User: Pats3327, Location: 44202
Asked on: Thursday, August 1, 2024 at 3:02 pm EDT
Answered on: Thursday, March 6, 2025 at 12:37 am EST
Question: We have control panels that have dual 120vac feeds, one commercial power and one UPS power.Should the grounds for each be run independently back to the plant ground grid, or can they be bonded together in the control panel, and run one ground wire back to plant ground grid?Each feed is 20 amps or less.
According to NEC (National Electrical Code) you MUST bond the grounds together in the control panel. You cannot have separately derived ground systems.Here's a breakdown of the reasoning and relevant code sections: Safety Imperative: Ground Fault Path
The primary purpose of grounding is to provide a low-impedance path back to the source in the event of a ground fault. This path allows sufficient current to flow to trip a circuit breaker or blow a fuse, quickly disconnecting the faulted circuit and preventing shock hazards.
Common Grounding System
All electrical equipment in a building or facility must be connected to a common grounding system. This ensures that all metallic parts that could become energized are at the same electrical potential. This is critical for preventing a potential difference between different pieces of equipment, which could create a shock hazard.
Separately Derived Systems are Different
While the UPS is technically a separately derived system, this is not why they must be bonded at the panel. The grounds MUST be tied together to prevent circulating current, which can cause issues with equipment operation. If your UPS did require a separate ground, it would need to be bonded at the source.
NEC Relevant Sections (Examples - consult the latest code for definitive guidance)
NEC 250.20(B): AC Systems to Be Grounded
Requires AC systems to be grounded in a manner that establishes an effective ground-fault current path.
NEC 250.24(A): Grounding Service-Supplied AC Systems
Defines how the grounding electrode conductor is connected to the service equipment.
NEC 250.30(A)(1): Grounding Separately Derived AC Systems
This section is often misinterpreted. While it addresses grounding separately derived systems, the KEY is understanding that the UPS output becomes part of the overall building electrical system when it feeds the control panel. This reinforces the need for a common ground within the panel.
NEC 250.130 Equipment Grounding and Equipment Grounding Conductors
Covers how to ground equipment supplied by branch circuits or feeders.
NEC 250.96 Bonding Other Enclosures The control panel must be bonded to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on it.
What to Do
Bonding
Within the control panel, securely bond the equipment grounding conductors (green wires or bare wires) from both the commercial power feed and the UPS power feed to a common ground busbar or terminal block.2.
Single Grounding Conductor
Run a single, appropriately sized equipment grounding conductor from this common ground point within the control panel back to the plant's grounding grid.3.
Sizing the Grounding Conductor
The size of this grounding conductor must be determined based on the overcurrent protection device (circuit breaker or fuse) protecting the feeders to the control panel. Refer to NEC Table 250.122 for proper sizing.
4.
Never Use the Metal Enclosure Only as a Ground
Always run a dedicated ground wire in addition to relying on the metal enclosure.
Important Considerations
Continuity
Ensure that all metallic enclosures and components within the control panel are properly bonded together and to the ground busbar.
Tight Connections
Use proper connectors and ensure all connections are clean and tight to minimize impedance in the ground fault path.
Inspect
Periodically inspect the grounding connections to ensure they are secure and free from corrosion.
Qualified Electrician
This work should be performed by a qualified and licensed electrician who is familiar with the NEC and local electrical codes. They can ensure that the grounding system is installed correctly and safely.
Document
Keep records of all grounding connections and inspections.
In summary, to comply with the NEC and ensure safety, you must bond the grounds from the commercial power and the UPS power together within the control panel and run a single, appropriately sized ground wire back to the plant ground grid. This creates a common grounding system, provides a low-impedance fault current path, and minimizes the risk of electrical shock. Flag for review