User: Legacy, Location: Maryland
Asked on: Saturday, August 3, 2024 at 11:16 am EDT
Answered on: Thursday, March 6, 2025 at 12:41 am EST
Question: Need to replace a GFI 15 amp breaker in an old Cutler Hammer panel, CH614D. The old breaker is a A-542, type CH.Looking for a recommended part number for a replacement breaker.Thanks much
You are on the right track. To replace your existing 15A Cutler Hammer CH type GFCI breaker (A-542), you need a new Cutler Hammer / Eaton CH115GFC.Here's why and what to confirm: Type CH
The Cutler Hammer CH series is a specific type of breaker and panel system. You absolutely need to match this.
15A
This specifies the amperage rating of the breaker. Do not deviate from this without understanding the wiring.
GFCI
You need a Ground Fault Circuit Interrupter (GFCI) breaker to provide ground fault protection.
CH115GFC : This is the Eaton/Cutler-Hammer part number for a single-pole, 15 amp, CH-series GFCI breaker. It's the modern replacement for your older A-542.
Important Safety Notes
Turn off the Main Breaker
Before working on any electrical panel,
absolutely shut off the main breaker that feeds the entire panel. This will de-energize the panel and greatly reduce the risk of shock. Verify Power is Off
Use a non-contact voltage tester to confirm that the breaker slot you will be working on is actually de-energized after you've shut off the main breaker.
Work Carefully
Handle breakers with care. Do not force anything.
Wiring
The GFCI breaker will have a neutral pigtail (white wire). This must be connected to the neutral bar in your panel. The load neutral (the neutral wire from the circuit you're protecting) connects to the breaker terminal marked for load neutral. If the GFCI is wired incorrectly, it will not function.
Test After Installation
After installing the new breaker, and before closing up the panel, use the "Test" button on the breaker. This will trip the breaker. Reset the breaker. Use a GFCI tester in an outlet on the circuit to ensure proper GFCI functionality.
If in Doubt, Hire an Electrician
If you are not comfortable or experienced working with electrical panels,
hire a qualified and licensed electrician. Electrical work can be dangerous, and improper installation can create a fire hazard. Local Codes
Ensure your installation complies with all local electrical codes.
Where to Buy
You can find CH115GFC breakers at:
Home Depot Lowe's Electrical Supply Houses (like Rexel, Graybar, etc.)* Online Retailers (Amazon, etc.)Make sure you are buying from a reputable source to ensure you get a genuine Eaton/Cutler-Hammer product. Counterfeit breakers are a serious safety hazard. Flag for review