Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Bitcoin Miner Shelving bond or not to bond

User: sparkmatic, Location: California

Asked on: Friday, August 2, 2024 at 3:19 pm EDT
Answered on: Thursday, March 6, 2025 at 12:40 am EST

Question: Is it more of an issue to bond the metal shelving to the system. The equipment is cord and plug connected from the individual miner's to the PDU, the PDU s feed from 150A breaker. The miners are supplied with 240V all cords run from PDU's along shelving . I see a potential (small as it may be) for a rack or more to become energized. I would hope the equipment ground would clear a fault but wanted to get some input.Again do not want to create a hazard by bonding if it will not be effectiveThanks

You're right to be concerned about this and to consider the potential for energized shelving. Here's a breakdown of the situation and why bonding might be a good idea, even with cord-and-plug connected equipment

Understanding the Risks
Fault Potential

While the equipment grounding conductors within the power cords
should clear a fault, relying solely on them isn't ideal. A high-impedance fault (e.g., a loose connection or partial short) might not trip the breaker quickly, leaving the shelving energized for a dangerous amount of time.

Multiple Faults

Consider the possibility of multiple simultaneous faults. One miner could have a ground fault that isn't clearing quickly, and then someone touches another miner or the shelving with a different ground potential.

Cord and Plug Reliance

Cord-and-plug connected equipment depends on the integrity of the cord, plug, and receptacle. Damage to any of these could compromise the ground path.


Induced Voltage

Even without a direct fault, the metal shelving can potentially develop a voltage on it due to capacitive or inductive coupling from the energized conductors running nearby. This is typically low voltage, but under some conditions could present a shock hazard, or at least cause nuisance tripping.

PDU Grounding

Confirm how your PDUs are grounded. They should be grounded back to the main panel.

Why Bonding Is Generally a Good Idea
Equipotential Bonding

The primary goal of bonding is to create an equipotential plane. By connecting all the metal parts together, you reduce the voltage differences between them. This significantly lowers the risk of electric shock if someone touches two different metal surfaces simultaneously.

Faster Fault Clearing

Bonding provides a lower impedance path for fault current back to the source. This can help the breaker trip faster, reducing the duration of the fault and the risk of injury or damage.


Redundancy

Bonding adds a layer of redundancy to the grounding system. If the equipment grounding conductor in a power cord fails, the bonding connection can still provide a path for fault current.

Mitigation of Static and Induced Voltages

The interconnected ground paths also help to dissipate static electricity build-up and provide a low impedance to induced voltages.

Arguments Against Bonding (and Why They're Usually Overcome)
Ground Loops

The biggest concern people have is that improperly done bonding can create ground loops, which can introduce noise into sensitive equipment. This is less of a concern for miners. In this case, you are not dealing with sensitive audio or data equipment, and the benefits of added safety far outweigh the potential for interference.

Proper Implementation is Key

Bonding must be done correctly. If it's done poorly, it can be ineffective or even create new hazards.

How to Bond the Shelving (Important Considerations)
Solid Connection

Use appropriately sized bonding jumpers (typically copper wire) to connect the metal shelving to a known good grounding point. This could be a grounding busbar in the panel feeding the PDUs, or a dedicated grounding electrode conductor.

Clean Connections

Ensure the connections are clean and free of corrosion. Use antioxidant paste to improve conductivity.


Star Configuration (Recommended)

Ideally, run a separate bonding jumper from each section of shelving to a common grounding point. This helps to minimize ground loop potential.

Daisy-Chaining (Acceptable)

If a star configuration isn't practical, you can daisy-chain the bonding jumpers, but make sure the connections are very secure. Start with a large conductor to your ground location, then branch off smaller jumpers to the shelves.


Proper Wire Size

Consult the NEC (National Electrical Code) or your local electrical code for the appropriate size of bonding jumpers based on the size of the circuit feeding the PDUs (in your case, the 150A breaker).

Inspection

Have the bonding system inspected by a qualified electrician to ensure it meets code and is properly installed.


Avoid Long Loops

Keep bonding conductors as short as possible. Long loops can act as antennas and pick up noise.

Recommendations
1. Consult a Qualified Electrician

This is the most important step. They can assess your specific setup, identify any potential hazards, and recommend the best bonding solution for your situation. They can also ensure compliance with local electrical codes.2.

Bond the Shelving

I strongly recommend bonding the metal shelving, provided it's done correctly. The safety benefits generally outweigh the potential downsides.3.

Verify Equipment Grounding

Double-check that the equipment grounding conductors in your power cords are properly connected and in good condition.4.

PDU Grounding

Verify that your PDUs are properly grounded back to the main panel.5.

Regular Inspection

Establish a regular inspection schedule to check the condition of the cords, plugs, receptacles, and bonding connections.

In Summary


Bonding the metal shelving in your miner setup is generally a good practice to improve safety and reduce the risk of electric shock. However, it's crucial to have the work done by a qualified electrician who can ensure it's installed correctly and meets all applicable codes. Don't rely solely on the equipment grounding conductors in the power cords. Flag for review

Previous Question Next Question