User: ItsMattsFault, Location: Iowa
Asked on: Tuesday, August 6, 2024 at 9:26 am EDT
Answered on: Thursday, March 6, 2025 at 12:46 am EST
Question: Good morning allI work on a site where they are making the conversion from THHN to XHHW wire as a standard.However, we have some THHN wire they don't want to just throw away, and as such are informing us to pull a mix of XHHW and THHN to use it upI was curious if I had some sort of code reference to be able to push back?The craftsman and common sense side of me doesn't want to pull a mix of insulation wires to a single piece of equipment.
Good morning! Your concerns are definitely valid, and it's wise to look for code references to support your position. Here's a breakdown of why mixing THHN and XHHW in the same raceway can be problematic and the code sections to potentially cite
Key Concerns & Potential Code Violations:
1. Ampacity and Temperature Rating Consistency
The fundamental issue
XHHW and THHN have different insulation temperature ratings and, therefore, potentially different ampacities when used in certain conditions. You want to ensure all conductors are rated for the same maximum operating temperature for the application.
Code Reference
NEC 310.15(A)(3) (Corrected by Errata) states that if multiple conductors with different insulation types are installed in a raceway or cable, the ampacity shall be determined based on the lowest temperature rating of any conductor in that assembly. Why this is important
If you have XHHW-2 (90°C) and THHN (75°C) in the same conduit, you must use the 75°C ampacity rating for all conductors in that conduit, even the XHHW. This negates any potential benefit of using the higher-rated XHHW. It also means you could be using wire that is theoretically capable of carrying more current, but is artificially limited by the presence of THHN.2.
Derating Calculations Become Complicated (and Potentially Error-Prone)
The issue
Derating for ambient temperature and number of conductors in a raceway becomes more complex. You must use the 75°C values for all conductors in the same raceway. This can easily lead to mistakes in calculations.
Code Reference
NEC 310.15(C) covers ampacity adjustment factors for ambient temperature and the number of conductors in a raceway. As stated above, you must use the lowest rated temperature rating within that raceway.3. Potential for Misinterpretation and Future Problems
The issue
Mixing wire types creates a potential for future confusion. An electrician troubleshooting the circuit later might not realize that both THHN and XHHW are present and might make incorrect assumptions about ampacity or insulation properties. This could lead to overloads or other unsafe conditions.
Code Reference
While not directly prohibiting the mix,
NEC 110.3(B) requires that equipment be installed and used in accordance with its listing and labeling. Mixing wire types could be argued to be a deviation from good engineering practice and potentially compromise the system's intended performance.4. Workmanship and Professional Standards
The issue
As you pointed out, it's simply not best practice. It looks unprofessional and introduces unnecessary complexity.*
Code Reference
While not a specific code section,
NEC 110.12 covers mechanical execution of work, requiring installations to be neat and workmanlike. While subjective, mixing wire types needlessly could be argued as being less than "neat and workmanlike."How to Push Back (Professionally and Effectively)
Present the Facts
Explain the ampacity limitations imposed by NEC 310.15(A)(3). Show them with a real-world example how mixing the wire essentially negates the benefits of the XHHW and could even force you to use larger conduit than necessary (because you're limited to the 75°C ampacity).
2.
Highlight the Increased Risk of Errors
Emphasize the potential for confusion and mistakes in derating calculations, especially if the installation is modified or repaired in the future.3.
Propose Alternatives
Suggest alternative uses for the existing THHN. Can it be used for control wiring, low-current circuits, or in a location where the 75°C rating is sufficient? Can it be used in other projects that are not converting to XHHW? If there is nothing to use it for, simply throw it away. It may be a sunk cost and you can't go wrong with being safe.4.
Safety First
Frame your concerns in terms of safety and long-term reliability. Remind them that electrical installations are expected to last for many years and should be designed to minimize the risk of failure.5.
Documentation
If they insist on mixing the wires, document your concerns in writing, including the potential code violations and the impact on ampacity. This protects you if there are problems later.
In summary, while the NEC may not explicitly forbid mixing THHN and XHHW, the practical implications and the need to comply with ampacity and derating requirements make it a poor practice. Focus on the safety and long-term reliability aspects to make your case.
Good luck! Let me know if you have any other questions. Flag for review