Topic: HVAC wire size ?

User: Robpaeschke, Location: Washington

Asked on: Monday, August 5, 2024 at 9:32 am EDT
Answered on: Thursday, March 6, 2025 at 12:43 am EST

Question: What wire size do I need for aElectric heat13.8 kwFull load amps60Minimum circuit ampacityCircuit 127.0Circuit 253Max overcurrentProtective DeviceCircuit 130Circuit 260Thanks

Okay, let's break down the wire sizing for your electric heater circuits based on the information you provided.

Understanding the Information Electric Heat: 13.8 kW

This is the total power consumption of the heater.


Full Load Amps: 60A

This is the total current draw of the heater when operating at full capacity.

Minimum Circuit Ampacity

This is the
minimum current-carrying capacity the wire must have, accounting for continuous use and safety factors.

Maximum Overcurrent Protective Device (OCPD)

This is the maximum size breaker or fuse allowed to protect the circuit.

Circuit 1
Minimum Circuit Ampacity: 27.0A Max Overcurrent Protective Device: 30A

Based on a minimum ampacity of 27.0 amps, and using the NEC (National Electrical Code) table 310.16: Copper Wire

You would need a

#10 AWG copper wire
. #10 AWG copper wire is typically rated for 30 amps at 60°C insulation (which is a common rating).
Aluminum Wire

A #8 AWG aluminum wire rated at 40 amps would suffice.

Circuit 2
Minimum Circuit Ampacity: 53A Max Overcurrent Protective Device: 60A

Based on a minimum ampacity of 53 amps, and using the NEC (National Electrical Code) table 310.16: Copper Wire

You would need a

#6 AWG copper wire
. #6 AWG copper wire is typically rated for 55 amps at 60°C insulation (which is a common rating). If you can use 75°C rated wire, #6 AWG can handle 65 amps.
Aluminum Wire

You would need a

#4 AWG aluminum wire
. #4 AWG aluminum wire is typically rated for 60 amps.

Important Considerations and Disclaimer NEC Code is Paramount

Always follow the National Electrical Code (NEC) and any applicable local codes. The NEC is the definitive guide for safe electrical installations. Local codes may be stricter than the NEC.

Wire Insulation Temperature Rating

The ampacity of a wire depends on its insulation temperature rating (e.g., 60°C, 75°C, 90°C). Make sure the wire you select is rated for the conditions of your installation (ambient temperature, etc.). Higher temperature ratings allow for higher ampacities.

Voltage Drop

For long wire runs, you need to calculate voltage drop. Excessive voltage drop can cause the heater to operate inefficiently or damage it. Using a larger wire size than the minimum required can reduce voltage drop.


Conduit Fill

If running wires in conduit, ensure you comply with conduit fill requirements. Too many wires in a conduit can cause overheating.

Terminals

Ensure the terminals on the heater and the breaker are rated for the wire size and conductor material (copper or aluminum) you are using.


Professional Installation is Recommended

Electrical work can be dangerous. I highly recommend that you hire a qualified, licensed electrician to perform the installation. They will ensure the installation is safe, code-compliant, and properly sized.

In summary, based on the information you provided and common NEC guidelines, you will likely need



Circuit 1: #10 AWG Copper or #8 AWG Aluminum
Circuit 2: #6 AWG Copper or #4 AWG AluminumDisclaimer: I am an AI chatbot and cannot provide professional electrical advice. This information is for general guidance only. You MUST consult with a qualified electrician for your specific situation. Electrical work is dangerous and should only be performed by qualified individuals. Failure to do so could result in serious injury, death, or property damage. Flag for review