Question: This tells me the what and how. But why does an insulated conductor used to bond metal water pipe when installed in a ferrous raceway according to 250.64 (E) need to bond both ends of the raceway.The next question, would be if one end was a myers hub, would that satisfy that end?The other end would be 6’ away and be an LB. For this reason I am using PVC.I would prefer emt.Just curious.Does anyone have Mike Holts grounding and bonding bible? Is it worth the investment?Thank you for your replies!

Okay, let's break down the code requirements for bonding insulated conductors in ferrous raceways and address your specific scenario.

The "Why" Behind Bonding Both Ends of a Ferrous Raceway with an Insulated Bonding Conductor per 250.64(E)

The fundamental reason for this requirement boils down to reducing impedance and ensuring a low-impedance fault current path. Here's a more detailed explanation: Impedance and Fault Current

In the event of a ground fault (a short circuit to a grounded metal part), you want a path for the fault current to quickly and reliably return to the source (usually the transformer). A low-impedance path allows a large fault current to flow. This high current is what trips the overcurrent protection device (circuit breaker or fuse) and clears the fault.


Ferrous Raceway Inductance

Ferrous metal (steel) raceways (like EMT or rigid metal conduit) have inherent inductance. This inductance impedes the flow of alternating current (AC), especially high-frequency fault currents. The longer the ferrous raceway, the greater the inductance.

Skin Effect

AC current tends to flow on the
surface of a conductor. In ferrous raceways, this "skin effect" further concentrates the current on the surface of the raceway, increasing its effective resistance and thus, the overall impedance.

Bonding to Reduce Impedance

By running an insulated bonding conductor inside the ferrous raceway and bonding it to both ends of the raceway, you accomplish the following:

Parallel Path

You create a parallel path for fault current that
bypasses the high impedance of the ferrous raceway itself. The insulated conductor, being inside, experiences a degree of "magnetic field cancellation" from the raceway, reducing its inductance compared to an external conductor.

Equal Potential

Bonding both ends forces the raceway and the insulated conductor to be at approximately the same potential, minimizing voltage differences that could hinder fault current flow.

Why Insulated?
You can use an insulated conductor in the raceway.In summary, the requirement to bond both ends of a ferrous raceway when using an insulated conductor inside it for bonding purposes is all about minimizing impedance and ensuring a reliable, low-impedance path for fault current to quickly trip the overcurrent protection in the event of a ground fault. The goal is electrical safety.

Your Specific Scenario: Myers Hub and LB Fitting
Myers Hub at One End

A Myers hub is a concentric knockout seal. It's designed to provide a watertight connection between a conduit fitting (like your LB) and an enclosure. It's generally considered a suitable bonding means when properly installed. The key is that it must be installed tightly and in a clean, corrosion-free environment. If the paint is removed, the surfaces are clean, and the locknut is wrench-tight, it can provide an acceptable ground path.

LB Fitting at the Other End

The LB fitting, especially if made of ferrous metal,
must be bonded separately. You cannot rely on the threads of the LB connection alone to provide a reliable low-impedance ground fault path. You need a bonding jumper from the grounding electrode conductor to the metal LB.

PVC Sections

The introduction of PVC conduit sections breaks the electrical continuity of the ferrous raceway. This means you absolutely must run a dedicated bonding conductor through the PVC to maintain the necessary fault current path. This conductor should be sized according to NEC Table 250.122 based on the size of the overcurrent device protecting the circuit.

EMT Preference

EMT is often preferred, but if your design includes a section of PVC, you
must run a grounding wire that is sized to code.

Recommendation for Your Situation
1. Run an appropriately sized insulated bonding conductor inside the entire raceway system (including the PVC section). Size it according to NEC Table 250.122.
2. Connect the insulated bonding conductor to the grounding electrode conductor or grounding bus at the source (where the GEC originates).3. At the Myers Hub end

Ensure the Myers Hub is installed correctly, and that the locknut is tightened appropriately.4.

At the LB end

Install a bonding jumper from the grounding electrode conductor or grounding bus to the LB fitting. Use appropriate grounding clamps or lugs to make secure connections.

Regarding Mike Holt's Grounding and Bonding Book



Is it Worth the Investment?
Absolutely! Mike Holt's "Understanding the NEC, Volume 1 and 2" and his "Grounding and Bonding" book are considered essential resources for anyone working with electrical systems. They provide clear explanations, detailed illustrations, and real-world examples that make complex concepts much easier to understand. Many electricians and inspectors swear by them. You will likely find them helpful in understanding and applying the NEC requirements.I hope this helps! Be sure to consult the latest edition of the NEC for the most up-to-date and accurate information and always consult with a qualified electrical inspector or engineer if you have any doubts or concerns about your specific installation. Flag for review