Topic: Searching for a metal outlet box, 4 inches high, but 2 or less inches deep

User: itisdillon, Location: NJ/NY

Asked on: Friday, August 2, 2024 at 3:49 pm EDT
Answered on: Thursday, March 6, 2025 at 12:40 am EST

Question: The cabinet installers cut out 4x2 holes for outlets on the side of the kitchen island. (I am aware of the new NEC on island receptacles).I'd like to run MC to a metal box. I searched for an hour last night, and couldn't find anything. I have 2 inches before it hits the track for the drawer. Everything I am finding is 3 inches high, or more than 2 inches deep, or a handy box (which I won't be able to mount).Am I missing something?TIA

You're right, finding a shallow 4x2 metal box that will work for your specific situation with the drawer clearance can be tricky. Here's a breakdown of what you might be missing and some possible solutions

Things You Might Be Missing/Considering:
"4x2" Terminology

Sometimes people refer to a standard single-gang box as a "4x2" because of its approximate dimensions. But you are looking for 4 inches wide and 2 inches high.


"Box Fill"

Make sure the box you choose has adequate "box fill" capacity according to NEC. This is the maximum number of conductors, devices, and internal clamps allowed inside the box. A shallow box will have a lower capacity.

MC Connector Depth

Factor in the depth of the MC connector itself! It will add to the overall depth needed. Some MC connectors are more compact than others. Straight connectors usually take up more room than right-angle connectors.


Orientation

Can you rotate the box 90 degrees? This might help with clearance, especially if the drawer track is in a fixed location and a horizontal orientation would avoid it. However, you'd then need a cover plate that matches the rotated orientation.

Specialty Boxes

Look at specialty boxes designed for shallow applications. They often come at a premium price, but may be the only solution.


Existing MC Cable

If you have existing MC cable, this makes the solution trickier - because you will have to make the bend within a small box. If you have flexibility to add MC cable at a new, more accessible point, this might be something to consider.

Possible Solutions


Pancake Box

Pancake boxes are very shallow. A pancake box can work with the MC to the back, but you'll need a surface-mounted receptacle. And of course, this might not look great on the side of an island.2.

Plastic Boxes and Low-Profile Mounting

Consider a very shallow plastic box. Plastic boxes don't require grounding. A plastic box is also thinner than a metal box. Mount the box as close to flush as possible by recessing it into the cutout. You might need to chisel out a very small amount of material for the box's ears/brackets to sit slightly below the surface of the cabinet side.3.

Offset the Box

If the drawer track isn't directly behind the entire 4x2 cutout, you might be able to offset the box slightly (up/down/left/right) within the 4x2 hole to gain some clearance. This will require careful measurement and potentially some modification of the cutout.4.

Modify the Drawer Track (Carefully!)
This is extremely risky and I generally advise against it, but if the drawer track has enough excess material and it's structurally sound to remove a tiny portion, you might gain enough clearance. Be extremely cautious not to weaken the track or compromise the drawer's operation.5. Relocate the Outlet

Could the outlet be moved slightly to a location where there's more clearance? Even a small shift might make a difference. This might involve patching the existing hole and creating a new one.6.

Use a Flexible Conduit to a Deeper Box Elsewhere

If you can't find a suitable shallow box directly behind the cutout, consider running MC to a more accessible location within the island (e.g., inside the cabinet base) and then using a short length of flexible metal conduit (FMC) or Liquidtight Flexible Metal Conduit (LFMC) to a standard box mounted in the cutout. This allows you to use a deeper, more readily available box and provides some flexibility in positioning.7.

Surface Mount Extension Box

If you are comfortable with the aesthetic and don't mind the box protruding from the side of the cabinet, you can use a metal or plastic surface-mounted extension box, which screws directly to the surface of the island, over the hole. You will need to drill a hole to run the MC cable into the extension box.

Important Considerations



Local Codes

Always adhere to local electrical codes.


Safety

If you're not comfortable working with electrical wiring, hire a qualified electrician.

Inspection

If required by local codes, have your work inspected by an electrical inspector.


Documentation:
Take photos of your work before closing everything up for your records and future reference.Good luck! This is a common issue, so don't get discouraged. Careful planning and a little ingenuity will usually find a solution. Flag for review