Question: Hello there I'm working on a project located at los angeles, This project has two buildings each building has two units. So can I run two feeders at the other building which will be terminated on a disconnect.
Okay, let's break down the scenario and the relevant considerations under the National Electrical Code (NEC), which is typically adopted and amended by local jurisdictions like Los Angeles.
The Scenario
Location
Los Angeles (Important because local amendments can exist)
Project
Two buildings
Building 1
No specific details mentioned (presumably the main service is here)
Building 2
Has two units and you want to run two feeders to it.
Proposed Setup
Two feeders from Building 1 to Building 2, each terminating in a disconnect switch in Building 2.
NEC Considerations and Feasibility NEC Article 225: Outside Branch Circuits and Feeders This is the core article governing feeders running between buildings. NEC 225.30: Number of Feeders or Branch Circuits. Supplying Buildings or Other Structures on the Same Property. General Rule
Generally, only ONE feeder or branch circuit is allowed to supply power to a single building or structure.
Exceptions
This is where your situation hinges. There are exceptions that allow more than one feeder. These are the only ways you can legally run two feeders to Building 2. Here's the relevant excerpt:
(A) For fire pumps installed in accordance with 695. (B) For stand-by systems installed in accordance with Article 701. (C) For parallel power production systems in accordance with 705. (D) Where the capacity requirements of a single feeder or branch circuit exceed the ampacity of the largest overcurrent protective device. (E) Where documented safe switching procedures are established and maintained for energy management or utilization requirements. (F) For electric vehicle supply equipment supplied by more than one branch circuit or feeder. (G) For integrated electrical systems where shared feeders may improve reliability and decrease potential cumulative downtime.Analysis of Your Situation and Possible Justifications
Let's see if any of the exceptions apply:1. Fire Pump (A)
If Building 2 has a fire pump and one feeder is exclusively for that fire pump, then you could have a second feeder for the rest of the building.2.
Standby System (B)
If Building 2 has a legally required standby system (e.g., emergency generator for life safety), one feeder could be for the standby system and the other for normal power.3.
Parallel Power Production (C)
If Building 2 has solar panels, wind turbines, or other distributed generation, it might be possible to justify a second feeder, but this is complex and requires careful engineering and coordination.4.
Capacity Exceeded (D)
This is probably the most likely justification if the electrical load of Building 2 is so large that a single feeder would require an overcurrent device larger than what's practically available or permitted by the equipment being fed in Building 2. You'd need to calculate the total load of Building 2 (using NEC Article 220) and demonstrate that a single feeder is insufficient. Keep in mind that large conductors can be used for a single feeder to provide a high ampacity service.
5.
Safe Switching Procedures (E)
This is a less common exception, but if the building has complex energy management requirements that require regular switching between different power sources, and documented procedures are in place, this might be a justification.6.
Electric Vehicle Supply Equipment (F)
Only if the electric vehicle supply equipment requires more than one branch circuit or feeder.7.
Integrated electrical systems (G)
Only if shared feeders would improve reliability and decrease potential cumulative downtime.
The Disconnects
NEC 225.31 requires a disconnecting means shall be provided where the feeders supply or pass through more than one building or other structure. NEC 225.32 requires that the disconnecting means shall consist of a circuit breaker or switch, or both, suitable for use as service equipment. NEC 225.33 requires that the disconnecting means shall be installed at a readily accessible location either outside of the building or structure, or inside nearest the point of entrance of the conductors.
Crucial Next Steps
Load Calculation
Perform a detailed load calculation for Building 2, following NEC Article 220. This is essential to determine if a single feeder is truly inadequate.2.
Justification
Determine which exception (if any) you can legitimately use to justify two feeders. Document this justification thoroughly.3.
Coordination with AHJ
Before you proceed with the design,
talk to the Los Angeles Department of Building and Safety (or whatever AHJ has jurisdiction over electrical inspections). Explain your situation, your proposed solution, and the exception you believe applies. Get their written approval before you proceed. The AHJ has the final say, and their interpretation of the code matters most.4. Professional Engineer/Electrical Contractor
This type of design work should be performed by a qualified professional. This ensures the installation complies with all codes and standards, and is safe.
In Summary:
Running two feeders to a single building is generally prohibited by the NEC unless a specific exception applies. Carefully evaluate your situation, perform load calculations, identify a valid exception, and, most importantly*, get approval from the Los Angeles AHJ before proceeding. This will help you avoid costly rework and ensure a safe and code-compliant installation. Flag for review