Topic: Cables from Tray to MCC

User: That Man, Location: California, United States

Asked on: Tuesday, July 30, 2024 at 5:14 pm EDT
Answered on: Thursday, March 6, 2025 at 12:30 am EST

Question: Please refer to the attached image. I had originally designed cable transitions from an overhead tray to the roof of an MCC through a cable gland (left half of image). The cable is TC-ER rated. It sounds like the client is thinking of adding conduit sleeves out the top of the MCC like the right half of the image. Wouldn't those need support on the top end? The tray doesn't necessarily align with the entries, so there would be lots of instances where supporting directly off the tray wouldn't work.

Okay, I've reviewed the description and image of the proposed cable transition designs. Here's a breakdown of the situation, the issues with the conduit sleeve proposal, and potential solutions

Understanding the Two Designs:
Original Design (Left)

Cable exits the overhead tray, runs down a short distance, and enters the MCC enclosure through a cable gland. This leverages the TC-ER (Tray Cable - Exposed Run) rating of the cable, which is designed for exposed runs between the tray and the equipment.


Proposed Design (Right)

Cable exits the tray, drops down into a conduit sleeve, and then enters the MCC enclosure from the top.

Issues with the Proposed Conduit Sleeve Design


Conduit Support

You're absolutely correct! Conduit, particularly vertical runs,

requires proper support.
The NEC (National Electrical Code in the US) and similar electrical codes in other regions dictate how frequently conduit must be supported. Without support, the weight of the cable within the conduit can cause stress on the conduit, the MCC enclosure, and potentially pull on the terminations inside. Furthermore, wind loading could be an issue.2. Cable Bending Radius

The cable needs to maintain its minimum bending radius as it enters the conduit and the MCC. This bending radius requirement is specified by the cable manufacturer and is crucial to prevent damage to the conductors and insulation.3.

Conduit Fill

The conduit needs to be sized appropriately for the number and size of cables it will contain. Exceeding conduit fill limits can cause overheating, insulation damage, and make pulling cables difficult.4.

Water Intrusion

The top of the conduit will be open to the environment. Rain and debris could enter the conduit, potentially causing corrosion or electrical problems inside the MCC.5.

Cost

The conduit sleeves themselves will add to the overall project cost. Conduit supports will also add additional costs.6.

TC-ER Rating Redundancy

The TC-ER rating of the cable allows for exposed runs. By introducing conduit, you're essentially negating the benefit of using TC-ER cable in the first place.7.

Possible Derating

Running the cables in a conduit sleeve that is exposed to sun could cause temperature derating of the conductors.

Why the Client Might Be Suggesting Conduit



Perceived Protection

They may believe that conduit offers better physical protection for the cables.


Aesthetics

They might prefer the look of conduit over exposed cable.

Misunderstanding of TC-ER

They may not fully understand the purpose and capabilities of TC-ER cable.


Company Standard

It might be a company standard to always use conduit, regardless of the cable type.

Solutions and Recommendations


Advocate for the Original Design (Cable Gland)



Explain TC-ER Benefits

Clearly explain the benefits of using TC-ER cable, including its ability to be run exposed, its cost-effectiveness, and its suitability for this application.


Highlight Code Compliance

Assure the client that the cable gland design is fully compliant with electrical codes when using TC-ER cable.2.

If Conduit is Required (Despite TC-ER)



Proper Support

Ensure the conduit is properly supported according to code requirements. This will likely require custom-fabricated supports that attach to the building structure or a dedicated support system.


Weatherproof Fittings

Use weatherproof conduit bodies and fittings (e.g., LB, LL, LR fittings) to direct the cable and protect it from moisture. Consider a sealing fitting at the top of the conduit to minimize water entry.

Bending Radius

Carefully plan the conduit runs to maintain the cable's minimum bending radius.


Conduit Fill Calculations

Calculate the appropriate conduit size based on the cable diameters.

Grounding

Properly ground the conduit system.


Consider Flexible Conduit

For shorter runs and to accommodate slight misalignments between the tray and the MCC entries, consider using flexible metallic conduit (FMC) or liquid-tight flexible metallic conduit (LFMC). These are easier to work with but still require support.3.

Hybrid Approach

If only physical protection is a concern, consider using short sections of metal conduit to physically protect the cable near the point of entry. The exposed run can then be used on the remainder of the route between the tray and the conduit.4.

Speak with the Manufacturer
The cable manufacturers may have specific recommendations for the use of their product in this application. They may also recommend specific methods of support.

Communication is Key



Have a Discussion

Talk to the client to understand their concerns and reasoning behind wanting conduit.


Present Options

Clearly present the pros and cons of each design, including cost, installation complexity, and long-term maintenance.*

Provide Documentation

Back up your recommendations with relevant code sections, cable specifications, and manufacturer recommendations.

In summary, while the client's intention might be well-meaning, simply adding conduit sleeves without proper planning and execution can create more problems than it solves. Emphasize the benefits of the TC-ER cable's exposed run capability. If conduit is insisted upon, ensure it's properly supported, weatherproofed, and sized appropriately, and that the cable's bending radius is maintained.