Topic: System grounding and neutral-to-case bonding for each store in a mall

User: alej27, Location: Venezuela

Asked on: Thursday, August 1, 2024 at 2:57 pm EDT
Answered on: Thursday, March 6, 2025 at 12:37 am EST

Question: I have a question regarding grounding and bonding, in the case of a multi-store mall.Consider a mall, with a dedicated transformer connected to the primary distribution lines on the HV side (say 13.8 kV). The LV side (say 240/120 V) conductors of the XFMR are then run to a set of cabinets. First, a main breaker (say 600 A) is encountered in a vertical cabinet. Then, the conductors are run to an adjacent horizontal cabinet with two-pole distribution breakers (say 70 A), one for each store. Then, the load-side of those breakers are connected to individual meters in another cabinet, again one for each store. Only the PoCo (power company) has access to the three previous cabinets. Finally, from the meters, conductors are run to another vertical cabinet with also two-pole distribution breakers, again one for each store, but now the mall owner has access to this cabinet; after each distribution breaker in this cabinet, conductors are run to the main panelboard of each store of the mall.I'd like to know how should the grounding and bonding (only connections) be done in this scenario, in two cases: 1) private transformer (owned by the mall); 2) utility-owned transformer.For case #1, I suppose that if it the transformer secondary neutral is not connected to the primary neutral, then the transformer is considered a SDS (separately derived system), hence the secondary neutral must be grounded and be bonded to the XFMR enclosure. Downstream of the XFMR enclosure, the neutral and ground wires are kept separate for each store. The main panelboard of each store must have the neutral and ground terminal bars separate. If each store owner want to, they can install more ground rods, connected to the ground (not neutral) terminal bar of their main panel. Is this correct? This is shown below.For case #2, would the answer be the same? Or would somehow the main panel of each store receive the two hots plus neutral with no ground wire, and then require to bond and ground their neutral (for each store)?

You've outlined the key concepts correctly, but let's refine the details for clarity and code compliance (referencing the NEC - National Electrical Code in the US, which is a common benchmark)

Understanding Key Terms
Separately Derived System (SDS)

As you mentioned, a transformer is an SDS if its secondary neutral is
not connected to the primary neutral. The key is direct electrical connection. The connection can be through equipment grounding conductors.

Grounding Electrode System (GES)

The system of grounding electrodes (ground rods, building steel, water pipes, etc.) that provides a path to ground.

Bonding

Connecting metallic parts (enclosures, conduit, etc.) to create a low-impedance path for fault current. This path ultimately leads back to the source (transformer neutral) allowing the overcurrent protective device to operate.


Equipment Grounding Conductor (EGC)

The wire (or conduit) that provides the fault current path for metal enclosures and non-current-carrying metal parts.

Neutral Conductor

The current-carrying conductor that is intentionally grounded.

Case #1: Privately Owned Transformer


Your understanding of a privately owned transformer scenario is mostly accurate. Let's break it down step-by-step:1. Transformer as SDS (Most Likely Scenario)

Unless there's a specific reason and approval from the Authority Having Jurisdiction (AHJ), the secondary neutral should
not be connected to the primary neutral. This is standard practice for safety and coordination reasons. Therefore, you are correct in treating it as an SDS.2.

Grounding at the Transformer (NEC 250.30)



Grounding Electrode Conductor (GEC)

A grounding electrode conductor (GEC) must connect the secondary neutral (X0 terminal, or the center-tapped point in your 240/120V system) to a grounding electrode system (GES). This GES can include: A ground rod. A concrete-encased electrode (Ufer ground) if it exists. The building steel (if properly grounded). Underground metal water pipe (with specific bonding requirements).

Bonding Jumper

A bonding jumper connects the secondary neutral terminal block to the transformer enclosure. This ensures that the enclosure is at the same potential as the neutral.


Size of GEC and Bonding Jumper

The size of the GEC and bonding jumper are determined by NEC Table 250.66, based on the size of the largest ungrounded (hot) conductor feeding the transformer.
3.


Downstream Distribution (Cabinets and Breakers)



Separate Neutral and Ground

After the transformer, the neutral and equipment grounding conductors
must be kept separate all the way to the load (i.e., the store's main panel). This is crucial.

Equipment Grounding Conductor (EGC)

From the transformer enclosure, an EGC (wire or metallic conduit) must run with the circuit conductors (hot and neutral) to each distribution cabinet, then to the meter cabinet, then to the last distribution cabinet before each store, and ultimately to each store's main panel. This EGC provides the fault current path. Use a green insulated wire.

Conduit and Metal Enclosures

All metallic conduit and metal enclosures must be properly bonded together to create a continuous fault current path. This can be achieved using bonding bushings and jumpers.4.

