Question: Hello,I have an application where my diff Press transducers will be located in the safe area and tubing to be ran into a C1D2 area. Does my transmitters in the safe area need to be Ex protected (IS)?If yes, can you share the explanation as to why and the code it falls under?thanks in advance
No, your differential pressure transmitters located in the safe area do not need to be Ex protected (intrinsically safe or otherwise) simply because the tubing runs into a Class 1 Division 2 (C1D2) hazardous area.Here's the explanation and reasoning: Location, Location, Location
The primary principle in hazardous area classifications is based on the location of the equipment. If the equipment itself is located in a safe (non-hazardous) area, it does not require hazardous area protection. The risk is the presence of flammable vapors or gases around the equipment.
Tubing is Passive
The tubing, while it transports a fluid that could be flammable, is a passive component. It does not generate electrical signals, sparks, or high temperatures that could ignite a flammable atmosphere. The tubing is not the source of ignition in the safe area. If there is a leak at a tubing connection in the safe area, that area might then become a hazardous area, but the existing safe area equipment might then need to be addressed.
Hazardous Area Boundary
The C1D2 area is defined by the likely presence of flammable materials. Any potential hazards are contained within that classified area. The safe area, by definition, does not have those hazardous materials present under normal operating conditions.
Code & Standards
While there's no specific code provision requiring protection in a safe area for equipment connected to a hazardous area via tubing, the absence of code requirements implies it's not necessary. Relevant standards focus on protecting equipment located within the hazardous area.
NEC (National Electrical Code), specifically Article 500-505
Deals with hazardous area classifications and appropriate protection methods within those areas. It does not mandate protection for safe area equipment.
ISA-12.0.
0.1
The Instrument Society of America (ISA) has numerous standards, the series of standards related to hazardous areas do not imply protection methods in safe areas where no flammable vapors or gases are present.
Important Considerations & Caveats
Process Fluid
While your transmitters in the safe area do not need Ex protection based solely on the tubing connection to a C1D2 area, you must consider the properties of the process fluid being measured. If that fluid is itself flammable or toxic, you need to consider the general safety requirements for handling such fluids in the safe area. This is independent of the hazardous area classification. Consider leak detection and containment measures in case of a tubing failure in the safe area.
Signal Wiring
The wiring from your transmitter (in the safe area) to a control system located potentially in the C1D2 area does need to be considered. The best practice for wiring running into a hazardous location, where signal wiring must run into a hazardous location from a safe location is to use galvanically isolated barriers.
Grounding & Bonding
Proper grounding and bonding are always crucial, regardless of hazardous area classifications. It can prevent static electricity build-up and provide a safe path for fault currents.
Local Requirements
Always consult with your local authority having jurisdiction (AHJ) and qualified professionals experienced in hazardous area classifications and safety regulations. They may have specific local interpretations or requirements.
In summary, your transmitters located in the safe area are not required to be Ex protected solely because the tubing runs into a C1D2 area. Focus on the safety of the process fluid, proper wiring methods, and always consult with qualified professionals and your local AHJ. Flag for review