User: hhsting, Location: Glen bunie, md, us

Asked on: Thursday, August 1, 2024 at 2:39 pm EDT
Answered on: Thursday, March 6, 2025 at 12:36 am EST

Question: I have fire pump 40HP 200V three phase with fla of 115A.The contractor is providing ocpd as main service disconnect. I have not on plans that says ocpd is 400A trip and in compliance with NEC 2017 Article 695.4(B)(2)(a). See below.The 400A trip is very questionable for 40Hp three phase 200V fire pump of 115A.How can it comply withNEC 2017 Article 695.4(B)(2)(a)?

You're right to question this. A 400A overcurrent protective device (OCPD) for a 40HP, 200V, 3-phase fire pump with an FLA of 115A does seem oversized at first glance. However, NEC Article 695.4(B)(2)(a) specifically addresses fire pump OCPD sizing, and it allows for a significantly larger OCPD than you would typically use for motor protection.Here's a breakdown of how it can comply, and what the contractor needs to demonstrate

NEC 2017 Article 695.4(B)(2)(a) Key Points:
"The overcurrent protective device shall be sized to carry indefinitely the sum of the locked-rotor current of the fire pump motor(s) and the full-load current(s) of all other equipment connected to the fire pump circuit(s)." This is the crux of the issue. It allows for an OCPD to be sized above the usual motor protection limits to ensure the fire pump never trips unnecessarily during a fire. Locked Rotor Amps (LRA)

This is the critical value. The code requires you to size the OCPD based on the LRA, not the FLA. The LRA is typically much higher than the FLA (usually 6-8 times higher).

Steps to Determine Compliance


Determine the Locked Rotor Amps (LRA) of the Fire Pump Motor

This is the most important step. You need to find the LRA on the motor nameplate or in the motor manufacturer's data sheets. Let's assume, for example, the LRA is 7 times the FLA: LRA = 115A 7 = 805A (This is just an example; you must use the actual LRA from the motor.)2.

Other Loads

Article 695.4(B)(2)(a) also needs to consider any other loads. Let’s assume there are no other loads, we'll skip this point for now, if there are any other loads their FLA must be added to the LRA.3.

Verify OCPD Size

The OCPD must be able to carry the LRA. In this example, the LRA (805A) is

greater
than 400A. So the 400A is not complaint.

Important Considerations



Selective Coordination

Article 695 requires selective coordination of the fire pump circuit. This means the fire pump breaker must trip
last in a fault condition, allowing upstream breakers to clear the fault first and minimizing the impact on other essential circuits. The large OCPD size is part of achieving this coordination.

Documentation

The contractor must provide documentation showing how the OCPD size was calculated and how it complies with Article 695. This should include the motor nameplate data (including LRA) and calculations. Request this from the contractor immediately.

Motor Protection

The large OCPD is

not
intended to provide standard motor overload protection. The motor itself should have integral overload protection or a separate overload relay to protect it from sustained overloads. The OCPD is primarily for short-circuit and ground-fault protection while allowing the pump to run under heavy load conditions. AHJ Approval

Ultimately, the Authority Having Jurisdiction (AHJ) has the final say on whether the installation complies with the code. Present your concerns and the contractor's documentation to the AHJ for review.

Voltage Drop

With such high potential currents at LRA, also check voltage drop calculations.

In Summary

The 400A OCPD
can comply, if* the motor LRA is less than or equal to the OCPD rating. The contractor needs to provide the following for you to properly assess the installation:1.

Motor Nameplate Data (Specifically the LRA)

This is absolutely essential.2.

Calculations

Show how the OCPD size was determined and how it meets the requirements of Article 695.4(B)(2)(a).
3.


Selective Coordination Study (if required by the AHJ):
This demonstrates that the fire pump breaker is selectively coordinated with upstream breakers.Without the LRA from the motor nameplate, it is impossible to determine if the 400A breaker is compliant. Based on the example above, the 400A is too small. If the contractor cannot provide this information, you should reject the installation. Flag for review