Topic: Dirty Ole Circuit Breaker

User: xguard, Location: Baton Rouge, LA

Asked on: Tuesday, July 30, 2024 at 5:38 pm EDT
Answered on: Thursday, March 6, 2025 at 12:31 am EST

Question: Working at one of our facilities that was built in the 1960's. The photos are of the service disconnect, unit mounted 225 amp breaker located outdoors. System voltage is 240/120 three phase.Just curious what you would do if asked to re-use this breaker, i.e. replace the feeder. I typically call to replace equipment in this condition when our project is required to tie into it, maybe I'm being too conservative. This is because I've heard of some of our old breakers cracking when trying to break the lugs loose and also I've assumed the wire insulation may fail if it's disturbed. What has been your experience in these situations?I've noticed that electrical equipment installed indoors, especially in conditioned spaces, seems to last much longer. Living in Louisiana with the head, humidity and bugs really takes a toll on everything.A couple notes:They used 3/0 for some reason when they spliced in a manual transfer switch.Noticed one phase conductor is smaller than the other two, assuming the high leg but I didn't check the voltage.

You've hit on a common dilemma when working with older electrical systems, especially in harsh environments like Louisiana. Your concerns are valid and reflect good risk management. Here's a breakdown of how I would approach the situation, balancing cost, safety, and reliability

Factors to Consider:
Age and Environment

1960s equipment has definitely seen better days. The heat, humidity, and bugs in Louisiana accelerate degradation of plastics, metals, and insulation. Outdoor equipment, like this disconnect, suffers even more.


Condition Assessment (Before Making a Decision)

This is crucial. A visual inspection alone isn't enough. You need to get your hands on it:

Breaker Housing

Look closely for cracks, fading, or deformation of the plastic housing. Pay special attention to areas around mounting points and lug terminations.


Lug Condition

Examine the lugs for corrosion, pitting, or signs of overheating.

Wire Insulation

Check for brittleness, cracking, or discoloration of the wire insulation where it enters the breaker. Gentle bending can reveal hidden cracking.


Breaker Operation

Test the breaker manually. Does it trip cleanly? Does it reset easily? Are there any unusual noises (like grinding or sticking)?

Infrared Scan

If possible, use an infrared camera to check for hot spots while the breaker is under load. This can indicate loose connections or internal problems.


Contact Resistance Test

A milli-ohmmeter can be used to measure the contact resistance of the breaker. High resistance indicates corroded or worn contacts.

Code Compliance

Even if the existing installation
technically met code when installed, current codes often have stricter requirements for safety and accessibility. Bringing the installation up to current code standards is always a good idea.

Load Requirements

Ensure the existing breaker and conductors are adequately sized for the anticipated load of the new feeder.

Risk Tolerance

How critical is the equipment being fed by this breaker? A failure could be catastrophic or just an inconvenience.


Budget

This is always a factor. Replacement costs money, but so does downtime and potential safety hazards.

Liability

If you reuse a questionable breaker and it fails, leading to damage or injury, you could be held liable.

My Approach, Step-by-Step


Thorough Inspection (as detailed above)

This is the non-negotiable first step. Document everything with photos.2.

Voltage Check and Phase Identification

Confirm the "high leg" issue and document the voltages on all three phases.3.

Consult with Your Supervisor/Engineer

Present your findings and concerns. Get their input and approval before proceeding.4.

Possible Scenarios and Actions



Scenario 1: Breaker and Wiring Appear to Be in Good Condition



Action



Clean

Carefully clean the breaker housing and lugs.

Tighten Connections

Torque lug connections to the manufacturer's specifications (if available). If you can't find the specs and it's an old breaker, I'd consider NOT torquing unless you have a lot of experience. Over-tightening is very easy to do on an old lug. If in doubt, replace.


Insulation Inspection

Closely inspect the wire insulation as you're tightening. Replace any conductors with signs of damage.

Document

Take photos of the breaker and connections after tightening.


Consider a short (1 year) maintenance schedule to ensure the equipment is still performing safely.
Use caution with conductors

Carefully bend and move conductors. They may be brittle and crack.


Scenario 2: Minor Corrosion, Some Cracking of Insulation, But Breaker Functioning



Action



Replace Conductors

Replace all the conductors connected to the breaker, ensuring proper size and insulation rating.

Clean and Treat

Clean corrosion from the breaker lugs with an appropriate cleaner. Apply a corrosion inhibitor.


Document

As above.

Scenario 3: Significant Corrosion, Cracks in Breaker Housing, Questionable Operation



Action



Replace the Breaker and, Ideally, the Entire Disconnect Enclosure.
This is the safest and most reliable option. The cost of replacement is justified by the reduced risk of failure and potential liability. Code Compliance

This is a good opportunity to bring the installation up to current code standards, including proper working clearances, grounding, and overcurrent protection.


Document

Photograph the old equipment before removal for your records.5.

Addressing the 3/0 Wiring and Smaller Conductor



3/0 Wiring

If the load doesn't require 3/0, downsize to the appropriate conductor size for the load and breaker rating. This also addresses the manual transfer switch issue.


Smaller Conductor (Assuming High Leg)

Replace the conductor with the correct size and color-coding for the high leg.

Justification for Replacement (if that's what you recommend)



Age and Condition

"The equipment is over 50 years old and shows signs of degradation due to environmental factors (heat, humidity, corrosion). Reusing it poses a significant risk of failure, which could lead to downtime, equipment damage, or safety hazards."


Liability

"Reusing questionable equipment increases our liability in the event of a failure."

Code Compliance

"Replacing the equipment allows us to bring the installation up to current code standards, improving safety and reliability."


Long-Term Cost

"While replacement is more expensive upfront, it reduces the risk of costly repairs and downtime in the future."

In Conclusion:


Your instincts are correct. Reusing old electrical equipment in harsh environments requires a careful and thorough assessment. Prioritize safety and reliability. Don't hesitate to recommend replacement if you have any doubts about the equipment's condition. Document your findings and get approval from your supervisor before proceeding. While replacement has higher upfront costs, it will most likely save money in the long run. Flag for review