can be used to control lighting loads.

Sense Energy Monitor

A whole-house energy monitor that can identify individual appliances. While Sense doesn't directly shed loads, you could use its data to manually manage them or potentially integrate it with other automation systems.

Important Considerations



Generator Rating

Absolutely essential. Know the continuous output rating (in watts or amps) of your generator. Don't rely on the "peak" or "starting" wattage.

Load Calculation

Calculate the total wattage of all appliances and devices you
might use simultaneously.

Safety

Work with a qualified electrician. Electrical work can be dangerous. Ensure all wiring complies with local electrical codes. Use appropriately rated components for your amperage and voltage.

Load Prioritization

Decide which loads are essential (e.g., refrigerator, lighting in critical areas) and which are non-essential (e.g., electric water heater, air conditioner, dryer, entertainment systems). Shed the non-essential loads first.


Contactors vs. Relays

For higher-amperage loads (e.g., water heaters, AC), use contactors. Relays are generally for lower-amperage loads (e.g., lighting).

Manual Override

Consider adding a manual override switch that allows you to disable the load shedding system if needed (e.g., in a medical emergency).


Testing

After installation, thoroughly test the load shedding system to ensure it works correctly. Simulate an overload by turning on multiple appliances at once.

Recommendation

For most residential backup power situations, the

Simple Current Monitoring with Overcurrent Relays/Sensors (Option 1) or the Combined Current and Voltage Monitoring (Option 3) are the most practical and cost-effective solutions. They provide a good balance of reliability, cost, and ease of implementation. If you want a more integrated and user-friendly experience, the

Smart Energy Management Systems (Option 5) are worth considering, although they can be more expensive. PLCs are generally overkill for most homes.Before proceeding, consult with a qualified electrician to determine the best approach for your specific needs and to ensure safe and code-compliant installation. Good luck! Flag for review

Previous Question Next Question