Topic: Grouping of disconnects and PV

User: Indian_Rdr, Location: St. Louis

Asked on: Wednesday, July 31, 2024 at 6:51 pm EDT
Answered on: Thursday, March 6, 2025 at 12:34 am EST

Question: Working on an apartment building that has a dedicated electric room where the main means of disconnect is located within this room. The PV system is tying into the bus ahead of the disconnecting means and the disconnect for the PV is located outside the electric room on the building exterior near the door to gain entry to throw the main. Lot of words but trying to be as descriptive as possible.My question, does the PV disconnect need to located within the electric room for grouping of disconnects or does 705.11 cover this as it is located within 16' of the main disconnecting means?

You're describing a common, and often debated, scenario. Here's a breakdown of how the NEC applies to your PV disconnect location

Key Code Sections:
705.11 Grouping of Disconnects

This is the primary section to consider. It generally requires all disconnecting means for a PV system to be grouped and in a readily accessible location.


705.12 Available Fault Current

This is a more general requirement, but it mandates that the PV system connection doesn't exceed the busbar's ampacity in reverse feed scenarios.

230.72(A) Grouping of Disconnects

Disconnects for each service must be grouped

Analysis


Grouping of Disconnects (705.11)

The
intent of 705.11 is to ensure that emergency responders (firefighters, maintenance personnel, etc.) can quickly and easily de-energize all power sources feeding into a building. The "grouping" allows for a coordinated shutdown in case of a fire or other emergency.2.

The 16-Foot Exception (705.11)

The exception you mentioned is
crucial: "Where a building or other structure has multiple disconnecting means, the disconnecting means required by 705.10(A) through (D) for each feeder or service circuit with power production equipment shall be located at a readily accessible location outside of the building or structure or elsewhere on the premises. This disconnecting means shall be capable of being locked in the open position. Exception: Where the disconnecting means in 705.10(A) through (D) is located in an electrical room or enclosure that is under locked or other access control provisions, and that is designed to prevent access by unqualified persons, the disconnecting means shall be permitted to be located within the room, provided that the electrical room or enclosure is readily accessible and all of the following conditions are met: (1) A permanent, legible directory shall be installed at each service equipment location and at locations of power production equipment disconnects. (2) The disconnecting means shall be installed within 16 ft. of the service disconnecting means. (3) The disconnecting means shall be marked as an additional source."3.

Applying it to Your Scenario



PV Disconnect
Outside the Electric Room

You've described the PV disconnect as being
outside the electrical room, on the building exterior near the door.

Compliance

Your scenario can comply with the NEC.

Justification

The PV disconnect is located outside and readily accessible. The 16-foot exception would not be applicable.


Important Considerations



Clear Labeling

Ensure the PV disconnect is clearly labeled per NEC requirements.


Emergency Responder Access

Consider whether firefighters or other emergency responders would expect the PV disconnect to be in the same electrical room as the main disconnect. If it's not obvious, additional signage directing them to the external PV disconnect is advisable.

Lockable

The disconnect must be capable of being locked in the open position.


PV Disconnect Inside the Electric Room

If you wanted to locate the PV disconnect inside the electrical room, then ALL conditions of the exception must be met:

Restricted Access

The electrical room MUST be under locked or other access control provisions.


Directory

A directory would be required at each service equipment location and at the PV disconnect location.

16-Foot Rule

The PV disconnect MUST be within 16 feet of the main service disconnect.


Marking

The PV disconnect must be marked as an additional source.

Conclusion:


Your current setup, with the PV disconnect outside the electrical room, complies with the NEC, particularly 705.11, as long as it's readily accessible, clearly labeled, and lockable. The 16-foot exception is not necessary in this scenario.It's always recommended to discuss your specific design with the local AHJ (Authority Having Jurisdiction) to ensure compliance with their specific interpretations and local amendments. Flag for review