Topic: Bonding PVC Jacketed MC

User: zzzzt, Location: Cherry Valley NY, Seattle, WA

Asked on: Thursday, August 1, 2024 at 12:02 pm EDT
Answered on: Thursday, March 6, 2025 at 12:36 am EST

Question: I’m new to HVAC systems and in an effort to satisfy requirements for an exposed run of the control cable I installed Southwire’s EZ-IN cable.Then I found out they the HVAC equipment is nonmetallic.So I figure I need to find a way to bond the AC armor to the EGC and look to connectors for EZ-IN. So far it’s only been the Diversitech connectors. I called Diversitech and they say that even though it has an aluminum body, the connection to the cable is insulated and does not make metallic contact with the armor.I’m hoping to find someone familiar with this stuff.Thanks for your help!

Okay, let's break down the situation and explore your options. You've run into a common issue when dealing with different wiring methods and equipment types.

Understanding the Problem EZ-IN Cable (AC)

This is likely referring to an Armored Cable (AC), sometimes called BX cable, that includes an internal bonding strip and insulated conductors within a flexible metal sheath (the armor). The armor provides mechanical protection for the wires.


Exposed Run Requirement

You're trying to protect the control cable (thermostat wire) from physical damage by running it through the armored cable.

Non-Metallic HVAC Equipment

The key here is that the HVAC unit is
non-metallic. This means that the equipment case is not designed to be bonded to ground.

Grounding/Bonding Confusion

Your instinct is right that you need to provide a path to ground for the armor of the AC cable. This ensures that if the armor becomes energized due to a fault (a wire shorting to the armor), the circuit breaker will trip.

Why This is Tricky with Non-Metallic Equipment


The fundamental problem is that you have a metallic raceway (the AC cable armor) terminating at a non-metallic enclosure. There's nothing to bond it to at the HVAC unit.

Why Diversitech (and Similar) Connectors Might Not Work

These types of connectors (even with aluminum bodies) often isolate the armor from the connection point. This is a common design choice, especially with MC (Metal-Clad) cable, because it can help prevent circulating ground currents and ground loops. You've confirmed this with Diversitech, which makes them unsuitable for your application.

Potential Solutions

Here are some approaches, listed from what is likely the most code-compliant to the least desirable, and considering your specific situation:1. Use a metallic junction box and adapt

This is often the best solution, if feasible. Install a small, metallic junction box near the HVAC unit. Terminate the AC cable into the junction box using a connector specifically rated for AC cable (e.g., a standard set screw connector for AC cable). These connectors provide a positive, metal-to-metal contact with the armor. Bond the junction box to the equipment grounding conductor (EGC). From the junction box, run appropriately rated wiring (e.g., THHN/THWN in conduit, or even a cable assembly like NM-B) to the HVAC unit's low voltage control connections. The metal box acts as the bonding point for the AC armor.2.

Change the wiring method for the exposed run

If the purpose of the AC cable is solely for physical protection of the thermostat wire, consider using a non-metallic conduit like PVC or ENT (electrical nonmetallic tubing). You can transition to the nonmetallic conduit at a junction box and run the thermostat wire inside the conduit to the HVAC unit.3.

Verify AC Cable & Use Appropriate Connector
Double-check that the EZ-IN is actually AC cable and not MC cable. AC cable has a bond strip in contact with the armor. MC does not. Find an AC cable connector that is UL listed for bonding to ground. Connect the EGC wire in the AC cable to the ground wire on the house side.

Important Considerations and Cautions
NEC (National Electrical Code)

Always consult the latest edition of the NEC and local electrical codes. The following sections will be helpful:

Article 250

Grounding and Bonding


Article 320

Armored Cable: Type AC

Local Inspector

Before proceeding with any solution,
talk to your local electrical inspector. They can provide specific guidance based on your local codes and the specifics of your installation. This is especially important because you're dealing with a grounding and bonding issue, which can have safety implications.

Don't Compromise Safety

Never sacrifice safety to save time or money. If you're not comfortable with any of these solutions, hire a qualified electrician.

Don't Rely on 'Hope'

Don't assume a connector will provide a bonding path just because it's metal.
Verify that it's designed to make that connection.

Verify Grounding

After completing the installation, test the grounding path with a multimeter to ensure continuity between the AC cable armor and the grounding system.

In Summary


Bonding AC cable to a non-metallic HVAC unit requires a creative solution. Using a metallic junction box to act as a bonding point is generally the most code-compliant approach. Switching to a non-metallic conduit system could also eliminate the issue entirely. Regardless, consult your local inspector before proceeding. Remember to always prioritize safety and code compliance. Flag for review