Topic: Electric Heat - Name plate doesn't make sense

User: olly, Location: Berthoud, Colorado

Asked on: Sunday, August 4, 2024 at 3:18 pm EDT
Answered on: Thursday, March 6, 2025 at 12:42 am EST

Question: Hi Guys,I am wiring an electric furnace. I have never wired one before. It takes 2 - 2 pole breakers. for the L1/L2 I assume minimum amps is 35.6/39.4 for the 60A breaker and a max of 52.1/56.9. It doesn't say min and max, just min ampacity, which I find confusing.How do these work, does the circuit board change the amperage based on demand? I am assuming the thermostat will determine how many amps to send to the resistive electrical element, like a high medium or low. Low being 35.6/39.4 and high being 52.1/56.9. Is that correct? Also, L3/L4 is that a second stage? So it only comes on when it needs it?

Okay, let's break down how an electric furnace works and address your questions. Wiring an electric furnace can be dangerous if not done correctly. I strongly recommend consulting with a qualified electrician if you are not completely comfortable and knowledgeable about electrical work.Understanding Electric Furnace Amperage and Operation

Here's the gist of how an electric furnace typically works: Resistive Heating Elements

Electric furnaces use resistive heating elements, similar to a toaster or electric stovetop. When electricity flows through these elements, they heat up and a blower fan circulates the heated air throughout your home.


Stages (Elements)

Most electric furnaces use multiple heating elements to provide different levels of heat output. This is what allows for "stages" of heating. When the thermostat calls for heat, one or more elements are activated.

Thermostat Control

The thermostat controls the furnace by turning the heating elements on and off. It does

not
vary the amperage going to a particular element. Each element is either fully on or fully off. Multiple Breakers/Circuits

Using two separate 2-pole breakers is common. One breaker powers certain heating elements and the blower motor, and the second breaker powers other heating elements.

Addressing Your Questions


"Minimum Ampacity"

What you are seeing is the minimum wire ampacity required for the circuit. This is based on the NEC (National Electrical Code) requirements. You must use wire that is rated for at least that ampacity to ensure safe operation.

Why "Minimum" and not "Maximum"

The minimum ampacity is the
lowest safe current-carrying capacity the wire must have. You can always use wire with a higher ampacity rating than required, but you cannot use wire with a lower rating. It's about safety.

60A Breaker

If the manufacturer specifies a 60A breaker, you must use one of the proper voltage and amperage rating. 60A breakers are designed to protect the circuit from overloading. The "minimum ampacity" of the wiring will depend on the total load of the furnace. You need to follow the installation guide, and local code.

Oversizing the Breaker

Never oversize the breaker beyond what the furnace manufacturer specifies. This defeats the breaker's purpose of protecting the wiring and could lead to a fire.2.

"How does it work? Does the circuit board change the amperage based on demand?"
No, the circuit board does not change the amperage of each element. The circuit board acts as a control center, turning elements on or off based on the thermostat's demand. Think of it as a switchboard.3. "I am assuming the thermostat will determine how many amps to send to the resistive electrical element, like a high medium or low. Low being 35.6/39.4 and high being 52.1/56.
9. Is that correct?"
No, that's not quite correct. The thermostat signals the furnace to turn on one or more heating elements. Each element draws a specific amount of current (amperage) when it's on. Example

Let's say you have two heating elements. Element 1 draws 35.6 amps. Element 2 draws 16.5 amps. When the thermostat calls for "low" heat, only Element 1 might be activated (35.6 amps). When the thermostat calls for "high" heat, both Element 1 and Element 2 might be activated (35.6 + 16.5 = 52.1 amps).
4.


"Also, L3/L4 is that a second stage? So it only comes on when it needs it?"
Yes, L3/L4 likely represents a second stage of heating. When the thermostat detects a significant temperature drop, or if the first stage cannot maintain the desired temperature, it will activate the second stage (L3/L4).

Important Considerations



Manufacturer's Instructions

Always follow the electric furnace manufacturer's installation instructions precisely. They will provide the specific wiring diagrams, breaker sizes, and other critical information for your particular model.

Wire Size

Use the correct wire gauge (thickness) for the amperage and length of the circuit. This is crucial for safety and preventing overheating. The manufacturer's instructions and local electrical codes will specify the required wire size.


Grounding

Ensure proper grounding of the furnace. This is essential for safety and preventing electrical shock.

Local Electrical Codes

Adhere to all local electrical codes and regulations. These codes are in place to ensure safety and proper installation.


Disconnect Switch

Install a disconnect switch near the furnace for easy power shutoff during maintenance or emergencies.*

Multimeter Readings

Once wired, use a multimeter to measure the voltage at the furnace terminals and the amperage draw of each element to ensure proper operation.

In summary

1. The circuit board does not vary the amperage. It acts as a switch, turning heating elements on and off.
2. The thermostat determines which elements (stages) are activated.3. L3/L4 likely represents a second stage of heating that comes on when more heat is needed.
4. Always follow the manufacturer's instructions, use the correct wire size and breaker sizes, and ensure proper grounding.5. Local code will override anything anyone tells you on the internet.


Disclaimer:
This information is for general guidance only and should not be considered a substitute for professional advice. Working with electricity can be dangerous. If you are not comfortable or knowledgeable about electrical work, please consult with a qualified electrician. Flag for review