Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: How do you apply 2023 NEC 690.8(A)(1)(a)(2) to calculate PV source circuit maximum current

User: pv_n00b, Location: CA, USA

Asked on: Wednesday, July 31, 2024 at 2:39 pm EDT
Answered on: Thursday, March 6, 2025 at 12:33 am EST

Question: I've seen people use 690.8(A)(1)(a)(2) and software like SAM to calculate PV source circuit maximum current in two ways:Find the three maximum hourly currents and average them. The three data points do not need to be consecutive hours.Find the highest three hour average of any three consecutive data points.NEC 690.8(A)(1)(a)(2) is not very specific about how to get the three hour average so either of these will comply. I'm just curious if one or the other is more commonly used. I've made a poll.

This is a great question that highlights a common area of interpretation within the NEC. You're right, 690.8(A)(1)(a)(2) leaves room for interpretation. Let's break down why this ambiguity exists and the implications of each method.

NEC 690.8(A)(1)(a)(2) and Its Intent

The code aims to account for realistic, sustained high current conditions. It's trying to avoid oversizing components based on fleeting, unrealistically high spikes. The "three-hour average" is meant to smooth out temporary fluctuations.

Method 1: Average of Three Highest Hourly Currents
Pros

Potentially more conservative, capturing the absolute highest current values regardless of temporal proximity. Simple to calculate if you have hourly data. Might be preferred by stricter AHJs (Authorities Having Jurisdiction) because it errs on the side of caution.

Cons

Might overestimate the sustained current. Three individual, unrelated high-current hours might not represent a genuine extended period of stress on the system. Could lead to unnecessary oversizing of conductors, fuses, and other equipment.

Method 2: Highest Three-Hour Rolling Average
Pros

More accurately reflects a period of sustained high current. A "rolling average" inherently considers the temporal relationship between data points. Likely to be closer to the true worst-case sustained current, potentially allowing for more efficient and cost-effective system design. Better represents the code's intent of averaging over time.

Cons

Slightly more complex to calculate, especially manually (though easily done with software like SAM or spreadsheets). Could potentially underestimate if the three highest, completely isolated hourly spikes are significantly higher than any three-hour block.

Which Method is More Commonly Used?


While it's hard to definitively say which method is more commonly used nationwide, the highest three-hour rolling average is generally considered to be a more appropriate and defensible interpretation of NEC 690.8(A)(1)(a)(2).

Reasons for Rolling Average Preference



Alignment with Code Intent

The rolling average aligns better with the code's intent of capturing
sustained high currents, not just isolated peaks.

Real-World Relevance

Electrical equipment ratings are often based on sustained thermal performance. A three-hour rolling average gives a better indication of thermal stress.

Industry Practice

Many experienced PV designers and engineers lean towards the rolling average method.

Important Considerations



Authority Having Jurisdiction (AHJ)

Always check with your local AHJ. Their interpretation is the ultimate deciding factor. Present your calculations and reasoning clearly. If the AHJ is not accustomed to PV, providing them with code references and explanation can be beneficial.

Documentation

Clearly document your chosen method in your design documentation. This transparency helps with the review process.


Software Defaults

Be aware of the default calculation method in your PV design software. Ensure the software is calculating as expected.

Conservative vs. Optimized Design

The choice between the two methods boils down to a balance between a more conservative design (Method 1) and a more optimized design (Method 2). A conservative design may result in higher upfront costs but greater safety margins. An optimized design may result in lower upfront costs but less safety margin.

In summary:


While both methods
could* be argued as compliant, the consensus leans toward using the highest three-hour rolling average because it better aligns with the intent of the NEC and reflects a more realistic sustained operating condition.Your poll is a great way to gauge current practices, but remember to always prioritize the AHJ's interpretation. Flag for review

Previous Question Next Question