Question: Hello all, i have a little confusion regarding 220.84 Multifamily Dwelling demand factor. I have a condomium building that has 30units. This building will require at least 2 meter center services to feed. My question is in regards to the demand factor %factor. Since each meter center is going to take care of 15 units. Do each meter center gets calculated seperate.So for example:Meter Center 1: 15 units - 40% Demand factorMeter Center 2: 15 units - 40% Demand factorORMeter center 1 + 2: 30 units - 33% Demand factor.As you see the demand and sizing of meter centers will come out to be a different based on which route you take. Which is the correct way to do it?Thank you
You are correct to be thinking about this carefully. The answer lies in understanding what 220.84 is trying to accomplish and how it's worded.Here's the breakdown: Purpose of 220.84
This section allows for reduced demand factors for the service or feeder supplying multiple dwelling units in a multifamily dwelling. It's based on the statistical likelihood that not all units will be drawing peak power simultaneously.
The Key Wording
The NEC 220.84 wording is crucial: "(A) Service or Feeder. The load for household ranges, wall-mounted ovens, counter-mounted cooking units, and electric dryers in a dwelling unit shall be permitted to be calculated in accordance with Table 220.55, Table 220.54, and 220.53, respectively. (B) Total Load. The calculated load of the service or feeder shall be permitted to be based on Table 220.84." Table 220.84 refers to: Number of Dwelling Units with the associated demand factor %.
The Correct Approach
You apply the demand factor based on the total number of dwelling units served by the service or feeder you are calculating. In your case, the
entire service is serving 30 units. Therefore, you use the 30-unit demand factor (33% according to Table 220.84). Meter Center 1 + 2: 30 units - 33% Demand factor. Each meter center serves as feeder that are part of the main feeder. Why this is the correct approach
Diversity
The demand factors are based on the principle of diversity: the larger the group of dwelling units, the less likely it is that all of them will be drawing their maximum load simultaneously. Splitting the calculation into two smaller groups (15 units each) ignores the diversity that exists across the entire building.
NEC Intent
The NEC's intent is to reduce the overall size of the service or feeder based on the total number of units. Calculating each meter center separately would defeat this purpose and lead to an unnecessarily oversized service.
Practical Considerations
Load Calculation (Detailed)
You'll need to perform a load calculation for each individual dwelling unit using the standard methods (220.12, 220.14, 220.16, 220.18, 220.53, 220.54, 220.55, etc.). This gives you the base load for each unit.
Sum the Unit Loads
Add up the calculated load for all 30 dwelling units.
Apply the Demand Factor
Multiply the total dwelling unit load (from the previous step) by the appropriate demand factor from Table 220.84 (33% in your case).
Add Common Area Loads
Remember to add in the calculated loads for any common areas (hallways, laundry rooms, elevators, exterior lighting, HVAC, etc.).
The Result
This total load is the calculated demand for your service and it should be divided between each meter center.
In summary:1. Calculate the load for each dwelling unit individually.2. Sum the individual dwelling unit loads.
3. Apply the demand factor from Table 220.84 based on the total number of dwelling units served by the service to that sum.4. Add in the load for common areas.
5. This is your service/feeder load.6. Divide between the Meter Centers.This will give you the most accurate and code-compliant calculation for your service. Good luck with your project! Flag for review