Question: I need to pull a new wire through conduit that already has 3 wires. Ive pulled even heavier gauge before, which wasn't too fun, but this is my first pulling with OTHER wires already in.All wire is stranded. I need to pull (1) #10 THHN thru underground 3/4" conduit that already has (3) #10 THHN for about 60 feet with two 90 deg bends.What approach should I take?Should I dig up the two 90 deg bends that are underground or will it take the corners ok? Is lube unnecessary? Should I pull the new wire (and a string) using an already installed wire and then pull old wire back in with string? Will fish tape have problem passing the 3 already installed wires?What would you pros do?
Okay, pulling a wire through existing conduit is always a bit trickier, but definitely doable. Here's a breakdown of my recommended approach based on your specific scenario, aiming for the most efficient and least damaging method
Key Considerations Before Starting:
Conduit Fill
Before you even start,
confirm that adding a #10 THHN wire won't exceed the maximum conduit fill percentage for 3/4" conduit. Overfilling can damage the wires during pulling, make future work difficult, and may violate electrical codes. A quick conduit fill calculation is a good idea. A quick Google search for "conduit fill calculator" can help. Condition of Existing Wires
Gently test the existing wires to make sure they're not brittle or damaged. If they're old, cracked, or show signs of wear, consider replacing them all while you're at it. It's easier to replace all 4 at once than to come back later and do it again.
Safety First
Turn off the power to the circuit at the breaker before doing ANY work. Double-check with a non-contact voltage tester to be absolutely sure.
My Recommended Approach
Lube is Your Friend - Absolutely Use It
Don't even think about doing this without wire pulling lubricant. It drastically reduces friction and makes the job much easier. Use a high-quality wire pulling lubricant specifically designed for electrical work. Apply it liberally to the wire as you feed it into the conduit.2.
Fish Tape is Your Primary Tool
Start at the End With More Room
If one end of the conduit is more accessible or has a larger pull box/enclosure, start there. It gives you more room to work and maneuver the fish tape.
Lubricate the Fish Tape
Apply a thin layer of wire pulling lubricant to the fish tape itself. This helps it slide past the existing wires.
Patience and Gentle Force
Carefully feed the fish tape into the conduit. Work it slowly, using a twisting motion to help it navigate past the existing wires. If you encounter significant resistance, don't force it! Pull it back a bit and try again, perhaps changing the angle slightly.
If you get stuck
Try pulling the fishtape out a little bit and rotating the fishtape as you advance it. This can sometimes make the fishtape nose find a new path.
If you get really stuck
Try sending a second fishtape in to try to get past the wires that are blocking you and use the second fishtape to push the other fishtape through.3.
Attaching the Wire
Hook the Wire Securely
Once the fish tape is through to the other end, create a secure hook or loop in the end of the fish tape.
Stagger the Wire End
Strip a longer portion of the insulation from the #10 THHN wire. Fold the bare wire back on itself to create a streamlined, tapered end. This helps it glide through the conduit more easily.
Tape Securely
Wrap the connection between the wire and the fish tape very securely with electrical tape. Use multiple layers of tape, overlapping each layer. A smooth, streamlined tape job is essential. Avoid a big bulky ball of tape.
Attach a Pulling String
This is often overlooked, but it's a great idea. Attach a strong nylon pulling string to the wire behind the taped connection. This gives you a backup if the tape fails. It also allows you to easily pull another wire or fish tape back through later if needed.4.
Pulling the Wire
Steady, Consistent Pull
At the pulling end, have someone feed the wire into the conduit while you pull the fish tape. Communicate clearly! Pull with a slow, steady, and consistent force. Avoid jerking or yanking.
Watch for Resistance
If you encounter significant resistance, stop pulling immediately. Try wiggling the wire back and forth slightly to see if it will free up. If not, you may need to pull the wire back out and re-lube it or re-evaluate your approach.
Two People Help
Having someone feed the wire into the conduit while you pull on the fish tape is ideal. The person feeding can also apply more lubricant as needed.5.
Addressing the Bends
Try Pulling First
With the liberal use of lubricant and a steady pull, it's entirely possible to make it through two 90-degree bends without digging.
If it Fails, Then Dig
If you are really struggling, only then consider exposing one or both of the 90-degree bends. Exposing the bend allows you to:
Inspect the Conduit
Check for any damage or kinks in the conduit that might be causing the obstruction.
Apply Lube Directly
You can apply lubricant directly at the bend, which can significantly reduce friction.
Shorten the Pull
You could cut the conduit at the bend (use a proper conduit cutter), pull the wire through in two sections, and then use a coupling to rejoin the conduit. This is a last resort, but it can save a lot of frustration.
Why I DON'T Recommend These Approaches
Using an Existing Wire to Pull
This is risky. The existing wire may not be strong enough to withstand the pulling force. Also, you risk damaging the insulation of the existing wire, creating a potential short circuit or ground fault. If that happened, you'd have to replace all the wires anyway, and you'd have made the situation much worse.
Skipping Lube
Just don't do it. It's tempting to save a few bucks, but you'll regret it. The friction will make the pull much harder, and you risk damaging the wires and the conduit.
Important Notes
Check Your Work
After the pull, visually inspect the new wire and the existing wires at both ends of the conduit for any signs of damage.
Test the Circuit: Once everything is connected, test the circuit to ensure it's working properly and that there are no shorts or ground faults.By following these steps, you should be able to pull the new wire through the existing conduit safely and efficiently. Good luck! Flag for review