Topic: Solaredge 66.6kW 3ph inverter wont work while 300hp pump with VFD

User: Devendra Rajwade, Location: CA

Asked on: Monday, August 5, 2024 at 6:29 pm EDT
Answered on: Thursday, March 6, 2025 at 12:45 am EST

Question: I would like to get some help with an issue with one of the solar systems.This is on a farm with 300HP pump-motor connected to a VFD. 3ph - 480/277V Power from the utility transformer terminates line side at 400AMp breaker in VFD cabinet going through the utility meter cabinet. Breaker has three termination lugs on each side. Wires from two load side lugs are connected to the VFD and the the 3rd load side lug is used to terminate the solar system. Solar side consists of two 66.6kW Solaredge 3Ph-480/277V inverters, whose combined output (160A) is connected to the breaker through a fused disconnectHere is the problem, Inverters run normally when pump is off. If inverters are producing power and then the pump is turned on they continue to run normally. If pump is running and then you start the inverters they will not produce power and go into starting loop. This scenario is usually in the morning when pump is running over night and inverters wake up in the morning as the sun rises.Solaredge support is aware of the issue but has not provided any resolution. Any guidance in identifying the cause is appreciated.

Okay, this is a tricky problem but we can break it down and analyze possible causes and solutions. The fact that SolarEdge is aware suggests this isn't a completely unheard-of issue, which is both good and bad. Good because it means there's likely some underlying reason they've seen before. Bad because they haven't fixed it (or told you the fix).Here's a structured approach to troubleshooting this

1. Understanding the Setup and Symptoms:
Parallel Operation

The key is that the solar inverters and the VFD/pump are operating in parallel on the same electrical bus
after the 400A breaker in the VFD cabinet.

Starting Loop

This suggests the inverters are detecting a condition that prevents them from synchronizing with the grid.

Order Matters

This is HUGE. The order in which things are energized (inverters vs. pump) makes a difference. This strongly suggests some kind of transient or voltage disturbance caused by the pump starting is the trigger.


Solaredge's Awareness

This is the most frustrating part. They should be providing you with specific diagnostic steps.

160A vs 400A

The combined solar output is a significant portion of the total breaker rating. This means voltage fluctuations can be pronounced.

2. Potential Causes

Here's a breakdown of possible causes, from most likely to less likely, with potential solutions:


A. Voltage Dip on Pump Start-up

This is the most likely culprit. Large motors, especially when started under load, draw a significant inrush current. This can cause a temporary voltage dip on the entire 480V bus. Solaredge inverters are sensitive to voltage fluctuations and may not start if the voltage is outside their acceptable range.

Why it explains the symptoms

If the inverters are already running, they are more resilient to temporary voltage dips. If the pump starts
before the inverters, the inverters see the dip and abort the start-up process.

Troubleshooting Steps



Voltage Monitoring

This is critical. You need to record the voltage at the 480V bus (at the breaker in the VFD cabinet) during the pump start-up. Use a data logger (power quality analyzer) that can capture transients and record voltage fluctuations over milliseconds. Look for the minimum voltage during pump start-up. Record the voltage before and after starting.

Inverter Voltage Range

Check the SolarEdge inverter specifications carefully for their acceptable input voltage range. Is the voltage dip causing the voltage to fall outside the acceptable range?

Inverter Fault Codes

Even though they go into a starting loop, do the inverters log
any fault codes related to voltage? Check the SolarEdge monitoring portal and/or physically access the inverters to check for fault codes.

Possible Solutions



Soft Starter (if applicable)

If the pump's VFD allows for soft starting or reduced voltage starting, try adjusting the settings to reduce the inrush current. This is the first thing to try.


Increase VFD Acceleration Ramp

A longer acceleration ramp on the VFD reduces inrush current demand.

Voltage Sag Correction

Some VFD's have voltage sag correction settings. Consider increasing that as well.


Add a Reactor/Inductor

An inductor placed in series with the solar inverter output (on the load side of the fused disconnect) can help buffer the inverters from voltage transients. Consult with an electrical engineer to size the inductor appropriately.

Dedicated Breaker/Connection (expensive)

Ideally, the solar inverters should be on their own breaker/dedicated wiring run back to the main distribution panel (MDP) or transformer, independent from the VFD. This isolates them from the voltage dip caused by the pump. This would involve significant electrical work.


Oversize Wiring to VFD

Reducing the wiring impedance to the VFD might reduce the voltage sag.

Adjust SolarEdge Inverter Settings

This is a long shot, but possible. Some inverters have settings related to voltage ride-through or low-voltage start-up. Check if the SolarEdge inverters have any such settings and experiment with adjusting them (with SolarEdge's guidance).

