User: Mumbaigirl, Location: USA
Asked on: Thursday, August 1, 2024 at 4:18 pm EDT
Answered on: Thursday, March 6, 2025 at 12:37 am EST
Question: I have a 480V Siemens P5 Panelboard with 1200A 3P-LNX Main Breaker with a 555 ETU-LSIG, GF Trip with a neutral sensor (CT).This panel is currently fed from a from a 13.2 - 480V Xfmr. We are now eliminating the transformer and bringing in a direct 480V feed to this panel from one of the MCCs. I want to know if not wiring the neutral thereby not using the neutral CT in the panelboard will be okay. Will there be something that I need to change in the 555-trip unit to disable the GF trip? The panelboard has three 3P-LMX breakers that feeds rental units.
Okay, let's break down this situation and the steps you need to take to safely and correctly transition to a direct 480V feed for your Siemens P5 panelboard.
Understanding the Situation Panelboard Setup
You have a 480V panelboard with a main breaker (Siemens 1200A 3P-LNX with 555 ETU-LSIG trip unit and GF trip with neutral CT). The panelboard feeds three 3-pole LMX breakers that feed rental units.
Original Configuration
Fed by a 13.2kV-480V transformer. This transformer likely provided a solidly grounded wye system, giving you a neutral.
New Configuration
Direct 480V feed from an MCC. This is important because it determines the grounding type of the new source. The MCC must have a solidly grounded source in order for the GF protection system to work properly.
Key Considerations and Questions1. MCC Grounding Type
This is the MOST critical factor.
What type of grounding system is used in the MCC that will now feed the panelboard? Solidly Grounded Wye
If the MCC provides a solidly grounded wye 480V system (meaning the neutral point of the source transformer is directly connected to ground), your ground fault protection can function correctly, but you still need to evaluate if it should function.
High Resistance Grounded
If the MCC uses a high resistance grounding system, the panelboard will no longer be properly grounded to function correctly.
Ungrounded (Delta) System
If the MCC provides an ungrounded delta system, your ground fault protection system cannot function. You MUST disable or remove it.2.
Neutral Load Imbalance
Do the rental units have significant neutral current due to single-phase loads? Even if the source is a solidly grounded system, you may have to eliminate the use of the GF protection for this circuit to prevent nuisance tripping.3.
Code Compliance (NEC)
The NEC (National Electrical Code) dictates requirements for ground fault protection in specific situations. Consult the applicable sections of the NEC based on your application. The typical rule of thumb is that you need ground-fault protection for solidly grounded wye electrical services of more than 150 volts to ground, but not exceeding 1000 volts phase-to-phase for each service disconnect rated 1000 amperes or more.
Steps to Take1. Determine MCC Grounding Configuration
Absolutely the first step. Trace the wiring back to the MCC transformer and identify the grounding method. Get the MCC electrical drawings. Without this information, you cannot proceed safely.2.
Evaluate Ground Fault Protection Needs
NEC Requirements
Does the NEC mandate ground fault protection in this scenario? Consider the size of the service, the type of occupancy, and any specific local amendments to the NEC.
Operational Necessity
Do you need ground fault protection on this panelboard? GF protection adds a layer of safety, but can cause nuisance tripping if not applied correctly. Consider the consequences of a ground fault and whether other protective devices (overcurrent protection) would adequately protect the equipment and personnel.3.
If Ground Fault Protection is Required/Desired (and the source is solidly grounded)
Neutral Connection
Connect the neutral conductor from the MCC to the neutral busbar in the panelboard. Ensure the neutral CT (current transformer) encircles the neutral conductor.
ETU-LSIG Trip Unit Settings
Verify that the ground fault trip setting (GF setting) on the 555 ETU-LSIG trip unit is appropriate for the application. You may need to adjust the pickup and time delay settings. Consult the Siemens documentation for the trip unit.
Testing
After installation, perform a ground fault test to ensure the system is functioning correctly. Use a primary injection test kit or similar device to simulate a ground fault and verify that the breaker trips.4.
If Ground Fault Protection is NOT Required/Desired (or the source is not solidly grounded)
Neutral Isolation
Do NOT connect the neutral conductor from the MCC to the panelboard neutral busbar. Leave it disconnected and properly insulated.
Disable or Remove GF Protection
This is the critical step. You have two options:
Disable
If the 555 ETU-LSIG trip unit allows you to completely disable the ground fault function (via a setting in the trip unit), this is the preferred method. Consult the Siemens documentation to determine how to disable the GF function.
Remove
If disabling is not possible, you may need to physically remove the neutral CT. In this case, you will need to determine if the breaker needs a specific termination after the CT has been removed.
Documentation
Clearly document that the ground fault protection has been disabled or removed and the reasons for doing so.
Important Cautions Qualified Electrician
This work MUST be performed by a qualified and licensed electrician who is familiar with 480V systems, panelboards, and ground fault protection.
Siemens Documentation
Consult the Siemens documentation for the P5 panelboard, the 1200A 3P-LNX breaker, and the 555 ETU-LSIG trip unit. This documentation will provide critical information about the trip unit settings, disabling/removing ground fault protection, and safe installation practices.
Coordination Study
Ideally, a short circuit and coordination study should be performed to ensure that the protective devices (breakers) are properly coordinated to protect the equipment and personnel. This is especially important when changing the source of power.
Lockout/Tagout
Always follow proper lockout/tagout procedures before working on any electrical equipment.
In Summary
The success of this transition hinges on understanding the grounding type of the new 480V source. If the MCC provides a solidly grounded wye system, you may be able to keep the ground fault protection. Otherwise, you MUST disable or remove the GF protection to prevent nuisance tripping and ensure the safety of the system. Always consult with a qualified electrician and refer to the manufacturer's documentation for specific instructions and safety precautions. Flag for review