Asked on: Friday, August 2, 2024 at 4:00 pm EDT
Answered on: Thursday, March 6, 2025 at 12:40 am EST
Question: I have commericial laundromat with washers and dryers.For the washers and dryers disconnect would NEC 2017 Article 422.31 apply? If not then which article NEC 2017 applies?
Yes, NEC 2017 Article 422.31 could apply, but it depends on the specific characteristics of the washers and dryers and their installations. Let's break it down
Article 422.31 (Appliances Rated Over 300 Volt Amperes)
General Requirement
This article generally applies to appliances rated over 300 volt-amperes or 1/8 horsepower. This is almost certainly true for your washers and dryers.
Means of Disconnection
It requires a means of disconnecting the appliance from all ungrounded conductors. This disconnection means must be one of the following:
(A) Separable Connector or an Attachment Plug and Receptacle
If the appliance is cord-and-plug connected. This is common for smaller, residential-style washers and dryers, but less common in commercial laundromats. If the appliance is cord and plug connection then the receptacle can serve as the disconnect, and must be accessible.
(B) Readily Accessible Switch
A switch readily accessible to the user or to a service person. This could be a dedicated switch near the appliance. A circuit breaker at the panel CAN be used, but it MUST be readily accessible to the user and marked as the disconnecting means.
(C) Circuit Breaker or Switch as a Disconnecting Means
The branch-circuit overcurrent device (breaker or fuse) can serve as the disconnect
IF it is readily accessible to the user of the appliance. This is the most common method in most commercial laundromats.
Key Considerations and Why 422.31 might not be the only relevant article
Overcurrent Protection
Article 422.11 addresses overcurrent protection. You must ensure the branch circuit feeding each washer and dryer is properly sized and protected according to the nameplate ratings of the appliances and the requirements of Article 422.
2.
Wiring Methods
The wiring method used to supply the washers and dryers must comply with Chapter 3 of the NEC. This includes things like conduit type, wire size, and grounding.3.
Grounding
Article 250 covers grounding and bonding requirements. This is critical for safety. Ensure proper equipment grounding is in place.4.
Location, Location, Location
Articles such as 300.6 and 300.7 for damp and wet locations can be relevant for laundry areas. Check the enviromental conditions of your laundromat and see if this article is relevant to you.
5.
Motor Requirements
If the washers/dryers have motors, Article 430 (Motors, Motor Circuits, and Controllers) might also be partially relevant, especially sections dealing with motor overloads.6.
Voltage
NEC 2017 210.6(C)(2) (Voltage Between Conductors—Dwelling Units) may come into play.
7.
Cord and Plug Connected
If the appliance is cord and plug connected then 422.16 (Flexible Cords) and 400.8 (Uses Not Permitted)
How to Determine What Applies
Read the Nameplates
The nameplate on each washer and dryer will give you critical information like voltage, amperage, wattage, horsepower (if applicable), and any special instructions.2.
Understand the Installation Method
Are the machines hardwired or cord-and-plug connected? This significantly affects the disconnection requirements.3.
Assess Accessibility
Is the breaker panel easily accessible to both customers and service personnel?4.
Consult a Qualified Electrician
This is always the best advice. A licensed electrician can assess the specific installation, local codes, and ensure compliance with all applicable NEC requirements.
In summary
Article 422.31 likely applies to your washers and dryers regarding disconnection means. You MUST also consider other articles, especially 422.11 (Overcurrent Protection), Article 250 (Grounding), and wiring methods in Chapter 3. The specific application depends on the details of the equipment and the installation.
Crucially, relying on this information alone is not a substitute for a professional electrical inspection and design. Engage a qualified electrician to ensure your laundromat's electrical system is safe and code-compliant. Flag for review