Topic: Potential failures from poor conductor sizing practices?

User: dec_primary, Location: New York

Asked on: Monday, August 5, 2024 at 6:22 pm EDT
Answered on: Thursday, March 6, 2025 at 12:45 am EST

Question: Hello,I am an EE doing design work for an EV charging project. We have a 400A panel and the EC would like to use 750 MCM ALU (THWN) conductors for the feeder.I'm aware this is compliant with 215.2(A)(1) since the conductors are rated for our load, but I worry because I've seen enough projects where property owners are squeezing as much as they can out of their panels to accommodate growing EV drivers (in select areas of course). My concern is that we are using a 400A MCB and a future EC will be tempted to keep adding chargers beyond the 385A that we are rating the conductors for. If EV adoption really does pick up like some anticipate, and these level 2 chargers are being used daily, how likely and when is it likely that there will be damage if the panel is overloaded but not to the point that the breaker will trip?Am I being paranoid? I want to be understanding that increasing the rating to 400A across the length of the run can really run up material costs and I want to design practically, but safety trumps costs so I appreciate the insight.Thanks!

You're right to be concerned and to think critically about the potential future scenarios. While code compliance is essential, future-proofing and minimizing the risk of future overloading are also important aspects of good design. Here's a breakdown of your concerns and some factors to consider

Understanding the Situation
Code Compliance

Yes, 750 MCM ALU THWN conductors rated at 385A are code-compliant for a 400A panel
fed by a 400A breaker, assuming your load calculations justify the 385A.

Derating and Load Diversity

EV charging loads are known to be continuous loads and generally don't have load diversity, hence NEC articles 625.41 and 625.
42.


Continuous Load Considerations

Your conductors are rated for 385 A so that leaves 15 amps that is allowed to be on the panel continuously before the 80% rule starts to affect your conductor's rating.


Future-Proofing

The crucial point is your concern about future overloading due to the addition of more EV chargers or other loads. You are wise to anticipate this.

Breaker Coordination

A properly sized breaker
should trip before the conductors overheat to the point of failure. However, breakers are not perfect, and there are failure modes (delayed tripping, nuisance tripping leading to breaker replacement with incorrectly sized breakers, etc.) that can lead to issues.

Likelihood and Timing of Damage


Here's what could happen and when:
Immediate Damage

Unlikely unless the panel is severely overloaded immediately after your installation.

Gradual Degradation (Most Likely)

This is the biggest concern. Even if the breaker
eventually trips, repeated near-overload conditions can gradually degrade the conductor insulation. This degradation happens over time, especially with heat cycling. The insulation becomes brittle, cracks, and loses its dielectric strength.

Long-Term Consequences



Increased Risk of Faults

Degraded insulation increases the chance of short circuits, ground faults, and arcing faults.


Fire Hazard

Overheated conductors and degraded insulation are fire hazards.

Equipment Damage

Prolonged undervoltage conditions (due to voltage drop from overloaded conductors) can damage EV chargers and other equipment connected to the panel.


Nuisance Tripping

The breaker might start tripping more frequently, leading to frustration and potential tampering (like replacing it with a higher-rated breaker).

Factors Influencing the Risk
EV Charger Usage Patterns

How frequently are the chargers used? Are they mostly used simultaneously during peak hours? If so, the risk is higher.


Ambient Temperature

Higher ambient temperatures exacerbate the heating of the conductors.

Conduit Fill

Too many conductors in a conduit can reduce heat dissipation, leading to higher conductor temperatures.


Installation Quality

Poor connections (loose terminations) create hotspots that accelerate conductor degradation.

Load Management Systems

Are there load management systems in place to limit the total current draw of the EV chargers? If so, the risk is lower.


Future Load Growth

How likely is it that additional loads (beyond EV chargers) will be added to the panel?

Recommendations


Here's a practical approach to address your concerns:1. Re-evaluate Load Calculations

Be conservative in your EV charger load calculations. Assume the maximum current draw for each charger unless there's a load management system in place that guarantees lower consumption. Consider adding a buffer for potential future loads, even if they aren't planned right now.2.

Consider a Larger Conductor

If you can reasonably budget it, increasing the conductor size to a size that is rated for the 400A breaker is a safety measure, especially if you foresee future EV chargers being installed. Use a conductor size that is rated for 400A.3.

Improve Overcurrent Protection



Consider an adjustable trip breaker

These breakers allow you to set the tripping threshold, giving you more control over when the breaker trips. This is an expensive option, though.


Ensure proper breaker coordination

Make sure the breaker is properly sized to protect the conductors and the equipment connected to the panel.4.

Load Management System (Recommended)

This is often the best long-term solution. A load management system can dynamically limit the current draw of the EV chargers to stay within the panel's capacity and prevent overloading. There are various types of load management systems, from simple current sensors that throttle back chargers to more sophisticated systems that optimize charging based on grid conditions and user preferences.5.

Communication and Documentation

Clearly label the panel, the EV charger circuits, and the conductor ampacity. Provide documentation to the property owner about the panel's capacity, the EV charger loads, and the importance of not overloading the panel.* Advise the property owner to consult with a qualified electrician before adding any new loads to the panel.6.

Consider a Subpanel

Depending on the number of chargers, you might consider a subpanel dedicated to the EV chargers. This isolates the EV charger loads from the existing panel and makes it easier to manage capacity.7.

Infrared Scan

It is possible to perform an infrared scan on your conductor if the installation has been performed for an extended period to check for heat spots. If you perform the test immediately after, the effects of an overloaded circuit would not be readily apparent.

Is Your Concern Paranoid?


No, you're being proactive and responsible. It's better to over-engineer and have peace of mind than to cut corners and risk future problems. The cost of a larger conductor is a small price to pay compared to the potential costs of a fire, equipment damage, or liability.

Practicality vs. Safety

While cost is a factor, safety should always be the priority. Clearly explain the rationale for your recommendations to the property owner and the EC. Emphasize the long-term benefits of future-proofing and minimizing risk.By carefully considering the factors above and implementing appropriate measures, you can design a safe and reliable EV charging system that can accommodate future growth. Flag for review