Topic: Need Help With EGC Question

User: cgamad550, Location: United States

Asked on: Wednesday, July 31, 2024 at 11:00 am EDT
Answered on: Thursday, March 6, 2025 at 12:33 am EST

Question: I have a Question that I'm hoping you can help answer for me.I recently purchased a property and at the service entrance. I have 2 copper wires coming from the EGC. One goes up top and is attached at the weather head to the neutral/ground coming in from the lines coming from the transformer, the other is going up into the meter can.Is this properly grounded? There no ground wire in the service panel attached to the ground bar but the neutrals and grounds are bonded with the bonding screw.We have issues with frequent power surges and I have installed a Square D HEPD80 SPD device. But someone told me if there's no EGC connected to the service panel itself that the SPD won't actually work. Is this correct?Or do I need to install 2 ground rods and connect an EGC directly into the service Panel.If you could please help me with this it would be greatly appreciated.

Okay, let's break down your grounding situation and address your concerns. It sounds like you have a potentially problematic, and possibly unsafe, service entrance configuration.

Understanding the Situation What you described sounds like a common (but often incorrect) interpretation of grounding in older installations. The fact that one EGC (Equipment Grounding Conductor) connects to the neutral/ground at the weatherhead and the other to the meter can suggest an attempt to establish a ground path. Key Problem: Lack of a Dedicated EGC to the Service Panel

The biggest red flag is the absence of a dedicated Equipment Grounding Conductor (EGC) connected to the ground bar within your service panel. This is essential for safety and proper SPD operation.

Bonding Screw Present

The fact that the neutral and ground bars are bonded with a screw in the service panel is normal
IF this is the

main service panel
for the building. This creates the required single point where neutral and ground are electrically connected. Power Surge Issue

Frequent power surges are concerning. While an SPD can help, a properly grounded system is the foundation for surge protection.

Is Your Current System Properly Grounded?
Likely NOT. The connections to the weatherhead and meter can are likely insufficient and potentially unsafe as a primary means of grounding the system.

Why This Matters: Safety and SPD Functionality1. Safety

The Equipment Grounding Conductor (EGC) provides a low-impedance path for fault current to return to the source (transformer). This allows a breaker to trip quickly in the event of a short circuit or ground fault. Without a good EGC connection to the panel, fault currents may take alternate paths (e.g., through plumbing, metal structures), creating a shock hazard.2.

SPD Functionality

Surge Protective Devices (SPDs) work by diverting surge current to ground. Without a solid ground connection to the service panel, the SPD has no effective path to divert the surge energy. This means it won't work as intended and can even be damaged.

What You Need to Do


Consult with a Qualified Electrician (REQUIRED)


DO NOT ATTEMPT THIS WORK YOURSELF IF YOU ARE NOT A QUALIFIED AND EXPERIENCED ELECTRICIAN.
Dealing with service entrance wiring is dangerous and requires expertise. A licensed electrician can properly assess your specific situation and ensure the work complies with local electrical codes and is done safely.2. Establish a Proper Grounding Electrode System

You will likely need to install a grounding electrode system, which typically consists of:

Ground Rods

Two ground rods, at least 8 feet long and spaced at least 6 feet apart, driven into the ground.


Grounding Electrode Conductor (GEC)

A properly sized copper conductor (based on the size of your service entrance conductors) connecting the ground rods to the ground bar in your service panel.3.

Connect EGC to the Service Panel

The electrician will run an Equipment Grounding Conductor (EGC) from the grounding electrode system (ground rods) to the ground bar in your service panel. This is the essential connection that is currently missing.4.

Assess Existing Connections

The electrician will evaluate the connections at the weatherhead and meter can. Depending on local codes and best practices, they may retain those connections in addition to the new grounding electrode system, or they may modify or remove them.

Regarding Your Specific Questions



"Is this properly grounded?"
Based on your description, almost certainly not. "If there's no EGC connected to the service panel itself that the SPD won't actually work. Is this correct?" Yes, that is correct. The SPD needs a low-impedance path to ground to effectively divert surge currents. "Or do I need to install 2 ground rods and connect an EGC directly into the service panel." This is likely what you need to do, but a qualified electrician needs to assess your specific situation and local codes.

Important Considerations



Local Electrical Codes

Grounding requirements vary by jurisdiction. Your electrician will be familiar with the applicable codes in your area.

Bonding

The electrician will ensure proper bonding of all metal enclosures (meter can, service panel) and any metallic water pipes entering the building within 5 feet of entry.


Main vs. Subpanel

It is critical to understand that you should only have ONE location where neutral and ground are bonded. The bonding screw is only used in the main panel. If this panel is a sub panel there shouldn't be a grounding screw.

In Summary:


Your primary concern should be to get a qualified electrician to inspect your service entrance and install a proper grounding electrode system (likely ground rods) with a dedicated EGC running to the ground bar in your service panel. This will improve safety, allow your SPD to function correctly, and protect your electrical equipment from surges. Do not delay in addressing this issue. Flag for review