Question: I installed a new photocell on some Parking Lot lights. When the photocell turns the lights off at Dawn the Breaker will trip also. I think it's a bad breaker. Going Monday to check into situation. Works fine until photocell turns lights of in the morning.
Okay, this is a tricky situation that definitely warrants a careful investigation. Here's a breakdown of possible causes, along with steps you should take when you investigate on Monday. Don't assume it's just a bad breaker until you've ruled out other possibilities.Possible Causes & Troubleshooting Steps
1. Overloaded Circuit (Most Likely Suspect)
The Core Issue
When the photocell switches off, there might be a surge or spike in current as the inductive load (the lights' ballasts or drivers) collapses. This can briefly exceed the breaker's rating.
Check the Load
Total Wattage
Carefully add up the wattage of all the lights on that circuit. Make sure the total wattage is significantly below 80% of the breaker's capacity (continuous load rule for breakers). For example, a 20A breaker at 120V is 2400VA, 80% of that is 1920VA.
Voltage Drop
Measure the voltage at the last light fixture in the circuit, both when the lights are on and when they are off. A significant voltage drop when the lights are on indicates the circuit is overloaded or has wiring issues.
Troubleshooting
Reduce Load
The simplest test is to temporarily remove one or two lights from the circuit to see if that stops the breaker from tripping.
Redistribute Load
If possible, move some of the lights to another circuit.
2. Inrush Current (Another Strong Possibility)
The Core Issue
Some lights, especially those with older ballasts or LED drivers, have a high inrush current when they are first turned on. While this shouldn't be a problem when turning off, it is plausible that the sudden change in state could cause a transient inrush. This is more likely with electronic ballasts/drivers that are not properly designed to handle the switching.
Troubleshooting
Use a Slow-Blow Breaker
Consider replacing the standard breaker with a "slow-blow" or "time-delay" breaker (Type D breakers in some standards). These breakers are designed to tolerate brief overcurrent surges, which is exactly what an inrush current is. Be sure the slow-blow breaker is appropriately sized for the wiring and the load.
Install Inrush Current Limiters
There are devices specifically designed to limit inrush current. These can be installed at the light fixtures or at the panel.
3. Wiring Problems
The Core Issue
A loose connection, damaged wire, or a near short-circuit somewhere in the lighting circuit can cause excessive current draw, especially when the circuit changes state (lights turning on or off).
Troubleshooting
Inspect Wiring
Carefully examine all wiring connections at the photocell, the breaker, and at each light fixture. Look for loose wires, corroded connections, burnt insulation, or any signs of damage. Pay special attention to the neutral connections.
Test for Shorts
Use a multimeter to test for shorts between the hot (live) wire and the neutral wire, and between the hot wire and ground. Do this with the breaker turned OFF! You should see very high resistance (ideally infinite) in both cases.
4. Faulty Photocell
The Core Issue
While less likely, a faulty photocell could be creating a surge or transient when it switches off. This is more likely if it's a cheap or poorly designed unit.
Troubleshooting
Test with a Different Photocell
Temporarily replace the new photocell with a known good one (if you have one available) to see if the problem goes away.
5. Bad Breaker (Possible, but Less Likely)
The Core Issue
Breakers can weaken over time and become more sensitive to tripping.
Troubleshooting
Test the Breaker
This is best done by a qualified electrician. A breaker tester can apply a specific load to the breaker to see if it trips at the correct current and time.
Replace the Breaker
If you suspect the breaker is faulty, replace it with a new one of the exact same type and amperage rating.
Steps to Take on Monday (in order)
Safety First
Always turn off the breaker before working on any electrical components. Use appropriate personal protective equipment (PPE), including insulated gloves and safety glasses.2.
Check the Breaker
Verify the breaker's amperage rating matches the circuit's requirements and that it's properly seated in the panel.3.
Inspect Wiring at Photocell
Carefully examine the wiring connections at the photocell. Make sure they are tight, clean, and properly insulated. Verify the photocell is rated for the voltage and amperage of the circuit.4.
Measure Voltage and Current
Use a multimeter to measure the voltage and current on the circuit while the lights are on. Record these readings. Also measure the voltage at the furthest light from the panel.5.
Monitor Current at Turn-Off
If possible, use a clamp meter to monitor the current on the circuit as the photocell turns off the lights. This will help you identify if there's a surge or spike in current.6.
Inspect Wiring at Light Fixtures
Check the wiring connections at each light fixture, looking for loose wires, corrosion, or damage.7.
Reduce the Load
Temporarily disconnect some of the lights to see if the problem disappears.8.
Test/Replace Photocell
If possible, swap out the photocell with a known good one.9.
Replace Breaker (If Necessary)
If you've ruled out all other causes, replace the breaker with a new one of the same type and amperage.
Important Considerations
Licensed Electrician
If you're not comfortable working with electricity, hire a qualified and licensed electrician. Electrical work can be dangerous and can lead to serious injury or property damage.
Code Compliance
Ensure all work complies with local electrical codes and regulations.
Document Everything: Keep a record of all tests, measurements, and changes you make. This will help you track down the problem and communicate with an electrician if needed.By systematically investigating these possibilities, you should be able to pinpoint the cause of the breaker tripping and resolve the issue. Good luck! Flag for review