Store's Main Panel



Separate Neutral and Ground Bars

Absolutely correct. The neutral and ground bars must be separate. The neutral conductor from the meter connects only to the neutral bar.

Equipment Grounding Conductors

All equipment grounding conductors from circuits within the store (from branch circuits to receptacles, lights, etc.) connect to the ground bar.


No Neutral-to-Ground Bond

There must not be a connection between the neutral bar and the ground bar in the store's main panel. This avoids parallel neutral current and ground loops, which can cause safety issues and nuisance tripping.5.

Supplemental Grounding Electrodes (Store Owner's Option)



Permitted, Not Required

While not required by the NEC for a service panel, a store owner
can install additional ground rods.

Connect to Ground Bar

If they do, the ground rod conductors must connect to the ground bar in their main panel, never to the neutral bar.

Case #2: Utility-Owned Transformer


This case is different and often misunderstood:1. Utility Responsibility

The utility is responsible for grounding their transformer and the service up to the service point. The service point is the location where the wiring leaves the control of the utility. In your scenario, the service point would typically be at the first set of cabinets (where the 600A main breaker is located).2.

Service Entrance

From the service point to the first disconnect (600 A main breaker in your case), it is considered a service entrance.3.

Grounding at the Service Entrance (NEC 250.24)



Service Neutral Grounding

The neutral conductor of the service
must be grounded at the service equipment (the 600A main breaker enclosure).

Grounding Electrode System (GES)

The neutral conductor must be connected to a grounding electrode system (GES) consisting of: A metal underground water pipe, electrically continuous for at least 10 feet and in direct contact with the earth. The building steel, if effectively grounded. A concrete-encased electrode (Ufer ground) if it exists. A ground ring encircling the building. Rod and pipe electrodes are supplemental to these electrodes.

Bonding

All metal enclosures (conduit, cabinets) from the service point to the 600A main breaker must be bonded together to form a continuous fault current path.4.

Downstream Distribution (After the 600A Main Breaker)



The important difference

Downstream of the 600A main breaker, the system is still considered service equipment. The grounding requirements remain the same as if it were your own privately owned transformer.

Separate Neutral and Ground

The neutral and equipment grounding conductors must be kept separate all the way to the load (i.e., the store's main panel).

Equipment Grounding Conductor (EGC)

From the 600A main breaker enclosure, an EGC (wire or metallic conduit) must run
with the circuit conductors (hot and neutral) to each distribution cabinet, then to the meter cabinet, then to the last distribution cabinet before each store, and ultimately to each store's main panel. Use a green insulated wire.

Conduit and Metal Enclosures

All metallic conduit and metal enclosures must be properly bonded together to create a continuous fault current path.5.

Store's Main Panel



Same as Case #1

Exactly the same as in Case #1. Separate neutral and ground bars. No neutral-to-ground bond. Grounding conductors connect to the ground bar. Supplemental ground rods connect to the ground bar.

Key Differences Summary - Utility vs Private XFMR
Utility-Owned

The utility owns and is responsible for the grounding up to the service point and up to the first disconnect in the building. From there, the same grounding rules apply as with your private transformer. However, since the utility grounds the neutral upstream, you (or the electrical contractor) must still ground the neutral conductor at the service entrance equipment.

Privately-Owned

You are responsible for grounding
at the transformer. This is an SDS, and the grounding requirements are slightly different, even if the end result at the store panel is the same.

Important Considerations and Code References
NEC Article 250

This is the core article for grounding and bonding requirements. Pay close attention to 250.24, 250.30, and 250.
104.


NEC Article 300

Wiring methods and materials; critical for proper installation and bonding of raceways and enclosures.


Coordination with Utility

Always coordinate with the utility company regarding their grounding practices and requirements, especially for a utility-owned transformer. They may have specific standards that must be met.

Authority Having Jurisdiction (AHJ)

The local electrical inspector has the final say. Consult with them during the design phase to ensure compliance with local codes and interpretations.


Qualified Personnel

This work should only be performed by qualified and licensed electricians who are familiar with the NEC and local codes. Incorrect grounding and bonding can be extremely dangerous.

Documentation

Keep detailed documentation of all grounding and bonding connections for future reference and maintenance.


Fault Current Study

A fault current study is recommended for a multi-store mall to ensure that the overcurrent protective devices (breakers and fuses) are properly sized to interrupt fault currents safely.

In summary:
The fundamental principle is that after the transformer (whether privately owned or utility-owned), the grounding system must provide a low-impedance path for fault current to return to the source, allowing overcurrent protective devices to operate quickly and safely. Maintaining separate neutral and ground conductors downstream of the transformer is crucial for proper operation and safety. Your original diagram is correct for the connection points in each store. Flag for review