Question: Here's what I came up with to eliminate any ambiguity as to the question "for the service to a duplex, can I calculate the load just by adding together the optional load calcs for each dwelling unit?"Do you think the single phrase added is sufficiently clear? I could try something even more direct, like adding a whole sentence stating "A feeder or service supplying multiple such dwelling units shall be permitted to have its load calculated as the sum of the individual loads of those dwelling units."Or I could further change the first sentence to say "This section applies to any number of dwelling units, each having theits total connected load served by a single 120/240-volt or 208Y/120-volt set of 3-wire service or feeder conductors with an ampacity of 100 or greater"Cheers, Wayne120.82(A) Feeder and Service Load.This section applies to a dwelling unit having the total connected load served by a single 120/240-volt or 208Y/120-volt set of 3-wire service or feeder conductors with an ampacity of 100 or greater. It shall be permissible to calculate the feeder and service loads in accordance with this section instead of the method specified in Article 120, Part III. The calculated load shall be the result of adding the loads from 120.82(B), 120.82(C), and 120.82(D) for each dwelling unit individually. Feeder and service-entrance conductors whose calculated load is determined by this optional calculation shall be permitted to have the neutral load determined by 120.61.Statement of Problem and Substantiation for Public CommentConsider a duplex with a single service that supplies two sets of service entrance conductors to two service disconnects, one for each dwelling unit. The service entrance conductors supplying just one dwelling unit can have their load computed using 120.82.There is, however, some uncertainty as to whether the service conductors supplying both dwelling units may have their load calculated as the sum of those two 120.82 calculations. The current wording of 120.82 leads some AHJs to the interpretation that 120.82 only applies to conductors carrying the load of exactly one dwelling unit, and that the results of that computation can not be used for determining the load on any upstream conductors that supply more than one dwelling unit. This point of view is supported by the observation that 120.84 is available for conductors supplying 3 or more dwelling units, and that 120.85 is available for conductors supplying exactly 2 dwelling units.However, it makes no sense to limit the calculation results from 120.82 to conductors that supply exactly one dwelling unit. Where a set of conductors supplies multiple other sets of conductors, it is is physically impossible for the load on those conductors to exceed the sum of the loads on the multiple other conductors supplied. Summing those individual loads is always a conservative overestimate of the load on the common supply conductors.Therefore this change clarifies that conductors that supply multiple dwelling units may have their load determined by calculating the 120.82 load of each dwelling unit separately, and then adding those results.
Okay, let's break down your proposed changes and how to best achieve clarity.
Analysis of the Current Issue
Your core problem statement is valid. The existing language of 120.82 (using your numbering) can be interpreted as only applying to the final set of conductors feeding a single dwelling unit. This leads to unnecessary complications when calculating the service load for a duplex (or potentially a triplex if you're using 120.84 for 3+ units).
Assessment of Your Proposed Solutions Adding "for each dwelling unit individually": This is a step in the right direction, but it's subtle. Some readers could still argue that 120.82 only applies if the entire service feeds only one unit before any splits. Adding "A feeder or service supplying multiple such dwelling units shall be permitted to have its load calculated as the sum of the individual loads of those dwelling units.": This is much better and addresses the problem head-on. It is direct and unambiguous. Changing the first sentence to "This section applies to any number of dwelling units, each having theits total connected load served by a single 120/240-volt or 208Y/120-volt set of 3-wire service or feeder conductors with an ampacity of 100 or greater": While this broadens the initial scope, it doesn't explicitly state that you can sum the individual calculations. It relies on the reader to infer that. While not bad, it is not a complete solution.
Recommended Approach
The best approach is to combine the addition of the sentence directly addressing the summation of individual loads with some adjustments to the first sentence for clarity.
Here's my suggested revised text
"120.82(A) Feeder and Service Load.This section applies to a dwelling unit whose total connected load is served by a single 120/240-volt or 208Y/120-volt set of 3-wire service or feeder conductors with an ampacity of 100 or greater. It shall be permissible to calculate the feeder and service loads for each dwelling unit in accordance with this section instead of the method specified in Article 120, Part III. The calculated load for each dwelling unit shall be the result of adding the loads from 120.82(B), 120.82(C), and 120.82(D). A feeder or service supplying multiple such dwelling units shall be permitted to have its load calculated as the sum of the individual loads of those dwelling units, calculated per this section. Feeder and service-entrance conductors whose calculated load is determined by this optional calculation shall be permitted to have the neutral load determined by 120.61."
Key improvements in this version
Clear Initial Scope
The first sentence makes it clear that the section applies to each individual dwelling unit meeting the voltage/ampacity criteria.
Explicit Summation
The added sentence directly and unambiguously states that you can sum the individual unit calculations for the overall service/feeder. The phrasing makes it clear that this summation is permitted (not required) which allows flexibility.
Reinforcement
By repeating the term "calculated per this section," it avoids any loophole where someone could try to use the summation while using a different calculation method for the individual units.
Why this is the strongest solution
Avoids ambiguity
No room for misinterpretation.
Directly addresses the problem
It states exactly what you want to be allowed.
Concise
Doesn't add unnecessary verbiage.
Additional Tip for Your Public Comment:
In your substantiation, consider adding a simple* example. For instance:"Example: A duplex has two dwelling units. Unit A has a calculated load of 80 amps per 120.82. Unit B has a calculated load of 90 amps per 120.
82. This change clarifies that the service conductors supplying both units can have a calculated load of 80 + 90 = 170 amps."This will make your case even more compelling to the code panel. Good luck! Flag for review