User: Nelatieh, Location: 17050
Asked on: Tuesday, July 30, 2024 at 10:54 pm EDT
Answered on: Thursday, March 6, 2025 at 12:31 am EST
Question: Mike, I am a residential electrician, I use a contractor license to work in Pa.I worked overseas in crazy poor areas.I studied 2 years in the USA to learn the codes.On top of my degree from a French technical school overseas.One of my customers has a large commercial building, he has 208/120 panels and 277 panels,He asked me to add an outlet in a large closet space.I tapped into a 120 outlet that was thereParallel using MC 12/2 7-8 feet long max.He plugged an Ethernet transfer switch 4.0 amp.Half the lights in that place flickered and we had a voltage drop of 8 volt after loading the circuit with the switch.Plug a 50 watt chip light and the drop is 18 volt.Hot to ground stayed 122.The lights are all on the 277 circuits not on the 120It is a 20000 square foot open building used for pickle ball.I did tell him to get a commercial electrician.Any thoughts ?Thank you
Okay, Mike, based on the information you've provided, here's a breakdown of possible issues and considerations, along with why telling him to get a commercial electrician was the right call
Likely Problems and Explanations
Overloaded Circuit
The biggest red flag is the voltage drop. An 8-volt drop with a 4-amp load, and an 18-volt drop with just a 50-watt light (less than 0.5 amps) is a sign the circuit is already heavily loaded or has a significant impedance issue. Even though you are only adding a relatively small load, the existing circuit could be close to capacity.
Long Circuit Run/High Impedance
While your additional 7-8 feet of MC cable isn't the primary problem, it exacerbates an existing issue. Long circuit runs from the panel to the original outlet can have a high impedance, resulting in voltage drop when loaded. Adding even a small load can trigger a noticeable effect.
Loose Connections/Corrosion
Loose connections anywhere along the circuit (at the breaker, the original outlet, your added outlet) can create high resistance and cause significant voltage drop under load. Corrosion can have the same effect.
Neutral Issues
A shared neutral on a multi-wire branch circuit can cause problems, especially if the loads aren't balanced. The neutral could be undersized or have loose connections as well.
Transformer Issues
While less likely if the rest of the building seems okay, it's possible there's an issue with the 208/120V transformer feeding that section of the building. It could be overloaded or have internal problems.
Power Quality
The issue could also be unrelated to the 120v circuit you added. It could be an overall power quality issue in the building affecting the lighting.
Why the Flickering Lights on 277V Circuits?
This is the most puzzling part. Here's how a problem on a 120V circuit could affect 277V lighting, though it's less direct: Shared Neutral
If the 120V circuit shares a neutral with other 120V circuits, and those circuits are also used to power control components for the 277V lighting (e.g., dimming systems, relays, or smart building controls), voltage fluctuations on the shared neutral could impact the sensitive electronics on the 277v circuit and make them flicker.
Weak/Shared Ground
A poor or shared grounding system could allow noise and voltage fluctuations from the 120V circuit to affect the reference ground for the 277V lighting control systems. This is less likely than a shared neutral problem.
Transformer Feedback
While uncommon, in some situations, a significant load imbalance on the 120V side of the transformer could potentially introduce harmonics or voltage fluctuations that affect the overall power quality feeding the building, which in turn might (but probably not) influence the 277V circuits. This is a very remote possibility.
Coincidence
It's possible the 277V lighting flickering is a separate issue entirely, and its onset just happened to coincide with your work on the 120V circuit.
Voltage Regulation
The building's voltage regulation is not good enough to keep from fluctuating.
Why You Were Right to Refer Him to a Commercial Electrician Scope of Work
The situation is beyond a simple residential service call. Diagnosing and fixing this properly requires more in-depth knowledge of commercial electrical systems, power quality analysis, and potentially working with three-phase power distribution.
Liability
As you found out, the problem is not as simple as adding an outlet. If you continued troubleshooting and inadvertently made the situation worse (or missed a critical issue), you could be held liable.
Proper Equipment
Commercial electricians typically have access to specialized equipment like power quality analyzers, thermal imaging cameras, and advanced testing tools to diagnose these types of problems effectively.
Knowledge of Commercial Codes
While you have code knowledge, commercial installations have their own nuances and specific requirements that a commercial electrician will be more familiar with.
Safety
Working in large commercial buildings can present different safety hazards than residential work. A commercial electrician will be better equipped and trained to handle these.
Recommendations for the Commercial Electrician You Refer
Advise the commercial electrician to:1. Perform a thorough load analysis
Measure the current on the circuit you tapped into and on other circuits in the area, and compare the readings to the breakers' ratings.2.
Check voltage drop at various points
Measure voltage at the panel, the original outlet, and your new outlet under load.3.
Inspect all connections
Carefully examine all connections along the circuit for looseness, corrosion, or damage.4.
Investigate the neutral
Check the neutral connection at the panel and at the first receptacle on the circuit. Look for signs of overheating or looseness. Check for shared neutrals with other circuits.5.
Check grounding system
Verify the integrity of the grounding system and look for any signs of poor grounding.6.
Consider a dedicated circuit
If the existing circuit is overloaded, the electrician should run a new, dedicated circuit from the panel to the closet.7.
Power quality analysis
If the flickering on the 277V circuits persists, the electrician should perform a power quality analysis to identify any harmonics, voltage fluctuations, or other issues that could be affecting the lighting.8.
Check voltage and current on the 277 Volt system. Check for voltage on each leg. Also, do an amp draw on each leg.By backing away and recommending a professional familiar with commercial systems, you protected yourself and your customer. Good call. Flag for review