Question: When using a MIGB are they usually only installed at pull boxes or everywhere along the run where the conduit terminates? Equipement etc.? Thanks
MIGBs (Main Bonding Jumpers) or equipment grounding conductors are required at each service equipment enclosure, not usually along the run of conduit or at every pull box. Here's the general principle and specific considerations
Where MIGBs/Grounding Conductors are Required:
Service Equipment
Absolutely required at the service equipment enclosure. This is where the electrical service enters the building. This ensures a low-impedance path back to the source for fault currents.
Separately Derived Systems (SDS)
Required at each SDS, such as a generator or transformer.
Equipment
Equipment grounding conductors are required to ground enclosures and non-current carrying metal parts of equipment.
Where MIGBs/Grounding Conductors are NOT Typically Required
Pull Boxes
Generally, you do not need a bonding jumper inside a pull box if the metallic conduit is properly installed and creates a continuous electrical path. However, there are exceptions (see below).
Along Conduit Runs
No, you don't need a grounding jumper at every point where conduit sections are joined. The conduit itself, when properly installed (with tight connections), is intended to serve as the equipment grounding conductor.
Exceptions and Considerations
Conduit Integrity
If you have reason to believe the conduit system is not providing a reliable ground path (e.g., loose connections, corrosion), you might consider adding a bonding jumper across a section. Use appropriately sized grounding bushings and bonding jumpers to bond the conduit to the enclosure at each end, if the enclosure is not designed for threaded conduit connections. When non-metallic conduit is used, an equipment grounding conductor must be installed within the conduit.
Long Runs
For very long conduit runs, impedance can become a factor. In some cases, particularly with larger systems, a separate equipment grounding conductor within the conduit might be required to supplement the conduit's grounding capability. This is less common in typical installations but important to consider.
Special Conditions
Hazardous Locations: Bonding requirements are often stricter in hazardous locations. Sensitive Equipment: Certain sensitive electronic equipment may require additional grounding measures to minimize noise or interference.
Code Requirements
Always consult the latest edition of the National Electrical Code (NEC) for specific requirements and exceptions in your area. Articles 250 and 300 are especially relevant.
In Summary:
Think of the grounding system as a chain. The strongest links need to be at the points where power enters (service equipment, SDSs), and where it connects to equipment. The conduit run itself serves as a link in the chain. You only need to reinforce the chain along the run if there's a weak link (e.g., poor conduit connections or a very long run). If you are not certain if a proper ground exists, install a redundant ground as part of your wiring practice.Always follow the NEC and local electrical codes, and consult with a qualified electrician if you have any doubts. Flag for review