Increase Utility Transformer Size (very expensive)

If the utility transformer is undersized, the voltage dip will be more severe.

Staggered Inverter Start-up

If the inverters support a staggered start-up sequence, try configuring them to start with a slight delay between them. This might reduce the impact on the voltage.


Change Pump Starting Time

Consider adjusting the pump's starting time in the morning to a time when the solar inverters are producing more power. This would increase the grid strength and make the inverters more resilient to the voltage dip.

B. Harmonic Distortion

VFDs are notorious for generating harmonic distortion on the electrical system. The SolarEdge inverters
might be sensitive to these harmonics, especially during the pump start-up when the harmonic content can be higher.

Why it explains the symptoms

Harmonics can interfere with the inverter's grid synchronization and cause it to abort the start-up process.

Troubleshooting Steps



Harmonic Analysis

Use a power quality analyzer to measure the Total Harmonic Distortion (THD) of the voltage and current during pump start-up and during normal pump operation. Pay attention to individual harmonic components (3rd, 5th, 7th, etc.).

Compare to Inverter Specs

Check the SolarEdge inverter specifications for their tolerance to harmonic distortion.


Possible Solutions



Harmonic Filter

Install a harmonic filter on the output of the VFD to reduce harmonic distortion. This is a common solution for VFD installations.


Line Reactor

Adding a line reactor to the input of the VFD can also help reduce harmonic distortion.

Active Harmonic Filter

These are more sophisticated and effective than passive filters.


Check VFD Filtering

Some VFDs have built-in harmonic filtering capabilities. Ensure these are enabled and properly configured.

C. Impedance Issues

High impedance in the wiring between the utility transformer, the VFD cabinet, and the solar inverters can exacerbate voltage dips and harmonic distortion.


Why it explains the symptoms

High impedance leads to larger voltage drops for a given current.

Troubleshooting Steps



Impedance Measurement

Use an impedance analyzer to measure the impedance of the wiring between the utility transformer and the VFD cabinet.

Check Wiring Size and Connections

Ensure all wiring is properly sized for the current it's carrying, and that all connections are clean and tight. Look for signs of corrosion or loose connections.


Possible Solutions



Upgrade Wiring

Replace undersized wiring with larger gauge wire to reduce impedance.


Tighten Connections

Ensure all electrical connections are tight and corrosion-free.

D. Grounding Issues

Improper grounding can lead to circulating currents and voltage fluctuations.


Why it explains the symptoms

Grounding issues can cause unpredictable behavior in sensitive electronic equipment like solar inverters.

Troubleshooting Steps



Ground Resistance Measurement

Use a ground resistance tester to measure the resistance of the grounding system.

Check Ground Bonds

Ensure all equipment is properly bonded to the grounding system.


Look for Ground Loops

Ensure there are no ground loops in the system.

Possible Solutions



Improve Grounding System

Improve the grounding system by adding ground rods or upgrading grounding conductors.

Eliminate Ground Loops

Reroute grounding conductors to eliminate ground loops.


E. SolarEdge Inverter Firmware/Software Bug

It's possible there's a bug in the SolarEdge inverter firmware that causes this issue.

Why it explains the symptoms

Software bugs can cause unpredictable behavior.


Troubleshooting Steps



Firmware Update

Ensure the inverters are running the latest firmware version.


Contact SolarEdge Engineering

Escalate the issue to SolarEdge engineering and demand a more thorough investigation.

3. Action Plan


Voltage Monitoring (Priority #1)

Get a power quality analyzer and record voltage during pump start-up.2.

Detailed Information from SolarEdge

Push SolarEdge for a detailed explanation of why they think this is happening and any specific diagnostic steps they recommend. Document all communication.3.

Check Inverter Fault Codes

Even if it's "just" a starting loop, there might be clues logged.4.

Review VFD Settings

Especially the soft-start and acceleration ramp settings.5.

Harmonic Analysis (if voltage dip isn't the problem).
6. Systematic Troubleshooting

If the initial troubleshooting doesn't reveal the cause, work through the list of potential causes, one by one.

Important Considerations



Safety

This is high-voltage equipment. Work should only be performed by qualified electricians who are familiar with working on solar power systems and VFDs.


Documentation

Keep detailed records of all troubleshooting steps, measurements, and settings changes.*

Communication:
Keep SolarEdge informed of your troubleshooting progress.Good luck! This is a challenging problem, but by systematically investigating the possible causes, you should be able to identify the root cause and find a solution. Remember to start with the most likely causes first. Flag for review