Question: Running wire to terminal through a 1/8 inch metal plate in the cabinet. that had the holes cut out and insulated with rubber, the wire size is 4/0 and there are 3 wire per phase. we have the 480 v 3phase B O Y..We brought all 3 brown cables through one of the holesthen did the exact same thing for the Ornge cables and the Yellow cables. Someone had told us that we need to put one of each color through each hole, otherwise it will generate too much heat. I can see in conduit, but not through a sheet metal plate with each hole insulated. Would this be a problem, or are we getting false information. Also is this a code requirement?

Yes, the person who told you to run one of each color through each hole is correct. This is a very important principle related to induced currents and heat generation in metallic enclosures. Here's a breakdown of why and the relevant code considerations

Why You Need to Group Conductors from Each Phase Together
Induced Currents (Eddy Currents)

When an alternating current (AC) flows through a conductor, it creates a magnetic field around that conductor. This magnetic field expands and collapses with the AC frequency. If this magnetic field passes through a conductive material (like your metal plate), it will induce circulating currents within that material called
eddy currents.

Heat Generation

Eddy currents flowing through the resistance of the metal plate generate heat (I²R losses). The magnitude of the eddy currents, and thus the heat, is proportional to the strength of the magnetic field and the conductivity of the metal.

Cancellation Effect (Ideal Scenario)

By running all the conductors of a circuit (all phases and neutral, if applicable) through the
same hole, the magnetic fields created by each conductor tend to cancel each other out. The closer the conductors are together, the more complete the cancellation. This significantly reduces the magnetic field passing through the metal plate, minimizing eddy currents and heat.

Your Current Setup (Problem)

In your described setup, you're essentially creating very strong, localized magnetic fields from each phase grouping (Brown, then Orange, then Yellow). These strong, unbalanced fields are very efficient at inducing significant eddy currents in the plate, leading to excessive heat generation. This heat can damage the insulation of the wires, create a fire hazard, and/or damage the equipment within the cabinet.

National Electrical Code (NEC) Considerations


The NEC doesn't explicitly say, "Thou shalt run all phase conductors together through the same hole in a metal plate." However, it contains sections that implicitly require this practice: NEC 300.3(B) Conductors of the Same Circuit

"All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, cable, or cord." While your rubber insulated holes might not be considered a
raceway in the formal sense, the intent is clear: keep the conductors of a circuit (including all phases) together to minimize inductive heating.

NEC 300.20(A) Induced Currents in Metal Enclosures or Metal Raceways

"Where conductors carrying alternating current are installed in metal enclosures or metal raceways, they shall be arranged so as to avoid heating the surrounding metal by induction." This section is the most direct guidance. Running all phases together helps you "avoid heating the surrounding metal by induction."

NEC 310.15(B)(3)(a) Adjustment Factors

While not directly addressing the initial installation method, if excessive heat is generated, you might have to apply ampacity adjustment factors to the conductors, further limiting the circuit's capacity.

What You Should Do (The Correct Installation)
1. Re-arrange the Wiring

This is essential. You
must run one Brown, one Orange, and one Yellow conductor through each hole. Think of it as creating a "miniature" three-phase system within each hole.2.

Consider Hole Size

Make sure the holes are large enough to safely and comfortably accommodate three 4/0 conductors, plus the rubber insulation. Don't cram them in tightly. It may even require increasing the hole size.3.

Use Proper Bushings/Connectors

Even with rubber insulation, use proper bushings or connectors that are listed and labeled for the application. These connectors can help to secure and protect the conductors as they pass through the metal plate.4.

Grounding

Ensure proper grounding and bonding of the metal enclosure to minimize any potential for fault currents to flow through the plate.5.

Torque Values

When connecting the wire to the terminals make sure you torque them to the manufacturer's specification.

Why the Rubber Insulation Alone Is Insufficient


While the rubber insulation provides electrical isolation, it does
nothing* to stop the magnetic fields from inducing eddy currents in the metal plate. The insulation prevents electrical shorts, but it's irrelevant to the magnetic induction problem.

In summary, your initial setup is a serious electrical hazard and violates the spirit, if not the exact letter, of the NEC. Re-wire immediately to group one conductor from each phase in each hole. Flag for review