User: kilovar1959, Location: Columbus OH
Asked on: Wednesday, July 31, 2024 at 10:27 am EDT
Answered on: Thursday, March 6, 2025 at 12:33 am EST
Question: Hello gentlemen, below is an image of the conduit connections into my personal home standby generator. I had the dealer do the installation to make sure my warranty was protected. The sub he hired dug a trench and went underground. My question is if the way they connected to the generator housing is proper? The generator is on vibration isolation inside the housing and the housing is bolted solid to the pad. However the pad is a "drop in" pad so it will likely settle over time. I do not see any allowances for ground movement.I should note the contractor did NOT pull a permit, so it was not inspected. They did use the can on the meter main as a (short) pull through for control wire, so they could share the same conduit with a 20 amp 120 volt station service circuit from a breaker in the meter main. I have had to make some control wiring repairs as some was incomplete, and RS485 wiring was done incorrectly.What are your thoughts?
Okay, let's break down the image and your concerns about the conduit connections to your home standby generator. You're right to be concerned about movement and proper installation, especially given the lack of permits and some observed issues with the wiring.
Here's a breakdown of what I see and my thoughts
Rigid Conduit Entry Points
From the look of the photo they used rigid conduit (likely galvanized steel) to enter the generator enclosure.
Lack of Flexibility
This is the core of your concern, and rightfully so. Rigid conduit, directly connected to the generator enclosure, offers
no flexibility. As the pad settles, or even just due to seasonal ground movement, the conduit can exert stress on the generator housing and the rigid conduit itself. This can lead to: Stress on the Generator Enclosure
Cracking or distortion of the enclosure is possible, especially where the conduit enters. This can compromise the weatherproof integrity of the generator.
Conduit Joint Separation
Underground conduit runs can be long. If the pad settles or ground movement occurs, this can put stress on the joints in the conduit run, potentially leading to separation and water ingress.
Damage to Internal Wiring
While less likely, the stress could transmit into the generator and potentially damage internal wiring connections.
Grounding Issues
Movement could loosen connections in the grounding system.
Vibration Isolation
While the engine and generator assembly itself may have vibration isolation mounts inside the enclosure, that doesn't isolate the enclosure itself from ground movement. Your concern about the settling pad is valid.
Potential Code Violations
Without a permit, it's hard to say definitively, but the lack of flexibility at the generator connection likely violates code (NEC). Codes require that electrical installations be done in a workmanlike manner and that all applicable codes and standards are followed.
Sharing Conduit
Sharing conduit between the generator control wires and the 120V service circuit is legal and compliant.
What Should Be Done
A Flexible Conduit Section is Required
A short section of flexible metal conduit (FMC) or liquidtight flexible metal conduit (LFMC) should be installed between the rigid conduit run and the generator enclosure. This "flex" section will absorb movement and vibration. Ideally, this flex section should be as short as reasonably possible (to minimize voltage drop, although that's less critical with control wiring).
Proper Grounding
Ensure that the flexible conduit is properly grounded. You'll need a grounding bushing on each end and a grounding jumper wire connecting the bushings if the flex conduit isn't listed as suitable for grounding.
Consider a Service Loop
If you are very concerned about movement, add a service loop of extra conduit length before the flex section, buried in the trench. This gives some additional slack to accommodate movement.
Pull a Permit Now (If Possible)
While it's already installed, pulling a permit now and having it inspected will give you peace of mind that it's done correctly and safely. It might be a bit awkward, but it's better than living with a potentially unsafe installation. The inspector will likely call out the rigid conduit connection.
Grounding
Make certain that all grounding screws are clean and the connection is tight.
Document Everything
Take pictures of the installation before and after any corrections. Keep copies of all permits, inspection reports, and any communication with the installer.
Key Considerations
Local Codes
Local electrical codes always take precedence. Consult with your local building department or a qualified electrician in your area to ensure compliance.*
Manufacturer's Instructions
Always follow the generator manufacturer's installation instructions.
In Summary:
The rigid conduit connection directly to the generator housing is a significant concern. You need a flexible section to accommodate movement. While the shared conduit for control wires is okay, the overall lack of permits and some wiring issues you've observed are red flags. I recommend getting a qualified electrician to inspect the installation and correct the conduit connection. Don't delay on this, as the longer it's left uncorrected, the more potential for problems down the road. Flag for review