Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Running three phase circuit from disconnect

User: fkeeney, Location: WV

Asked on: Thursday, August 1, 2024 at 8:00 pm EDT
Answered on: Thursday, March 6, 2025 at 12:38 am EST

Question: I am hoping someone can give me some advice on running a 3 phase circuit. Basically, I have 5 machines that need electrical supply. I have a 20Hp RPC powered by single phase 200A load center with 100amp double pole breaker pushing out three phase from the converter panel into a 100amp disconnect. From the bottom lugs of that disconnect I was hoping that I could run #6 wire to the first machine contactor then somehow carry on that supply to the next machine's contactor without the need to buy a three phase panel and breakers($$$$). I was also hoping that I could run a second "circuit" to essentially daisy chain to the other three machines.1st supply line: disconnect to Table saw 5hp to Planer 9hp,2nd supply line: disconnect to Shaper 7.5hp to Radial Arm Saw 5hp to Jointer 3hpWith both of these originating at the bottom lugs of the disconnectOnly one machine will ever be powered on at a time. I assumed that the contactors, with their voltage overload protection, would allow it to be done. I don't know if this setup would require some sort of junction box to be able to "y" off to each machine at that point or if the power would be run from contactor to contactor? This project will not be inspected but safety is a concern.Please advise lolthanks in advanceFrank

Okay, Frank, let's break down your 3-phase wiring plan. While your intentions are good regarding cost-saving, there are some significant safety and code concerns with daisy-chaining high-powered machinery like this, even if only one runs at a time.

Here's a breakdown of the issues and recommendations



1. Overcurrent Protection (Crucial for Safety)



The Problem

Your primary concern must be overcurrent protection (fuses or breakers). Relying
solely on the contactor's overload protection is not sufficient. Overload protection protects the motor from sustained overcurrent (like a jammed blade). It does not protect the wiring from short circuits or ground faults. A short circuit will quickly melt wiring and create a fire hazard.

The Code Requirement (and common sense)

The National Electrical Code (NEC) requires overcurrent protection at the point where conductors receive their supply. In your current plan, you only have a 100A breaker at the disconnect. This only protects the wire running from the disconnect. If the Tablesaw (5hp) had a short circuit, the #6 wire might burn up before the 100 amp breaker trips. Each machine needs its own breaker to properly protect the wiring and equipment.

Why Daisy-Chaining is Problematic

Daisy-chaining means the same #6 wire is carrying current for multiple machines. If a fault occurs in the last machine in the chain, the entire length of that #6 wire is exposed to potentially dangerous current levels until the 100A breaker trips. This increases the risk of fire and damage.

2. Wire Sizing and Ampacity



The Problem

#6 AWG wire has a limited ampacity (current-carrying capacity). While it might be sufficient for the largest single motor running, it's likely inadequate to feed the whole chain of machines if they were to all start simultaneously or experience a fault condition. Even though you only run one at a time, the potential for a fault drawing more current than the wire is rated for exists.

NEC and Best Practice

Wire ampacity must be suitable for the
potential load, not just the typical load. The NEC has complex calculations for motor circuits, considering starting currents (which can be several times higher than running current).

3. Contactor Overload Relays



Purpose

Contactor overload relays are important for protecting the motor itself from overheating due to sustained overloads (e.g., trying to cut too thick a piece of wood).

Limitation

They do
not protect the wiring from short circuits or ground faults. They are relatively slow to react. A short circuit needs immediate interruption.

4. Disconnect Switch Location
Good Practice

The disconnect switch is ideally located within sight of the machines. Having only one at the RPC and running the conductors across the shop is not the most efficient solution.

Recommendations and Alternatives



The Right Way: A Proper 3-Phase Panel
This is the safest and most code-compliant approach. It involves installing a small 3-phase panel with appropriately sized breakers for each machine. Cost Consideration

Yes, it's an upfront cost, but it's an investment in safety and long-term reliability. Look for used or surplus panels to save money. Even a small 6 or 8-circuit panel would likely suffice.


Wiring

Run individual conductors from the 3-phase panel to each machine, with each circuit protected by a properly sized breaker. This allows for individual machine isolation and overcurrent protection.

Breaker Sizing

Calculate the Full Load Amps (FLA) for each motor. The breaker size should typically be sized at 125% of the FLA. Consult the motor's nameplate for FLA or use online charts for common motor HP ratings.


Wire Sizing

The wire size is based on the breaker size and the distance of the run. Use the NEC ampacity tables to ensure the wire is properly sized.

A Compromise (If absolutely budget-constrained)



Individual Disconnects and Fuses

If a 3-phase panel is entirely out of reach financially at this moment (though I still highly recommend saving for one), you could potentially use individual 3-phase disconnects with fuses at each machine.

How it Would Work

1. Run the #6 wire from the main disconnect (or better yet, a slightly larger gauge, depending on the total calculated load) to a
junction box.2. From the junction box, run individual conductors to each machine's 3-phase disconnect/fused switch.3. The fuses within each disconnect would provide the necessary overcurrent protection for the wiring to that specific machine. The fuse size would be based on the motor's FLA.

Important Caveats

This is not ideal, and a 3-phase panel is still better. You MUST carefully calculate the total load on the #6 wire to ensure it's adequate. The junction box must be properly sized and rated for the voltage and amperage. The disconnects and fuses must be 3-phase rated and sized appropriately for the motor's FLA. This setup may not meet code, even if not inspected.

Example Calculation (Illustrative)

Let's take your 5HP table saw motor. Let's assume it draws 15 amps at 230V 3-phase (check your motor nameplate for actual FLA).1.

Breaker/Fuse Sizing

15 amps x 1.25 = 18.75 amps. You'd likely use a 20-amp breaker or fuse.
2.


Wire Sizing

For a 20-amp circuit, #12 AWG copper wire is typically sufficient (check NEC tables for ampacity at your installation's temperature rating).

Critical Safety Precautions (Regardless of the Chosen Method)



Grounding

Ensure that all machines are properly grounded to the electrical system. This is critical for safety.

Qualified Electrician

If you're not 100% confident in your electrical skills,
hire a qualified electrician. Electricity is dangerous, and mistakes can be fatal. At the very least, have an electrician review your plans.

Local Codes

Even if not inspected, try to adhere to local electrical codes as much as possible. They are there for a reason.

Lockout/Tagout

Implement a lockout/tagout procedure to ensure that machines are de-energized before maintenance or adjustments.

In summary:


While trying to save money is understandable, the safest and most reliable approach is to install a proper 3-phase panel with individual breakers for each machine. This provides the necessary overcurrent protection and allows for individual machine isolation. If you
must* pursue a more budget-conscious option, use individual fused disconnects at each machine, but understand the limitations and potential risks. Always prioritize safety and consult with a qualified electrician.Good luck with your workshop project! Flag for review

Previous Question Next Question