User: hhsting, Location: Glen bunie, md, us
Asked on: Monday, August 5, 2024 at 8:36 am EDT
Answered on: Thursday, March 6, 2025 at 12:43 am EST
Question: Engineer used NEC 2017 Article 220.54 demand factors in commericial laundromat sub panel demand load calculation. Sub panel is 208/120V three lhase.NEC 2017 Article 220.54 is for dwelling units. I don’t see anywhere else it can be used for commericial laundromat.Am I correct or incorrect NEC 2017 Article 220.54 doesn’t apply to commericial laundromat? If it doesn’t apply then which section in NEC 2017 Article 220 applies to commericial laundromat?
You are correct. NEC 2017 Article 220.54 specifically applies to dwelling units and electric clothes dryers. Using it for a commercial laundromat is incorrect.Here's why and what you should be using: Article 220.54 is explicitly for dwellings
The heading and text of 220.54 clearly state it is for the calculation of loads for electric clothes dryers in dwelling units. This includes single-family homes, apartments, and similar residential settings.
Commercial laundromats are not dwellings
Commercial laundromats are commercial establishments, not residential units.
Applicable sections for commercial laundromats
For a commercial laundromat, you should be using the general load calculation rules for non-dwelling occupancies within
NEC 2017 Article 220, Part III, General. Here are the specific areas to address: 220.10 General
States that branch-circuit, feeder, and service loads shall be calculated as provided in Part III.
220.12 Lighting Load for Non dwelling occupancies
Determines the required load for general lighting, based on the occupancy type and square footage, table 220.12 for general lighting loads by occupancy.
220.14 Other Loads – All Occupancies
Outlets not used for general illumination must be calculated based on the type of load as specified by 220.14.
220.14(D) Electric Clothes Dryers – Non dwelling
Calculate based on the nameplate rating.
220.14(H) Motors
Motor loads will be calculated based on NEC 430 and its applicable parts.
How to calculate the load for a commercial laundromat
Determine the load of each dryer
You need the nameplate rating (in kVA or kW) of each dryer. If it's in amps, convert to kVA using the voltage (208V or 120V).2.
Calculate General Lighting and receptacles Calculate this in accordance with 220.12 and 220.
143. Calculate Motors
Based on nameplate rating, horsepower, etc. Refer to Article 430.4.
Sum individual loads
Add up the loads of all the dryers.5.
Apply Demand Factors (if applicable)
This is where judgment and experience come into play. There are NO specific demand factors in Article 220 that apply directly to commercial laundromat dryers. You need to determine if a demand factor is appropriate based on the actual likely usage. The engineer likely inappropriately used 220.54 instead of appropriately using 220.61 for a commercial application.
6.
Consider Diversity
Think about how likely it is that all dryers will be running at full load simultaneously. If the laundromat is typically only 50% full, a diversity factor (similar in principle to a demand factor) might be justifiable, but this requires careful justification and documentation. This is where engineering judgement is important and should be documented.
Important Considerations
Document your assumptions
Any demand or diversity factors applied must be thoroughly documented and justified. You should have a strong rationale for why you believe a certain percentage of the total connected load will be the maximum likely load.
Local Amendments
Always check with your local AHJ (Authority Having Jurisdiction) for any local amendments to the NEC. They might have specific requirements or interpretations for commercial laundromats.*
Engineering Judgement: Electrical engineering involves more than just plugging numbers into formulas. Consider the specific characteristics of the laundromat (size, clientele, operating hours, etc.) when making load calculations.In summary, using NEC 2017 Article 220.54 for a commercial laundromat is incorrect. You must use the general commercial load calculation rules in Article 220, Part III, and carefully consider appropriate demand or diversity factors based on actual usage patterns. Flag for review